Pin assignment, display and diagnosis

EL3214

Pin assignment, display and diagnosis 1:
Fig.18: EL3214 pin assignment

EL3214 – pin assignment

Terminal point

No.

Comment

+R1

1

Input +R1, current-carrying

RL1

2

Input RL1, de-energized sense line

+R2

3

Input +R2, current-carrying

RL2

4

Input RL2, de-energized sense line

+R3

5

Input +R3, current-carrying

RL3

6

Input RL3, de-energized sense line

+R4

7

Input +R4, current-carrying

RL4

8

Input RL4, de-energized sense line

-R1

9

Input -R1, current-carrying

n. c.

10

not used

-R2

11

Input -R2, current-carrying

n. c.

12

not used

-R3

13

Input -R3, current-carrying

n. c.

14

not used

-R4

15

Input -R4, current-carrying

n. c.

16

not used

Notice

Increased measurement uncertainty with signal bundling of the AGND line

In this terminal, the AGND contacts (signal return line -R) are connected in the terminal.
If the connection lines are to be reduced on the system side, one line instead of n lines can be used for all n RTD sensors at this terminal.
However, since each channel individually permanently drives its measuring current (some 100 µA, see explanations chapter "RTD measurement in EL32xx"), all n RTD currents then flow via one line, there is an n-fold increase in voltage drop there, which is also recorded by the ratiometric voltage measurement in the terminal.
The result is the same as for long lines. If RTD sensors are to be connected in this way, a system-side check and, if necessary, compensation using WireCalibration CoE 0x80n0:1B (convert voltage drop to apparent line resistance for this purpose) or UserScale 0x80n0:11/12 is recommended.
Since the line resistances are temperature-dependent and the measuring current depends on the RTD resistance, however, such a static "compensation" cannot achieve the measurement uncertainty as in operation with two lines connected short.

Pin assignment, display and diagnosis 2:

Connection of analog RTD signal lines

To ensure that the analog signals can be measured with as little interference as possible, also observe the notes in the chapter "Connection of analog RTD signal lines".

EL3214 – LEDs

LED

Color

Meaning

RUN

green

This LED indicates the terminal's operating state:

off

State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for terminal firmware updates

flashing

State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set

single flash

State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state

on

State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible

ERROR1 - 4

red

Short circuit or wire break. The resistance value is in the invalid range of the characteristic curve.