Technical data
EL4112
EL4112-0010
Number of outputs
2
Output current per channel
0 ... 20 mA
(short-circuit proof)
-10 ... +10 mA (short-circuit proof)
Accuracy
± 0.1%
of full-scale value
± 0.3%
of full-scale value (at load < 200 Ω, max. 500 Ω permitted)
Resolution
16 bits (including sign)
Sampling type
simultaneous
Ground reference
single ended
Load
< 500 Ω
Distributed Clocks (DC)
Yes, from EL4112-0000-1017
Yes, from EL4112-0010-1017
Max. sampling rate (output rate)
DC disabled **)
Normal operation: 10 kSps (corresponds to minimum EtherCAT cycle time of 100 µs)
Fast mode: 15 kSps (corresponds to minimum EtherCAT cycle time of 66.6 µs)
Fast mode 1-channel: 20 kSps (corresponds to minimum EtherCAT cycle time of 50 µs)
DC enabled
Normal operation: 5 kSps (corresponds to minimum EtherCAT cycle time of 200 µs)
Fast mode: not possible
Power supply for outputs
via the power contacts
Current consumption power contacts
15 mA typ. + load
Power supply for the electronics
via the E-bus
Current consumption via E-bus
typ. 110 mA (160 mA***))
typ. 110 mA (150 mA****))
Electrical isolation
500 V (E-bus/field voltage)
Bit width in process image
Outputs: 2 x 16 bit data
Configuration
no address or configuration settings required
Weight
approx. 60 g
approx. 65 g
Permissible ambient temperature range during operation
0 °C ... +55 °C
Permissible ambient temperature range during storage
-25 °C ... +85 °C
Permissible relative air humidity
95 %, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Installation
on 35 mm mounting rail, conforms to EN 60715
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
see also Installation instructions for enhanced mechanical load capacity
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable
Identification / approval*)
CE, EAC, UKCA
ATEX, IECEx, cULus
**) SyncManager synchronous, EtherCAT frame triggered.
The EL41xx does not support oversampling, therefore the output rate is equal to the EtherCAT cycle time.
***) valid for HW / FW / revision combinations before HW 12 / FW 09, Rev.-1021
***) valid for HW / FW / revision combinations before HW 09 / FW 09, Rev.-1021
Ex markings
Standard
Marking
ATEX
II 3 G Ex nA IIC T4 Gc
IECEx
Ex nA IIC T4 Gc