Measurement 3.6…21 mA (NAMUR NE43)
Measurement mode | 3.6…21 mA (NAMUR NE43) | ||||
Measuring range, nominal | 4…20 mA | ||||
Measuring range, end value (full scale value) | 20 mA | ||||
Measuring range, technically usable | 3.6…21 mA | ||||
Fuse protection | Internal overload limiting, continuous current resistant | ||||
PDO resolution | 24 Bit | ||||
PDO LSB (Extended Range) | 2.048 nA | ||||
PDO LSB (Legacy Range) | n.a. | ||||
Common-mode voltage Vcm | max. +/- 10V related to -Uv (internal ground) | ||||
Basic accuracy: Measuring deviation at 23°C, with averaging | < ±0.01%FSV = ±100 ppmFSV | ||||
Offset/Zero Point deviation (at 23°C) | EOffset | < 65 ppmFSV | |||
Gain/scale/amplification deviation (at 23°C) | EGain | < 50 ppm | |||
Non-linearity over the whole measuring range | ELin | < 40 ppmFSV | |||
Repeatability | ERep | < 40 ppmFSV | |||
Noise (without filtering) | ENoise, PtP | < 100 ppmFSV | < 781 [digits] | ||
ENoise, RMS | < 18 ppmFSV | < 141 [digits] | |||
Max. SNR | > 94.9 dB | ||||
Noisedensity@1kHz | < 5.09 | ||||
Noise (with 50Hz FIR filtering) | ENoise, PtP | < 10 ppmFSV | < 78 [digits] | ||
ENoise, RMS | < 2.0 ppmFSV | < 16 [digits] | |||
Max. SNR | > 114.0 dB | ||||
Temperature coefficient | TcGain | < 15 ppm/K typ. | |||
TcOffset | < 5 ppmFSV/K typ. | ||||
Common-mode rejection ratio (without filtering) | DC: < 3 nA/V typ. | 50 Hz: < 5 nA/V typ. | 1 kHz: < 80 nA/V typ. | ||
Common-mode rejection ratio (with 50Hz FIR filtering) | DC: < 3 nA/V typ. | 50 Hz: < 3 nA/V typ. | 1 kHz: < 3 nA/V typ. | ||
Largest short-term deviation during a specified electrical interference test | ±0.05%FSV = ±500 ppmFSV typ. | ||||
Input impedance ±Input 1 (Internal resistance) | Differential 200 Ω || 11 nF typ. | ||||
CommonMode 1 MΩ || 40 nF typ. Methodology: Resistor against -UV, capacitance against SGND | |||||
Input impedance ±Input 2 | No usage of this input in this mode | ||||
Current measuring range 3.6…21 mA (NAMUR)
Fig.39: Chart: current measuring range 3.6…21 mA (NAMUR)![]() | Only Extended Range mode for measuring range 4 mA NAMUR Legacy Range mode is not available for this measurement range. The Extended Range Mode will be set automatically and although a corresponding write access to the CoE Object 0x8000:2E (Scaler) is not declined, the parameter is not changed. |
Fig.34: Frequency response 20 mA measurement range, fsampling = 10 kHz, integrated filter 1/2 deactivated