EL3453 - Technical data
Analog specifications
EL3453
EL3453-0020
EL3453-0100
Number of inputs
4 x current, 3 x voltage
Technology
3-phase power measurement
Special feature
factory calibrated with calibration certificate
Oversampling factor
Internal sampling rate
approx. 9.7 ksps (per channel)
Sampling type
simultaneously across all channels
Ground reference
single-ended
Update time
with each half-wave (10 ms at 50 Hz)
Parameters measured
EL3453
EL3453-0020
EL3453-0100
Measured values
Current, voltage, active power, reactive power, apparent power, active energy, reactive energy, apparent energy, fundamental power and energy, cos φ, power factor, frequency, THD, harmonics (up to the 63rd harmonic), power quality factor (PowerQualityFactor)
Measuring error
0.3 % relative to full scale value (U/I), 0.6 % calculated values
Accuracy class according to IEC 61557-12
  • 0.2 Active power
  • 1 Reactive power
  • 0.2 Apparent power
  • 0.5 Active energy
  • 2 Reactive energy
  • 0.5 Apparent energy
  • 0.02 Frequency
  • 0.5 Current
  • 0.1 Voltage
  • 0.5 Power factor
  • 0.2 Voltage unbalance
  • 1 Voltage harmonics
  • 1 Current harmonics
  • 1 Voltage THD
  • 1 Current THD
in preparation
Measuring procedure
true RMS value calculation
Nominal voltage range (mains voltage)
AC: 400 Vrms (ULX-N) or 690 Vrms (ULX-ULY) (TN network: 600 Vrms)
DC: 480 V with connection via L1 and L2 (or L3)
corresponding to AC:
100 Vrms (ULX-N) for voltage transformers
Technical voltage measuring range
80-520 Vrms (ULX-N) or 139-897 Vrms (ULX-ULY) common reference potential N/GND
max. time for voltages above 500 Vrms (ULX-N) or 863 Vrms (ULx-ULy): tmax < 10 s **)
145 Vrms (ULX-N) common reference potential N/GND
Max. permitted overvoltage
max. ±736 V (peak value, ULX-N, equivalent to 520 Vrms) or max. ±1270 V (peak value, ULX-ULY, equivalent to 897 Vrms) **)
max. 300 Vrms (ULX-N) **)
Internal resolution
24 bit
Input resistance voltage circuit
typ. 1.5 MΩ
Nominal current range
corresponding to AC:100 mArms;1 Arms (default);
5 Arms recommended via measuring transformer x A AC/1 A AC
Technical current measuring range
2.25 A (peak value, equivalent to 1.59 Arms) or 9.6 A (peak value, equivalent to 6.8 Arms)
Permissible overcurrent**)
max. ±10 A peak value, equivalent to 7 Arms **) per channel and
max. sum current (I1+I2+I3+IN) ±20 A peak value, equivalent to 14 Arms
Short-time current carrying capacity
60 A (sinusoidal) for 1 sec., the upstream use of current-limiting current transformers is recommended
Largest short-term deviation during a specified electrical interference test
< ±0.5 % of full scale value for the current measurement
Input resistance current circuit
typ. 3 mΩ
Frequency range***)
15 … 400 Hz
Cut-off frequency
4000 Hz
CAUTION
**) Consequences of prolonged operation above the nominal range of the measuring voltage
Prolonged operation above the nominal range can lead to functional impairment and/or shortening of the service life.
EL3453 - Technical data 1:
***) Frequency measurement EL3453
The time source for the frequency measurement has a stability of 100 ppm or better. The accuracy of the frequency measurements with a constant 50 Hz voltage signal is 5 mHz or more.
Supply and potentials
EL3453
EL3453-0020
EL3453-0100
Electrical isolation
4500 V
Current consumption of power contacts
Current consumption via E-bus
260 mA typ.
Communication
EL3453
EL3453-0020
EL3453-0100
Configuration
via TwinCAT System Manager
Distributed clocks
optional (for determining the zero crossing time)
Accuracy of Distributed Clocks
<< 1 µs
Environmental conditions
EL3453
EL3453-0020
EL3453-0100
perm. ambient temp.
range during operation
-25 °C ... +60 °C
0 °C ... +55 °C
perm. ambient temp.
range during storage
-40 °C ... +85 °C
-25 °C ... +85 °C
Relative humidity
95 %, no condensation
General data
EL3453
EL3453-0020
EL3453-0100
Weight
approx. 100 g
Dimensions (W x H x D)
approx. 27 mm x 100 mm x 70 mm (width aligned: 24 mm)
Installation
on 35 mm mounting rail, conforms to EN 60715
Installation position
variable
Standards and approvals
EL3453
EL3453-0020
EL3453-0100
Vibration/shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity/emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Marking/certification*)
CE, EAC, UKCA, cULus