Object description EL3204-0200
Object description EL3204-0200 1:
EtherCAT XML Device Description
The display matches that of the CoE objects from the EtherCAT XML Device Description. We recommend downloading the latest XML file from the download area of the Beckhoff website and installing it according to installation instructions.
Object description EL3204-0200 2:
Parameterization via the CoE list (CAN over EtherCAT)
The terminal is parameterized via the CoE - Online tab (double-click on the respective object) or via the Process Data tab (allocation of PDOs). Please note the following general CoE information when using/manipulating the CoE parameters: - Keep a startup list if components have to be replaced - Differentiation between online/offline dictionary, existence of current XML description - Use "CoE reload" for resetting changes
Object description EL3204-0200 3:
Relevant objects
The object description refers to the analog input terminals for Pt100 (RTD) in 1 to 8 channel versions. Observe the indices with regard to the objects relevant for the respective terminal (channel dependent).
Introduction
The following section first describes the objects required for normal operation, followed by a complete overview of missing objects.
Objects for commissioning
Index 1011 Restore default parameters
Index (hex)
Meaning
Data type
Flags
Default value
1011:0
UINT8
RO
0x01 (1dec)
1011:01
SubIndex 001
If this object is set to "0x64616F6C" in the set value dialog, all backup objects are reset to their delivery state.
UINT32
RW
0x00000000 (0 dec)
Index 80n0 RTD settings for 0 ≤ n ≤ 3 (Ch. 1 - 4)
Object description EL3204-0200 4:
The filter properties are set only via index 0x8000:15
The filter frequencies are set for all channels of the EL3204-0200 terminals centrally via index 0x8000:15 (channel 1). The corresponding indices 0x80n0:15 have no parameterization function!
Index (hex)
Meaning
Data type
Flags
Default value
80n0:0
RTD Settings
Maximum subindex
UINT8
RO
0x1B (27dec)
80n0:01
Enable user scale
User scale is active.
BOOLEAN
RW
0x00 (0dec)
80n0:02
Process data Presentation
permitted values
0: Signed
1: Absolute MSB sign
2: High resolution (1/100°C)
BIT3
RW
0x00 (0dec)
80n0:05
Siemens bits
The S5 bits are superimposed on the three low-order bits (value 0x60n0:11)
Bit 0 = 1 (“overrange” or “underrange”)
Bit 1 (not used)
Bit 2 (not used)
BOOLEAN
RW
0x00 (0dec)
80n0:06
Enable filter
Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x00 (0dec)
80n0:0A
Enable user calibration
Enabling of the user calibration
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Enable vendor calibration
Enabling of the vendor calibration
BOOLEAN
RW
0x01 (1dec)
80n0:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
80n0:12
User scale gain
This is the user scaling gain.
The gain is represented in fixed-point format, with the factor 2-16.
The value 1 corresponds to 65535 (0x00010000).
INT32
RW
0x00010000 (65536dec)
80n0:15
Filter settings
This object determines the digital filter settings, if it is active via Enable filter (index 0x80n0:06).
The possible settings are sequentially numbered.
permitted values:
0: 50 Hz
1: 60 Hz
2: 100 Hz
3: 500 Hz
4: 1 kHz
5: 2 kHz
6: 3.75 kHz
7: 7.5 kHz
8: 15 kHz
9: 30 kHz
10: 5 Hz
11: 10 Hz
UINT16
RW
0x0000 (0dec)
80n0:17
User calibration offset
User offset calibration
INT16
RW
0x0000 (0dec)
80n0:18
User calibration gain
User gain compensation
UINT16
RW
0xFFFF (65535dec)
Index (hex)
Meaning
Data type
Flags
Default value
