Standard objects
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave:
  • The Lo-Word contains the used CoE profile (5001).
  • The Hi-Word contains the module profile according to the modular device profile.
UINT32
RO
0x00001389 (5001dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EL4374
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
00
Index 100B Bootloader version
Index (hex)
Meaning
Data type
Flags
Default
100B:0
Bootloader version
Bootloader version
STRING
RO
n/a
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x11163052 (286666834dec)
1018:03
Revision
Revision number of the EtherCAT slave:
  • The Low Word (bit 0-15) indicates the special terminal number.
  • The High Word (bit 16-31) refers to the device description.
UINT32
RO
0x00000000 (0dec)
1018:04
Serial number
Serial number of the EtherCAT slave:
  • Low Word
    • The Low Byte (bit 0-7) of the Low Word contains the year of production.
    • The High Byte (bit 8-15) of the Low Word contains the week of production.
  • The High Word (bit 16-31) is 0.
UINT32
RO
0x00000000 (0dec)
Index 10E2 Manufacturer-specific Identification Code*)
Index (hex)
Meaning
Data type
Flags
Default
10E2:0
UINT8
RO
0x01 (1dec)
10E2:01
SubIndex 001
reserved
STRING
RO
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 10F3 Diagnosis History
Index (hex)
Meaning
Data type
Flags
Default
10F3:0
Diagnosis History
Maximum subindex
UINT8
RO
0x15 (21dec)
10F3:01
Maximum Messages
Maximum number of stored messages
A maximum of 16 messages can be stored.
UINT8
RO
0x00 (0dec)
10F3:02
Newest Message
Subindex of the latest message
UINT8
RO
0x00 (0dec)
10F3:03
Newest Acknowledged Message
Subindex of the last acknowledged message
UINT8
RW
0x00 (0dec)
10F3:04
New Messages Available
Indicates that a new message is available.
BOOLEAN
RO
0x00 (0dec)
10F3:05
Flags
not used
UINT16
RW
0x0000 (0dec)
10F3:06
Diagnosis Message 001
Message 1
OCTET STRING[24]
RO
{0}
10F3:15
Diagnosis Message 016
Message 16
OCTET STRING[24]
RO
{0}
Index 10F8 Timestamp Object
Index (hex)
Meaning
Data type
Flags
Default
10F8:0
Timestamp Object
Timestamp Object [ns]
For SM synchronous operation: Time since power-on
For DC synchronous operation: copy of the DC time
Time can be used by the device e.g. for timestamps of the DiagMessage
UINT64
RO
Index 1420 AO RxPDO-Par Standard (INT16) Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1420:0
Ch.3
PDO Parameter RxPDO 33
UINT8
RO
0x06 (6dec)
1420:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 33.
OCTET-STRING[2]
RO
22 16
Index 1422 AO RxPDO-Par Standard (Real32) Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1422:0
PDO Parameter RxPDO 35
UINT8
RO
0x06 (6dec)
1422:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 35
OCTET-STRING[2]
RO
20 16
Index 1430 AO RxPDO-Par Standard (INT16) Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1430:0
PDO Parameter RxPDO 49
UINT8
RO
0x06 (6dec)
1430:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 49.
OCTET-STRING[2]
RO
32 16
Index 1432 AO RxPDO-Par Standard (Real32) Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1432:0
PDO Parameter RxPDO 51
UINT8
RO
0x06 (6dec)
1432:06
Exclude PDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 51.
