Measurement ±10 V
Measurement mode
±10 V
Measuring range, nominal
-10…+10 V
Measuring range, end value (full scale value)
10 V
Measuring range, technically usable
-10.737…+10.737 V
PDO resolution
24 bit (including sign)
PDO LSB (Extended Range)
1.28 µV
PDO LSB (Legacy Range)
1.192.. µV
Basic accuracy: Measuring deviation at 23°C, with averaging
< ±0.01%FSV = ±100 ppmFSV
Offset/Zero Point deviation (at 23°C)
EOffset
< 70 ppmFSV
Gain/scale/amplification deviation (at 23°C)
EGain
< 60 ppm
Non-linearity over the whole measuring range
ELin
< 25 ppmFSV
Repeatability
ERep
< 20 ppmFSV
Noise (without filtering)
ENoise, PtP
< 100 ppmFSV
< 781 [digits]
ENoise, RMS
< 18 ppmFSV
< 141 [digits]
Max. SNR
> 94.9 dB
Noisedensity@1kHz
< 2.55 Measurement ±10 V 1:
Noise (with 50Hz FIR filtering)
ENoise, PtP
< 10 ppmFSV
< 78 [digits]
ENoise, RMS
< 2.0 ppmFSV
< 16 [digits]
Max. SNR
> 114.0 dB
Temperature coefficient
TcGain
< 8 ppm/K typ.
TcOffset
< 5 ppmFSV/K typ.
Common-mode rejection ratio (without filtering)
DC: >115 dB typ.
50 Hz: >105 dB typ.
1 kHz: >80 dB typ.
Common-mode rejection ratio (with 50Hz FIR filtering)
DC: >115 dB typ.
50 Hz: >115 dB typ.
1 kHz: >115 dB typ.
Largest short-term deviation during a specified electrical interference test
±0.05%FSV = ±500 ppmFSV typ.
Input impedance ±Input 1
(Internal resistance)
Differential 4.1 MΩ || 11 nF typ.
CommonMode 1 MΩ || 40 nF typ.
Methodology: Resistor against -UV, capacitance against SGND
Input impedance ±Input 2
No usage of this input in this mode
According to the Beckhoff „measurement error” a reference value can be calculated as specified in section “General information on measuring accuracy/measurement uncertainty”.
That result is for the measurement range ±10V by the above given data and an environment temperature of TEnvironment,max = 55°C to ±321 ppmFSV (or 0.032%FSV).
See also measurement error/measurement deviation/measurement uncertainty, output uncertainty under Further documentation for I/O components with analog in and outputs.
Measurement ±10 V 2:Fig.8: Representation ±10 V measurement range
Note: In Extended Range Mode the Underrange/Overrange display in the PDO status has the character of an information/warning when the nominal measuring range is exceeded, i.e. no Error is displayed in the PDO status and LED. If the technical measuring range is also exceeded, Error = TRUE is also displayed. The detection limit for Underrange/Overrange Error can be set in the CoE.
In Legacy Range mode, an Underrange/Overrange event also leads to an Error in the PDO status.
Measurement ±10 V 3:Fig.9: Frequency response ±10 V measurement range, fsampling = 10 kHz, integrated filter 1/2 deactivated