Technical data
Encoder
EL5021
Number of channels
1
Encoder connection
A+/Sin+, A-/Sin-
B+/Cos+, B-/Cos-
C+, C-
Level: nominal 1 Vpp (0.6...1.2 Vpp), averaged voltage to GND: 2.5 V
Notice Unipolar SinCos signals (i.e. without A-, B- or C-) are recognized as wire break/amplitude error
Position specification
32 bits (period counter + period portion, adjustable)
Period counter
19 ... 24 bits according to setting, default: 22 bits
Period resolution
8 ... 13 bits (256 ... 8192 steps per period),
depends on input frequency,
auto. reduction of resolution depending on the input frequency, default: 10 bits
Signal frequency
max. 250 kHz @ 10-bit period resolution
Sampling of the input signals with 70 MHz
Function and communication
EL5021
min. sampling rate/cycle time
80 µs
Sampling
EtherCAT-synchronously or Distributed Clocks triggered
Distributed Clocks
yes
Functions
  • C-Reset,
  • C-Latch,
  • Display amplitude/frequency error,
  • Change counting direction,
  • Frequency measurement, velocity measurement (from FW07)
Supply and potentials
EL5021
Power supply for the electronics
via the power contacts, approx. 50 mA without external encoder
Current consumption via E-bus
typ. 120 mA
Electrical isolation
500 V (E-bus/field voltage)
Encoder operating voltage/
Encoder supply
5 V (-5% / +10%), max. 0.5 A (short-circuit proof)
(generated from the 24 VDC power contacts)
Environmental conditions
EL5021
Permissible ambient temperature range during operation
-25°C... +55°C
Permissible ambient temperature range during storage
-40°C... +85°C
Permissible relative air humidity
95%, no condensation
General data
EL5021
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Weight
approx. 50 g
Installation
on 35 mm mounting rail, conforms to EN 60715
Standards and approvals
EL5021
Enhanced mechanical load capacity
Yes, see also Installation instructions
for terminals with enhanced mechanical load capacity
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable
Approvals, markings*
CE, EAC, UKCA, CCC
cULus
ATEX, IECEx
Ex markings
Standard
Marking
ATEX
II 3 G Ex nA IIC T4 Gc
IECEx
Ex nA IIC T4 Gc