OCTET-STRING[2]
RO
30 16
Index 1600 AI RxPDO-Map Control Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1600:0
PDO Mapping RxPDO 1
UINT8
RO
0x04 (4dec)
1600:01
SubIndex 001
1. PDO Mapping entry (3 bits align)
UINT32
RO
0x0000:00, 3
1600:02
SubIndex 002
2. PDO Mapping entry (object 0x7000 (AI Outputs Ch.1), entry 0x04 (Tare))
UINT32
RO
0x7000:04, 1
1600:03
SubIndex 003
3. PDO Mapping entry (object 0x7000 (AI Outputs Ch.1), entry 0x05 (Peak Hold Reset))
UINT32
RO
0x7000:05, 1
1600:04
SubIndex 004
4. PDO Mapping entry (11 bits align)
UINT32
RO
0x0000:00, 11
Index 1610 AI RxPDO-Map Control Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1610:0
PDO Mapping RxPDO 17
UINT8
RO
0x04 (4dec)
1610:01
SubIndex 001
UINT32
RO
0x0000:00, 3
1610:02
SubIndex 002
2. PDO Mapping entry (object 0x7010 (AI Outputs Ch.2), entry 0x04 (Tare))
UINT32
RO
0x7010:04, 1
1610:03
SubIndex 003
3. PDO Mapping entry (object 0x7010 (AI Outputs Ch.2), entry 0x05 (Peak Hold Reset))
UINT32
RO
0x7010:05, 1
1610:04
SubIndex 004
UINT32
RO
0x0000:00, 11
Index 1620 AO RxPDO-Map Standard (INT16) Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1620:0
PDO Mapping RxPDO 33
UINT8
RO
0x01 (1dec)
1620:01
SubIndex 001
1. PDO Mapping entry (object 0x7020 (AO Outputs Ch.3), entry 0x11 (Value))
UINT32
RO
0x7020:11, 16
Index 1622 AO RxPDO-Map Standard (Real32) Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1622:0
PDO Mapping RxPDO 35
UINT8
RO
0x01 (1dec)
1622:01
SubIndex 001
1. PDO Mapping entry (object 0x7020 (AO Outputs Ch.3), entry 0x13 (Value (Real32)))
UINT32
RO
0x7020:13, 32
Index 1623 AO RxPDO-Map Cycle Counter Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1623:0
PDO Mapping RxPDO 36
UINT8
RO
0x01 (1dec)
1623:01
SubIndex 001
1. PDO Mapping entry (object 0x7020 (AO Outputs Ch.3), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7020:14, 16
Index 1630 AO RxPDO-Map Standard (INT16) Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1630:0
PDO Mapping RxPDO 49
UINT8
RO
0x01 (1dec)
1630:01
SubIndex 001
1. PDO Mapping entry (object 0x7030 (AO Outputs Ch.4), entry 0x11 (Value))
UINT32
RO
0x7030:11, 16
Index 1632 AO RxPDO-Map Standard (Real32) Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1632:0
PDO Mapping RxPDO 51
UINT8
RO
0x01 (1dec)
1632:01
SubIndex 001
1. PDO Mapping entry (object 0x7030 (AO Outputs Ch.4), entry 0x13 (Value (Real32)))
UINT32
RO
0x7030:13, 32
Index 1633 AO RxPDO-Map Cycle Counter Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1633:0
PDO Mapping RxPDO 52
UINT8
RO
0x01 (1dec)
1633:01
SubIndex 001
1. PDO Mapping entry (object 0x7030 (AO Outputs Ch.4), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7030:14, 16
Index 1800 AI TxPDO-Par Standard (INT16) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1800:0
PDO parameter TxPDO 1
UINT8
RO
0x06 (6dec)
1800:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1.
OCTET-STRING[6]
RO
01 1A 02 1A 03 1A
Index 1801 AI TxPDO-Par Compact (INT16) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1801:0
PDO parameter TxPDO 2
UINT8
RO
0x06 (6dec)
1801:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2.
OCTET-STRING[6]
RO
00 1A 02 1A 03 1A
Index 1802 AI TxPDO-Par Standard (Real32) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1802:0
PDO parameter TxPDO 3
UINT8
RO
0x06 (6dec)
1802:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 3.
OCTET-STRING[6]
RO
00 1A 01 1A 03 1A
Index 1803 AI TxPDO-Par Compact (Real32) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1803:0
PDO parameter TxPDO 4
UINT8
RO
0x06 (6dec)
1803:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 4.
OCTET-STRING[6]
RO
00 1A 01 1A 02 1A
Index 1810 AI TxPDO-Par Standard (INT16) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1810:0
PDO parameter TxPDO 17
UINT8
RO
0x06 (6dec)
1810:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 17.
OCTET-STRING[6]
RO
11 1A 12 1A 13 1A
Index 1811 AI TxPDO-Par Compact (INT16) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1811:0
PDO parameter TxPDO 18
UINT8
RO
0x06 (6dec)
1811:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 18.
OCTET-STRING[6]
RO
10 1A 12 1A 13 1A
Index 1812 AI TxPDO-Par Standard (Real32) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1812:0
PDO parameter TxPDO 19
UINT8
RO
0x06 (6dec)
1812:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 19.
OCTET-STRING[6]
RO
10 1A 11 1A 13 1A
Index 1813 AI TxPDO-Par Compact (Real32) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1813:0
PDO parameter TxPDO 20
UINT8
RO
0x06 (6dec)
1813:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 20.
