Technology
Table of contents
General description
Specifications
 - Accuracy
 - Internal resistances - Fuse
Default setting
General description
The functionality of the EL3681 is similar to that of a commercial digital multimeter. The terminal offers the following features:
The data collection is shown in fig. Data flow EL3681.
Technology 1:
Data flow EL3681
Application note
For the measurement of a 60 Hz signal, the CoE (0x8000:0A) object should be set accordingly. For all other signal frequencies the 50 Hz preset is valid, because of the longer integration time. The accuracy information shown below refer to a input signal of a frequency range of >0 .. 1 kHz. With higher frequencies the measurement accuracy decreases (-3 dB > 500 kHz).
It is possible to measure a non-sinus AC input signal, if the Crest factor is < 3. The accuracy information below refers to a Crest factor of max. 2.
The simultaneous electrical connection of both current paths (10, 1 A) and the voltage path for a following alternating measurement of values is possible, but not recommended. In case of AC components in the signal, a parasitic crosstalk from path to path can occur. After switching over, the process data update time can be up to 1 second.
Specifications
Accuracy
The unused measurement input should be connected to the COM port of the terminal in order to make the analysis as accurate as possible and minimize interference.
The measuring accuracy depends on the type of signal to be measures and on the terminal settings.
The accuracy values specified in the following table apply to the default settings for the terminal parameters:
- Enable vendor calibration
true
- Enable filter
true
- Frequency
50 Hz
- Zero compensation interval
Off (0)
- Presentation
Scaled (1Bit/1µV) (2)
Signal to be measured
Typical max. tolerance in % of full scale value 1)
Typical temperature drift 2)6)
Measurement type
Measuring range
40°C 3)
0 .. 55°C
ppm/°C
DC
3 V - 300 V 8)
0.01
0.2
35
300 mV 8)
0.05
0.2
35
100 mA 7)
0.1
0.5
50
1 A
0.1
0.5
50
10 A
0.2
1.2
170
AC 4) 5)
3 V - 300 V
0.25
0.75
130
300 mV
0.25
0.5
50
100 mA
0.5
1
50
1 A
0.5
0.7
50
10 A
0.5
1.2
150
Table 1: Measuring tolerances depending on temperatures. MBE = full scale value.
1) In 60 Hz mode of ADC 0.02 should be added to the specified tolerance
2) The values apply to a minimum terminal warm-up time of 30 minutes
3) The compensation temperature is 40 °C
4) All AC voltage and current ranges are specified for a range of 5% to 100%
5) Crest factor < 2
6) In 60 Hz mode an additional temperature drift of 20 ppm / °C is to be expected.
7) The maximum deviation under EMC test conditions according to IEC 61131 is 1 %
8) The maximum deviation under EMC test conditions according to IEC 61131 is 0.2 %
Measuring procedure
The measuring technique in the terminal is based on the dual-slope technique.
The Zero Offset Compensation function reads the internal ADC offset and corrects the analog value accordingly. The additional temperature drift can thus be partly compensated, either cyclically or through external control.
Operating conditions
Internal resistance
Measurement type
Measuring range
Internal resistance
DC
300 mV - 300 V
12.5 MΩ
100 mA - 1 A
0.2 Ω
10 A
3 mΩ
AC 4) 5)
300 mV - 300 V
1 MΩ, approx. 33 pF
100 mA - 1 A
0.2 Ω
10 A
3 mΩ
Table 2: Internal resistances
Fuse
Notes on replacing the fuse can be found in section Accessories.
Default Setting
The factory setting for the multimeter terminal enables voltages up to 300 VDC to be measured directly without additional settings. The Autorange function is active and selects the measuring range automatically. The measured value is displayed with 1 bit/µV, i.e. no adjustment is required. Fig. Display of measured value in TwinCAT shows an example for measured values in the TwinCAT tree. In the example the value 10448400 corresponds to a voltage of 10.448400 V
Technology 2:
The terminal is supplied with a sample program that enables the process data of the EL3681 to be modified and the terminal to be re-parameterized.