80n0:19
RTD element
permitted values:
0: Pt1000 (-200...850°C)
2: Ni1000 100 °C (TK5000, at 100 °C 1500 Ohm, -30 to 160 °C)
3: Ni1000 (-60...250°C)
4: NTC 5k (0°C: 16325 Ohm, -40...100°C)
5: NTC 10k (0°C: 32650 Ohm, -30...150°C)
6: NTC 10k (0°C: 29490 Ohm, -30...150°C)
7: NTC 10k (0°C: 27280 Ohm, -40...110°C, as for KL3204-0030)
8: NTC 20k (0°C: 70200 Ohm, -20...150°C)
9: Fet (-30...150°C)
101: Resolution 1/10 Ohm (0 to 6553.5 Ohm)
102: Resolution 1/10 Ohm (0 to 65535 Ohm)
103: Resolution 1/10 Ohm (0 to 240 kOhm)
110: RTD table (for further parameters see 0x80n1)
111: B-parameter equation (for further parameters see 0x80n2)
112: DIN IEC 60751 equation (for further parameters see 0x80n3)
113: Steinhart-Hart equation (for further parameters see 0x80n4)
UINT16
RW
0x0000 (0dec)
80n0:1A
Connection technology
permitted values
0: Two-wire connection
3: n. c. (channel deactivated)
UINT16
RW
0x0000 (0dec)
80n0:1B
Wire calibration
Offset value for the calibration of the supply lines
[1/10] Ohm
INT16
RW
0x0000 (0dec)
Index 80n1 RTD Table
The standard values in the following table show by way of example the conversion values of a Pt1000 within the range from 0 °C to 140 °C with a resolution of 1/10 Ohm
Index (hex)
Meaning
Data type
Flags
Default value
80n1:0
RTD Table
The sensor characteristic can be programmed with this table
UINT8
RO
105
80n1:01
Distance in Degrees
The value set describes the distance of the entries in °C
UINT16
RW
10
80n1:02
Amount of Entries
The value entered describes the number of entries with which the dependence on distance in °C, start temperature of the measuring range and final temperature are displayed according to the equation below
Final temperature = start temperature + ((number of entries -1) * distance in °C)
UINT16
RW
15
80n1:03
Start Temperature
The value entered describes the start of the measuring range
Standard value 0 °C
INT16
RW
0
80n1:04
Conversion Factor
1 = 1/10 Ohm per digit in the table entries
10 = 1 Ohm per digit in the table entries
100 = 10 Ohm per digit in the table entries
UINT16
RW
1
80n1:05
Value 1
UINT16
RW
0x2710 (10000dec)
80n1:06
Value 2
UINT16
RW
0x2896 (10390dec)
80n1:07
Value 3
UINT16
RW
0x2A1B (10779dec)
80n1:08
Value 4
UINT16
RW
0x2B9F (11167dec)
80n1:09
Value 5
UINT16
RW
0x2D22 (11554dec)
80n1:0A
Value 6
UINT16
RW
0x2EA3 (11939dec)
80n1:0B
Value 7
UINT16
RW
0x3024 (12324dec)
80n1:0C
Value 8
UINT16
RW
0x31A3 (12707dec)
80n1:0D
Value 9
UINT16
RW
0x3321 (13089dec)
80n1:0E
Value 10
UINT16
RW
0x349E (13470dec)
80n1:0F
Value 11
UINT16
RW
0x361A (13850dec)
80n1:10
Value 12
UINT16
RW
0x3795 (14229dec)
80n1:11
Value 13
UINT16
RW
0x390E (14606dec)
80n1:13
Value 14
UINT16
RW
0x3A87 (14983dec)
80n1:14
Value 15
UINT16
RW
0x3BFE (15358dec)
80n1:15
Value 16
UINT16
RW
0x0000 (0dec)
80n1:69
Value 100
UINT16
RW
0x0000 (0dec)
Index 80n2 RTD B-parameter equation for 0 ≤ n ≤ 3 (Ch. 1 - 4)
Index (hex)
Meaning
Data type
Flags
Default value
80n2:0
RTD B-Parameter Equation
UINT8
RO
0x05 (5dec)
80n2:01
Min Temperature
Start of the measuring range in °C.
INT16
RW
-30
80n2:02
Max Temperature
End of the measuring range in °C.
INT16
RW
150
80n2:03
Rn
Resistance value at Tn. In most cases = 25 °C.
INT16
RW
1000
80n2:04
Tn
Reference temperature for Rn [°C]
INT16
RW
25
80n2:05
B-parameter
B-parameter [Kelvin]
REAL32
RW
3710
Index 80n3 RTD DIN EN 60751 equation for 0 ≤ n ≤ 3 (Ch. 1 - 4) 1 - 4)
Index (hex)
Meaning
Data type
Flags
Default value
80n3:0
Standard parameter for Pt1000 within the range 0 to 850°C.
