Common technical data
Technical data | EL3751 |
Analog inputs | 1 channel |
Connection technology | 2 - 6 wire |
Resolution | 24 bit including sign, 32 bit display |
Sampling type | simultaneous |
Ground reference | differential |
Selection of oversampling factors | 1, 2, 4, 5, 8, 10, 16, 20, 25, 32, 40, 50, 64 |
ADC conversion method | deltaSigma ΔΣ, 1.28 msps (internal sampling rate) |
Limit frequency input filter hardware | Before AD converter: 30 kHz hardware filter |
Measuring error | Typically ±0.01% @ 23°C, exceptions for individual measuring ranges, details see function tables and 2) below. |
Max. sampling rate/conversion time | 10 ksps/ 100 µs (fixed, additionally free downsampling in firmware through decimation factor) |
Supported EtherCAT cycle time (depending on the operation mode) | DistributedClocks: min. 100 µs, max. 25 ms (max. 10 ms recommended) FrameTriggered/Synchron: min. 200 µs, max. 100 ms FreeRun: not supported |
Signal delay (step response) | tbd. |
Signal delay (linear) | tbd. Phase response linear, constant envelope delay |
Acquisition method | Simultaneous (1 channel, simultaneous with DC synchronization of several terminals) |
Dielectric strength - destruction limit | max. permitted short-term/continuous voltage
Note: -UV, corresponds to internal GND |
Recommended operation voltage range to compliance with specification (UCM, common mode) | max. permitted voltage during specified normal operation
Distributed Clocks | Yes, with oversampling |
Electrical isolation bus/channel | 500 V DC (1 min. typical test voltage) |
Electrical isolation channel/channel | (not applicable since 1 channel) |
Bit width of the process image (default setting) | 32 bit / per value |
Supports CoE Interface function | Yes |
Special features | integrated switchable ¼ bridge extension for 120 and 350 Ω Higher-order synchronization, PeakHold drag indicator, predefined and freely configurable software filters, TrueRMS, freely selectable downsampling, 2-stage integrator/differentiator, free scaling function (also non-linear), end value limiter, extended/legacy range, line compensation Available with factory calibration certificate on request |
Internal surge voltage protection of the inputs related to -Uv (internal ground) | +IN1, -IN1: at approx. 12 ±0.5 V +IN2, -IN2: at approx. < -0.3 V or > +5.3 V |
Supply voltage for electronic | via the E-bus |
Current consumption via E-bus | typ. 260 mA |
Thermal power dissipation | typ. 1.2 W |
Current consumption from the power contacts | none |
Permissible operating altitude range | 0 to 2000 m (derating at higher altitudes on request) |
Weight | approx. 65 g |
Permissible ambient temperature range during operation | 0…+55 °C (in horizontal installation position) 0…+45°C (all other installation positions) |
Permissible ambient temperature range during storage | -25…+85 °C |
Installation position | Operation possible in all installation positions; compliance with full accuracy only possible in horizontal/standard position. |
Permissible relative humidity | 95 %, no condensation |
Max. sensor wire length | The wire length from the EtherCAT terminal to the sensor/encoder must have max. 30 m without any action of protection. For larger wire lengths a proper over voltage protection (surge protection) is required. |
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) |
Mounting | on 35 mm mounting rail conforms to EN 60715 |
Vibration/shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
EMC immunity/emission | conforms to EN 61000-6-2 / EN 61000-6-4 |
Protection class | IP20 |
Approvals/ markings *) |
2) Dominant part of the basic accuracy is its offset specification (see following tables). The process described in the Offset correction section eliminates this proportion and increases the measurement accuracy considerably.
Ex markings
Standard | Marking |
ATEX | II 3 G Ex ec IIC T4 Gc |
IECEx | Ex ec IIC T4 Gc |