Connection assignment
Caution: Risk of electric shock! If you do not connect the terminal point N with the neutral conductor of your mains supply (e.g. if the EL3773 is used purely for current measurements), terminal point N should be earthed, in order to avoid dangerous overvoltages in the event of a current transformer fault! |
Caution: Risk of electric shock! Please note that many manufacturers do not permit their current transformers to be operated in no-load mode! Connect the EL3773 to the secondary windings of the current transformers before using the current transformer! |
Fig.4: EL3773Connection
Terminal point |
Description |
Comment | |
Name |
No. | ||
L1 |
1 |
Phase L1 |
Connections for the voltage measurement. Please observe the notes. |
L2 |
2 |
Phase L2 | |
L3 |
3 |
Phase L3 | |
N |
4 |
Neutral conductor N | |
IL1 |
5 |
Consumer at phase L1 |
Connections for the current transformers. Please observe the notes. |
IL2 |
6 |
Consumer at phase L2 | |
IL3 |
7 |
Consumer at phase L3 | |
IN |
8 |
Star point of the current transformers | |
Fig.27: Block diagram