UINT8
RO
0x06 (6dec)
80n3:01
Min Temperature
INT16
RW
0
80n3:02
Max Temperature
INT16
RW
850
80n3:03
R0
see equation
UINT16
RW
1000
80n3:04
A parameter
see equation
REAL32
RW
3.908E-3
80n3:05
B parameter
see equation
REAL32
RW
-5.775E-7
80n3:06
C parameter
see equation
REAL32
RW
-4.183E-12
Index 80n4 RTD Steinhart-Hart equation for 0 ≤ n ≤ 3 (Ch. 1 - 4)
Index (hex)
Meaning
Data type
Flags
Default value
80n4:0
RTD Steinhart Hart Equation
Standard values for an NTC10K with 32650 Ohm at 0 °C:
C1 default = 1.12119E-03
C2 default = 2.35346E-04
C3 default = 0
C4 default = 8.34620E-08
UINT8
RO
0x06 (6dec)
80n4:01
Min Temperature
INT16
RW
-30
80n4:02
Max Temperature
INT16
RW
150
80n4:03
C1
see equation
REAL32
RW
1.1211E-03
80n4:04
C2
see equation
REAL32
RW
2.35346E-04
80n4:05
C3
see equation
REAL32
RW
0
80n4:06
C4
see equation
REAL32
RW
8.24620E-08
Complete overview
Standard objects
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default value
1000:0
Device type
Device type of the EtherCAT slave: the Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile.
UINT32
RO
0x01401389 (20976521dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default value
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EL3204-0200
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default value
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default value
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
01
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default value
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x0C843052 (209989714dec)
1018:03
Revision
Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description
UINT32
RO
0x00000000 (0dec)
1018:04
Serial number
Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default value
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 180n RTD TxPDO-Par for 0 ≤ n ≤ 3 (Ch. 1 - 4)
Index (hex)
Meaning
Data type
Flags
Default value
180n:0
RTD TxPDO-Par
PDO parameter TxPDO 1
UINT8
RO
0x09 (9dec)
180n:06
Exclude TxPDOs
This entry specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1
OCTET-STRING[0]
RO
180n:07
TxPDO State
The TxPDO state is set if it was not possible to correctly read in the associated input data
BOOLEAN
RO
0x00 (0dec)
180n:09
TxPDO Toggle
The TxPDO toggle is toggled with each update the corresponding input data
BOOLEAN
RO
0x00 (0dec)
Index 1A0n RTD TxPDO-Map 0 ≤ n ≤ 3 (Ch. 1 - 4)
Index (hex)
Meaning
Data type
Flags
Default value
1A0n:0
RTD TxPDO-Map
PDO Mapping TxPDO 1
UINT8
RO
0x08 (8dec)
1A0n:01
SubIndex 001
1. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.1), entry 0x01 (Underrange))
UINT32
RO
0x60n0:01, 1
1A0n:02
SubIndex 002
2. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.1), entry 0x02 (Overrange))
UINT32
RO
0x60n0:02, 1
1A0n:03
SubIndex 003
3. PDO Mapping entry (4 bits align)
UINT32
RO
0x0000:00, 4
1A0n:04
SubIndex 004
4. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.1), entry 0x07 (Error))
UINT32
RO
0x60n0:07, 1
1A0n:05
SubIndex 005
5. PDO Mapping entry (7 bits align)
UINT32
RO
0x00n0:00, 7
1A0n:06
SubIndex 006
6. PDO Mapping entry (object 0x180n (RTD TxPDO-Par Ch.1), entry 0x07 (TxPDO State))
UINT32
RO
0x180n:07, 1
1A0n:07
SubIndex 007
7. PDO Mapping entry (object 0x180n (RTD TxPDO-Par Ch.1), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x180n:09, 1
1A0n:08
SubIndex 008
8. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.1), entry 0x11 (Value))
UINT32
RO
0x60n0:11, 16
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default value
1C00:0
Sync manager type
Using the sync managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync-Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync-Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync-Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync-Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default value
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RO
0x00 (0dec)
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default value
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RO
0x04 (4dec)
1C13:01
Subindex 001
1. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RO
0x1A00 (6656dec)
1C13:02
Subindex 002
2. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RO
0x1A01 (6657dec)
1C13:03
Subindex 003
3. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RO
0x1A02 (6658dec)
1C13:04
Subindex 004
4. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RO
0x1A03 (6659dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default value
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
Current synchronization mode:
  • 0: Free Run
  • 1: Synchronous with SM 3 event (no outputs available)
  • 2: DC - Synchronous with SYNC0 Event
  • 3: DC - Synchronous with SYNC1 Event
  • 34: Synchronous with SM 2 event (outputs available)
UINT16
RW
0x0000 (0dec)
1C33:02
Cycle time
Cycle time (in ns):
  • Free Run: Cycle time of the local timer
  • Synchronous with SM 2 event: Master cycle time
  • DC-Mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x00000000 (0dec)
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:04
Sync modes supported
Supported synchronization modes:
  • Bit 0: free run is supported
  • Bit 1: synchronous with SM 2 event is supported (outputs available)
  • Bit 1: synchronous with SM 3 event is supported (no outputs available)
  • Bit 2-3 = 01: DC mode is supported
  • Bit 4-5 = 01: input shift through local event (outputs available)
  • Bit 4-5 = 10: input shift with SYNC1 event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 1C33:08)
UINT16
RO
0xC007 (49159dec)
1C33:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
0x00000000 (0dec)
1C33:06
Calc and copy time
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:07
Minimum delay time
UINT32
RO
0x00000000 (0dec)
1C33:08
Command
  • 0: Measurement of the local cycle time is stopped
  • 1: Measurement of the local cycle time is started
The entries 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values.