OCTET-STRING[6]
RO
10 1A 11 1A 12 1A
Index 1A00 AI TxPDO-Map Standard (INT16) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
PDO Mapping TxPDO 1
UINT8
RO
0x0B (11dec)
1A00:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x01 (Underrange))
UINT32
RO
0x6000:01, 1
1A00:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x02 (Overrange))
UINT32
RO
0x6000:02, 1
1A00:03
SubIndex 003
3. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x03 (Limit 1))
UINT32
RO
0x6000:03, 2
1A00:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x05 (Limit 2))
UINT32
RO
0x6000:05, 2
1A00:05
SubIndex 005
5. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x07 (Error))
UINT32
RO
0x6000:07, 1
1A00:06
SubIndex 006
6. PDO Mapping entry (4 bits align)
UINT32
RO
0x0000:00, 4
1A00:07
SubIndex 007
7. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x0C (Tare Active))
UINT32
RO
0x6000:0C, 1
1A00:08
SubIndex 008
8. PDO Mapping entry (2 bits align)
UINT32
RO
0x0000:00, 2
1A00:09
SubIndex 009
9. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x0F (TxPDO State))
UINT32
RO
0x6000:0F, 1
1A00:0A
SubIndex 010
10. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x10 (TxPDO Toggle))
UINT32
RO
0x6000:10, 1
1A00:0B
SubIndex 011
11. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x11 (Value))
UINT32
RO
0x6000:11, 16
Index 1A01 AI TxPDO-Map Compact (INT16) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A01:0
PDO Mapping TxPDO 2
UINT8
RO
0x01 (1dec)
1A01:01
SubIndex 001
UINT32
RO
0x6000:11, 16
Index 1A02 AI TxPDO-Map Standard (Real32) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A02:0
PDO Mapping TxPDO 3
UINT8
RO
0x0B (11dec)
1A02:01
SubIndex 001
UINT32
RO
0x6000:01, 1
1A02:02
SubIndex 002
UINT32
RO
0x6000:02, 1
1A02:03
SubIndex 003
UINT32
RO
0x6000:03, 2
1A02:04
SubIndex 004
UINT32
RO
0x6000:05, 2
1A02:05
SubIndex 005
UINT32
RO
0x6000:07, 1
1A02:06
SubIndex 006
UINT32
RO
0x0000:00, 4
1A02:07
SubIndex 007
UINT32
RO
0x6000:0C, 1
1A02:08
SubIndex 008
UINT32
RO
0x0000:00, 2
1A02:09
SubIndex 009
UINT32
RO
0x6000:0F, 1
1A02:0A
SubIndex 010
UINT32
RO
0x6000:10, 1
1A02:0B
SubIndex 011
11. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x13 (Value (Real32)))
UINT32
RO
0x6000:13, 32
Index 1A03 AI TxPDO-Map Compact (Real32) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A03:0
PDO Mapping TxPDO 4
UINT8
RO
0x01 (1dec)
1A03:01
SubIndex 001
UINT32
RO
0x6000:13, 32
Index 1A04 AI TxPDO-Map Cycle Counter Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A04:0
PDO Mapping TxPDO 5
UINT8
RO
0x01 (1dec)
1A04:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x14 (Input Cycle Counter))
UINT32
RO
0x6000:14, 16
Index 1A10 AI TxPDO-Map Standard (INT16) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A10:0
PDO Mapping TxPDO 17
UINT8
RO
0x0B (11dec)
1A10:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x01 (Underrange))
UINT32
RO
0x6010:01, 1
1A10:02
SubIndex 002
2. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x02 (Overrange))
UINT32
RO
0x6010:02, 1
1A10:03
SubIndex 003
3. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x03 (Limit 1))
UINT32
RO
0x6010:03, 2
1A10:04
SubIndex 004
4. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x05 (Limit 2))
UINT32
RO
0x6010:05, 2
1A10:05
SubIndex 005
5. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x07 (Error))
UINT32
RO
0x6010:07, 1
1A10:06
SubIndex 006
UINT32
RO
0x0000:00, 4
1A10:07
SubIndex 007
7. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x0C (Tare Active))
UINT32
RO
0x6010:0C, 1
1A10:08
SubIndex 008
UINT32
RO
0x0000:00, 2
1A10:09
SubIndex 009
9. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x0F (TxPDO State))
UINT32
RO
0x6010:0F, 1
1A10:0A
SubIndex 010
10. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x10 (TxPDO Toggle))
UINT32
RO
0x6010:10, 1
1A10:0B
SubIndex 011
11. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x11 (Value))
UINT32
RO
0x6010:11, 16
Index 1A11 AI TxPDO-Map Compact (INT16) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A11:0
PDO Mapping TxPDO 18
UINT8
RO
0x01 (1dec)
1A11:01
SubIndex 001
UINT32
RO
0x6010:11, 16
Index 1A12 AI TxPDO-Map Standard (Real32) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A12:0
PDO Mapping TxPDO 19
UINT8
RO
0x0B (11dec)
1A12:01
SubIndex 001
UINT32
RO
0x6010:01, 1
1A12:02
SubIndex 002
UINT32
RO
0x6010:02, 1
1A12:03
SubIndex 003
UINT32
RO
0x6010:03, 2
1A12:04
SubIndex 004
UINT32
RO
0x6010:05, 2
1A12:05
SubIndex 005
UINT32
RO
0x6010:07, 1
1A12:06
SubIndex 006
UINT32
RO
0x0000:00, 4
1A12:07
SubIndex 007
UINT32
RO
0x6010:0C, 1
1A12:08
SubIndex 008
UINT32
RO
0x0000:00, 2
1A12:09
SubIndex 009
UINT32
RO
0x6010:0F, 1
1A12:0A
SubIndex 010
UINT32
RO
0x6010:10, 1
1A12:0B
SubIndex 011
11. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x13 (Value (Real32)))
UINT32
RO
0x6010:13, 32
Index 1A13 AI TxPDO-Map Compact (Real32) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A13:0
PDO Mapping TxPDO 20
UINT8
RO
0x01 (1dec)
1A13:01
SubIndex 001
UINT32
RO
0x6010:13, 32
Index 1A14 AI TxPDO-Map Cycle Counter Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A14:0
PDO Mapping TxPDO 21
UINT8
RO
0x01 (1dec)
1A14:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x14 (Input Cycle Counter))
UINT32
RO
0x6010:14, 16
Index 1A20 AO TxPDO-Map Status Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1A20:0
PDO Mapping TxPDO 33
UINT8
RO
0x08 (8dec)
1A20:01
SubIndex 001
1. PDO Mapping entry (1 bits align)
UINT32
RO
0x0000:00, 1
1A20:02
SubIndex 002
2. PDO Mapping entry (object 0x6020 (AO Inputs Ch.3), entry 0x02 (Output Overload))
UINT32
RO
0x6020:02, 1
1A20:03
SubIndex 003
3. PDO Mapping entry (object 0x6020 (AO Inputs Ch.3), entry 0x03 (Underrange))
UINT32
RO
0x6020:03, 1
1A20:04
SubIndex 004
4. PDO Mapping entry (object 0x6020 (AO Inputs Ch.3), entry 0x04 (Overrange))
UINT32
RO
0x6020:04, 1
1A20:05
SubIndex 005
5. PDO Mapping entry (1 bits align)
UINT32
RO
0x0000:00, 1
1A20:06
SubIndex 006
6. PDO Mapping entry (object 0x6020 (AO Inputs Ch.3), entry 0x06 (Warning))
UINT32
RO
0x6020:06, 1
1A20:07
SubIndex 007
7. PDO Mapping entry (object 0x6020 (AO Inputs Ch.3), entry 0x07 (Error))
UINT32
RO
0x6020:07, 1
1A20:08
SubIndex 008
8. PDO Mapping entry (9 bits align)
UINT32
RO
0x0000:00, 9
Index 1A30 AO TxPDO-Map Status Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1A30:0
PDO Mapping TxPDO 49
UINT8
RO
0x08 (8dec)
1A30:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1A30:02
SubIndex 002
2. PDO Mapping entry (object 0x6030 (AO Inputs Ch.4), entry 0x02 (Output Overload))
UINT32
RO
0x6030:02, 1
1A30:03
SubIndex 003
3. PDO Mapping entry (object 0x6030 (AO Inputs Ch.4), entry 0x03 (Underrange))
UINT32
RO
0x6030:03, 1
1A30:04
SubIndex 004
4. PDO Mapping entry (object 0x6030 (AO Inputs Ch.4), entry 0x04 (Overrange))
UINT32
RO
0x6030:04, 1
1A30:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1A30:06
SubIndex 006
6. PDO Mapping entry (object 0x6030 (AO Inputs Ch.4), entry 0x06 (Warning))
UINT32
RO
0x6030:06, 1
1A30:07
SubIndex 007
7. PDO Mapping entry (object 0x6030 (AO Inputs Ch.4), entry 0x07 (Error))
UINT32
RO
0x6030:07, 1
1A30:08
SubIndex 008
UINT32
RO
0x0000:00, 9
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the Sync Managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x02 (2dec)
1C12:01
Subindex 001
1. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x1622 (5666dec)
1C12:02
Subindex 002
2. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x1632 (5682dec)
1C12:03
Subindex 003
3. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:04
Subindex 004
4. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:05
Subindex 005
5. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:06
Subindex 006
6. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x04 (4dec)
1C13:01
Subindex 001
1. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A02 (6658dec)
1C13:02
Subindex 002
2. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A12 (6674dec)
1C13:03
Subindex 003
3. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A20 (6688dec)
1C13:04
Subindex 004
4. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A30 (6704dec)
1C13:05
Subindex 005
5. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C13:06
Subindex 006
6. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x0000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
1C32:0
SM output parameter
Synchronization parameters for the outputs
UINT8
RO
0x20 (32dec)
1C32:01
Sync mode
Current synchronization mode:
  • 0: Free Run
  • 1: Synchron with SM 2 Event
  • 2: DC-Mode - Synchron with SYNC0 Event
  • 3: DC-Mode - Synchron with SYNC1 Event
UINT16
RW
0x0000 (0dec)
1C32:02
Cycle time
Cycle time (in ns):
  • Free Run: cycle time of the local timer
  • Synchron with SM 2 Event: cycle time of the master
  • DC-Mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x000F4240 (1000000dec)
1C32:03
Shift time
Time between SYNC0 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:04
Sync modes supported
Supported synchronization modes:
  • Bit 0 = 1: Free Run is supported
  • Bit 1 = 1: Synchron with SM 2 Event is supported
  • Bit 2-3 = 01: DC mode is supported
  • Bit 4-5 = 10: Output Shift with SYNC1 Event (DC mode only)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08)
UINT16
RO
0x0001 (1dec)
1C32:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
0x000186A0 (100000dec)
1C32:06
Calc and copy time
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:09
Maximum delay time
Time between SYNC1 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:0B
SM event missed counter
Number of missed SM events in OPERATIONAL (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0dec)
1C32:0D
Shift too short counter
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only)
BOOLEAN
RO
0x00 (0dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
  • 0: Free Run
  • 1: Synchron with SM 3 Event (no outputs available)
  • 2: DC - Synchron with SYNC0 Event
  • 3: DC - Synchron with SYNC1 Event
  • 34: Synchron with SM 2 Event (outputs available)
UINT16
RW
0x0000 (0dec)
1C33:02
Cycle time
UINT32
RW
1C33:03
Shift time
Time between SYNC0 Event and reading of the inputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:04
  • Bit 0: Free Run is supported
  • Bit 1: Synchron with SM 2 Event is supported (outputs available)
  • Bit 1: Synchron with SM 3 Event is supported (no outputs available)
  • Bit 2-3 = 01: DC-Mode is supported
  • Bit 4-5 = 01: Input shift through local event (outputs available)
  • Bit 4-5 = 10: Input shift with SYNC1 event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08 or 0x1C33:08)
UINT16
RO
0x0001 (1dec)
1C33:05
Minimum cycle time
as 0x1C32:05
UINT32
RO
1C33:06
Calc and copy time
Time between reading of the inputs and the inputs being available for the master (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:07
Minimum delay time
UINT32
RO
0x00000000 (0dec)
1C33:09
Maximum delay time
Time between SYNC1 event and reading of the inputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:0B
as 0x1C32:11
UINT16
RO
0x0000 (0dec)
1C33:0C
as 0x1C32:12
UINT16
RO
0x0000 (0dec)
1C33:0D
as 0x1C32:13
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
as 0x1C32:32
BOOLEAN
RO
0x00 (0dec)
Index F008 code word
Index (hex)
Meaning
Data type
Flags
Default
F008:0
Code word
Code word (currently reserved)
UINT32
RW
0x00000000 (0dec)
Index F009 Password protection
Index (hex)
Meaning
Data type
Flags
Default
F009:0
Password protection
Password protection user calibration
UINT32
RW
0x00000000 (0dec)