Technical data
Technical data | EL3201-0010 | EL3201-0020/0030 |
Number of inputs | 1 | |
Sensor types | Pt100, Pt200, Pt500, Pt1000, Ni100, Ni120, Ni1000 | |
Connection technology | 4-wire | |
Temperature range | Range-dependent: -60…+250°C High-precision measurement | |
Resolution (default) | 0.01°C per digit | |
Sampling type | Simultaneous | |
Ground reference | Single-ended | |
Conversion time | Approx. 4…500 ms (configurable), depending on configuration and filter setting | |
ADC conversion method | ΔΣ (Delta-Sigma) | |
Measuring current (depending on the sensor element and temperature) | typ. < 0.5 mA | |
Sensor supply | Continuous current (not switched) | |
Measuring error | for Pt100 sensors, 4-wire connection technology, < ±0.1°C at ambient temperature of 40°C Note: other sensor cases according to CoE can be used with reduced accuracy (e. g. Pt1000, 3-wire connection etc.) | |
Support NoCoEStorage | Yes | |
Width in the process image | Max. 4 bytes input | |
Power supply for the electronics | via the E-bus | |
Current consumption via E-bus | typ. 190 mA | |
Electrical isolation | 500 V (E-bus/field voltage) | |
Configuration | via TwinCAT System Manager | |
Weight | Approx. 60 g | |
Permissible ambient temperature range during operation | -25°C…+60°C | |
Permissible ambient temperature range during storage | -40°C…+85°C | |
Permissible relative air humidity | 95%, no condensation | |
Dimensions (W x H x D) | Approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | |
On 35 mm mounting rail in compliance with EN 60715 | ||
Vibration / shock resistance | In accordance with EN 60068-2-6 / EN 60068-2-27 | |
EMC immunity / emission | In accordance with EN 61000-6-2 / EN 61000-6-4 | |
Protection rating | IP20 | |
Installation position | Any | |
Identification / approval*) | ||
Ex markings
Standard | Marking |
ATEX | II 3 G Ex ec IIC T4 Gc |
IECEx | Ex ec IIC T4 Gc |