For a subsequent measurement the measured values are reset
UINT16
RW
0x0000 (0dec)
1C33:09
Maximum delay time
Time between SYNC1 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:0B
SM event missed counter
Number of missed SM events in OPERATIONAL (DC mode only)
UINT16
RO
0x0000 (0dec)
1C33:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0 dec)
1C33:0D
Shift too short counter
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only)
UINT16
RO
0x0000 (0 dec)
1C33:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only)
BOOLEAN
RO
0x00 (0 dec)
Profile-specific objects (0x6000-0xFFFF)
The profile-specific objects have the same meaning for all EtherCAT slaves that support the profile 5001.
Index 60n0 RTD Inputs for 0 ≤ n ≤ 3 (Ch. 1 – 4)
Index (hex)
Meaning
Data type
Flags
Default value
60n0:0
RTD Inputs
Maximum subindex
UINT8
RO
0x11 (17dec)
60n0:01
Underrange
The measuring range is undershot.
BOOLEAN
RO
0x00 (0dec)
60n0:02
Overrange
The measuring range is overshot.
BOOLEAN
RO
0x00 (0dec)
60n0:07
Error
The error bit is set if the data is invalid.
BOOLEAN
RO
0x00 (0dec)
60n0:0F
TxPDO State
Validity of the data of the associated TxPDO (0 = valid, 1 = invalid).
BOOLEAN
RO
0x00 (0dec)
60n0:10
TxPDO Toggle
The TxPDO toggle is toggled by the slave when the data of the associated TxPDO is updated.
BOOLEAN
RO
0x00 (0dec)
60n0:11
Value
The analog input data
INT16
RO
0x0000 (0dec)
Index 80nE RTD Internal Data for 0 ≤ n ≤ 3 (Ch. 1 - 4)
Index (hex)
Meaning
Data type
Flags
Default value
80nE:0
RTD Internal Data
Max. subindex
UINT8
RO
80nE:01
ADC raw value
ADC raw value.
INT32
RO
80nE:02
Resistor (1/10 Ohm)
resulting measured resistance
UINT32
RO
Index 80nF RTD Vendor Data for 0 ≤ n ≤ 3 (Ch. 1 - 4)
Index (hex)
Meaning
Data type
Flags
Default value
80nF:0
RTD Vendor Data
Max. subindex
UINT8
RO
0x03 (3dec)
80nF:01
Calibration offset
Calibration offset
INT32
RW
0x00000DAC (3500dec)
80nF:02
Calibration gain
Gain value for measuring range 0 to 5000 Ohm
UINT16
RW
0x3D68 (15720dec)
80nF:03
Calibration gain ext.
Gain value for measuring range 5 to 240 kOhm
UINT16
RW
0x05A0 (1440dec)
Index (hex)
Meaning
Data type
Flags
Default value
F000:0
General information for the modular device profile
UINT8
RO
0x02 (2dec)
F000:01
Module index distance
Index spacing of the objects of the individual channels
UINT16
RO
0x0010 (16dec)
F000:02
Maximum number of modules
Number of channels
UINT16
RO
0x0004 (4dec)
Index F008 Code word
Index (hex)
Meaning
Data type
Flags
Default value
F008:0
Code word
currently reserved
UINT32
RW
0x00000000 (0dec)
Index F010 Module list
Index (hex)
Meaning
Data type
Flags
Default value
F010:0
Module list
Maximum subindex
UINT8
RW
0x04 (4dec)
F010:01
SubIndex 001
Analog Input Profile for RTD
UINT32
RW
0x00000140 (320dec)
F010:02
SubIndex 002
UINT32
RW
0x00000140 (320dec)
F010:03
SubIndex 003
UINT32
RW
0x00000140 (320dec)
F010:04
SubIndex 004
UINT32
RW
0x00000140 (320dec)