Description of the visualization

The visualization for the editing of two EL3351s has the following appearance as standard:

Description of the visualization 1:Fig.168: Main page of the visualization

Clicking on the "Go to CoE Settings" button on the "Main" page during operation takes you to the page on which the CoE entries can be set. A small example of RGB color editing is opened by clicking on the "Show RGB" button.

System Time

The current Windows system time is displayed in this field.

Status information

The upper text field displays the status of the EtherCAT device. For further information see:  EtherCAT Master Diagnostics
The second text field indicates whether an error has occurred in the terminals during operation. If this is the case, the number of the terminal in which the error has occurred is displayed.

Device status information

The status of the terminal is displayed here. The field with the label "WcState" displays the status of the working counter.

Description of the visualization 2:Fig.169: Working Counter EL3351

As soon as WcState adopts the value "1", the terminal is no longer participating in the process data traffic. If valid real-time communication is taking place, WcState has the value "0".

The "InfoData State" field displays the status of the terminal.

Description of the visualization 3:Fig.170: State EL3351

If this status is not equal to 8, then the terminal is not in the OP (operational) status. Information about which different statuses the value can adopt is provided by the Infobox in the System Manager (see fig. State EL3351).

Bridge Status/ Supply Status

This area informs you about the status of the channels for the acquisition of the bridge voltage and the reference voltage. The individual values take the form of Boolean variables. There is an error if the value "1" is adopted.

Visualization - Main

Description of the visualization 4:Fig.171: Visualization example program for EL3351, main page

Bridge Voltage/ Supply Voltage

The size of the measuring signal UDiff in mV and the reference signal URef in V are displayed in this area.

Settings

The nominal characteristic value and the nominal load of the connected load cell must be set at the beginning. Clicking on the respective field enables a value to be entered. The input of a zero error (zero balance) is optional.

Calibration

Clicking on the "Calibration Mode" button activates the calibration mode. This mode permits the automatic determination of the size of the zero error and the nominal characteristic value of a connected load cell. If the mode is activated, instructions appear in the text field of the visualization to guide you through the entire calibration process. The calibration is started by clicking on the "Start Calibration" button.

Description of the visualization 5:Fig.172: Calibration mode: Start

If it has not already been done, the nominal load of the connected load cell must be entered first.

Description of the visualization 6:Fig.173: Calibration mode: Input of nominal load

If this has been done, the next step is initiated by pressing the "Save" button.

Description of the visualization 7:Fig.174: Calibration mode: Confirmation of nominal load

The zero error of the load cell is now determined. It must be ensured when doing this that the load cell is not loaded. If this is the case you can move to the next step with "Save".

Description of the visualization 8:Fig.175: Calibration mode: Determining the zero error

In order to determine the nominal characteristic value, the load cell must be loaded with a known reference weight. The higher and more precise the reference weight is, the more precise the nominal characteristic value will be. The reference weight must be entered into the associated field.

Description of the visualization 9:Fig.176: Calibration mode: Entering the reference weight

The calibration process is concluded by pressing the "Save" button.

The size of the calculated nominal characteristic value and zero error can be taken from the respective fields under Settings.

Description of the visualization 10:Fig.177: Calibration mode: Conclusion

A new calibration can be started by pressing the "Start Calibration" button. If the calibration mode is ended by clicking on the "Calibration Mode" button, the calculated settings are retained.

Measuring Function

On basis of the functions provided in the example program, the weight loading the load cell is calculated from the values for the nominal load, the nominal characteristic value, the measuring signal and the reference signal and - if it exists - from the zero error. The tare weight can be set via the "Set Tare weight" button if a weight is loading the load cell. The set tare weight is deleted by pressing the "Reset Tare weight" button. If a tare weight is set, the net weight is calculated using the equation net weight = gross weight - tare weight.

Description of the visualization 11:

Supply voltage and characteristic value of the load cell

The supply voltage of the load cell should be selected to suit its characteristic value. The maximum measuring range of the measuring signal is +/- 20 mV. If the load cell has a characteristic value of 2 mV/V, for example, then a supply voltage of 10 V should be selected so that the maximum differential voltage is 20 mV/10 V.

If the load cell used has a nominal characteristic value of 4 mV/V, the 5 V supply voltage can be picked up directly at the terminal, for optimum utilization of the measuring range (as described in Fig. Connection of a load cell with 5 V supply via the EL3351).

Visualization - CoE

The CoE entries can be read and modified on page 2 of the visualization of the example program.

Description of the visualization 12:

Fig. 31: CoE page of the visualization

Clicking on the "Go to Main" button on the "CoE" page during operation takes you to the page on which the weight calculation takes place.

CoE Index 0x8000 / 0x8010

At this point "User Scaling" can be activated and the offset and gain of "User Scaling" can both be adjusted. Values can only be entered if "User Scaling" is activated. This is done by clicking on the On/Off button. The changes are confirmed by pressing the "Write CoE" button.

Description of the visualization 13:Fig.178: Activation of "User Scaling"

After activating "User Scaling" both the offset and the gain can be adjusted. All changes must be confirmed by pressing the "Write CoE" button.

Description of the visualization 14:Fig.179: Input of offset and gain

Button "Read CoE"

Pressing this button causes the CoE entries in the indices 0x8000:0 and 0x8010:0 to be read out successively and their values displayed on the visualization.

Button "Write CoE"

If you wish to modify CoE entries, you must enter the changes via the display elements. The changes are confirmed by clicking on the "Write CoE" button.

Button "Set CoE to Default"

Actuating this button causes all CoE entries to be reset to the factory preset values and directly written.

Filter

The filter setting determines the filter frequency and thus the conversion time for both channels of the terminal. The higher the filter frequency, the faster the conversion time. Furthermore, the toggle bit is evaluated over a period of 10 seconds. A new set of process data is present on both a rising and falling edge. An example of this is given in the section TwinCAT Scope View 2 demonstration. The update time is calculated directly from the number of rising and falling edges of the toggle bit.

Dealing with real characteristic values

The nominal characteristic values of load cells are subject to tolerances which can be taken from the associated certificates. Hence it could be the case, for example, that the nominal characteristic value of a load cell is specified as 2 mV/V, but deviates slightly from that according to the certificate. In addition to that there is a zero error in most cases.

The following is intended to describe how the example program can be adjusted with these values. The data of the load cell in this calculation example should be as follows:

First of all the real nominal characteristic value can be entered in the "Rated Output (Cn)" field and the zero error in the "Zero Balance" field. Another possibility to compensate the zero error is to employ the user scaling. The associated value must be entered in the "User Scale Offset" field. The following calculations must be performed in order to obtain the value that balances the zero error from this example:

The following maximum differential voltage results from fully loading the load cell:

Description of the visualization 15:

The raw value of the measuring signal at 20 mV/V is 2147483647. Hence, the maximum raw value that can be achieved with a measuring signal of 10.6 mV is:

Description of the visualization 16:

From this, the raw value of the zero error becomes:

Description of the visualization 17:

In order to compensate this error, the zero point must be "shifted downwards" by precisely this value; hence, "- 24696063" must be entered in the User Scale Offset field.

Visualization - RGB

A small example of RGB color editing is opened by clicking on the "Show RGB" button. The color in which the text field with the instructions appears is dynamically composed of the basic colors red, green and blue. The values of these three colors are shown in this window, as is the combined value of all three colors. The red, green and blue components can be adapted using the regulators and the combined color appears in the lowest field.

Description of the visualization 18:Fig.180: RGB window