Technical data
Technical data
EL3202-0010
EL3202-0020/0030
Number of inputs
2
Sensor types
Pt100, Pt200, Pt500, Pt1000, Ni100, Ni120, Ni1000
KT/KTY from firmware 06
resistance measurement 10 Ω…1 kΩ or 10 Ω…4 kΩ (e. g. for potentiometer connection)
Connection technology
4-wire
Temperature range
Range-dependent:
-200…+850°C
(Pt sensors)
-60…+250°C
(Ni sensors)
High-precision measurement
only for Pt100 sensors,
Measuring range
-200…+320°C,
see Note!
Resolution (default)
0.01°C per digit
Sampling type
Multiplex
Ground reference
Single-ended
Conversion time
Approx. 800 ms…2 ms (configurable), depending on configuration and filter setting
approx. 85 ms, preset
ADC conversion method
ΔΣ (Delta-Sigma)
Measuring current (depending on the sensor element and temperature)
typ. < 0.5 mA
Sensor supply
Continuous current (not switched)
Measuring error
for Pt100 sensors, 4-wire connection technology, measuring range -200 to 320°C, 50 Hz filter, according to the local mains frequency (example: EU/China: 50 Hz, North America: 60 Hz):
< ±0.1°C at ambient temperature of 40°C
< ±0.3°C in operating temperature range
< ±1.0°C (extended temperature range, EL3201-0010)
Note: other sensor cases according to CoE can be used with reduced accuracy (e. g. Pt1000, 3-wire connection etc.)
Support NoCoEStorage
Yes
Width in the process image
Max. 8 bytes input
Power supply for the electronics
via the E-bus
Current consumption via E-bus
typ. 190 mA
Electrical isolation
500 V (E-bus/field voltage)
Configuration
via TwinCAT System Manager
Weight
Approx. 60 g
Permissible ambient temperature range during operation
-25°C…+60°C
Permissible ambient temperature range during storage
-40°C…+85°C
Permissible relative air humidity
95%, no condensation
Dimensions (W x H x D)
Approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Assembly
On 35 mm mounting rail in compliance with EN 60715
Vibration / shock resistance
In accordance with EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
In accordance with EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
Any
Identification / approval*)
CE, EAC, UKCA, CCC
ATEX, IECEx, cULus
Ex markings
Standard
Marking
ATEX
II 3 G Ex ec IIC T4 Gc
IECEx
Ex ec IIC T4 Gc