Capacitive and inductive influences
Internal and external capacitive and inductive influences may distort the measurement reading through their dynamic characteristics. In order to minimize these influences, a delay is set between switching on of the measuring current and the start of the measurement. The delay time can be set via object 0x80n0:31 and switched on or off for each channel via object 0x80n0:05. The delay time is set in 0x80n0:37 as a channel-specific value. In the measuring ranges -1 to 5 this value is multiplied with 20 ms, in the measuring ranges 6 and 7 with 50 ms. The standard delay time is therefore 200 or 500 ms.
The delay time does not become active if two consecutive measurements take place in the same measuring range and on the same channel.
The delay time largely allows charging processes at the test specimen to complete. Once the charging process is complete based on the sensitivity setting (steady-state tolerance object 0x80n0:3E ), the steady state bit is set to TRUE.