Configuration of 0/4..20 mA differential inputs
This section describes the 0/4..20 mA differential inputs for terminal series EL301x, EL302x, EL311x, EL312x and terminals EL3174, EL3612, EL3742 and EL3751.
For the single-ended 20 mA inputs the terminal series EL304x, EL305x, EL314x, EL315x, EL317x, EL318x and EL375x they only apply with regard to technical transferability and also for devices whose analogue input channels have a common related ground potential (and therefore the channels are not to each other and/or not to power supply electrically isolated). Herewith an example for an electrically isolated device is the terminal EL3174-0002.
Technical background
The internal input electronics of the terminals referred to above have the following characteristic (see Fig. Internal connection diagram for 0/4..20 mA inputs):
Accordingly, for multi-channel measurements Vcm specifications must be followed.
Configuration of 0/4..20 mA differential inputs 1:
Internal connection diagram 0/4...20 mA inputs
The block diagram for a 2 channel terminal shows the linked GND points within the terminal (Fig. Internal connection for 0/4..20 mA inputs of a EL3xx2):
Configuration of 0/4..20 mA differential inputs 2:
Internal connection diagram for 0/4..20 mA inputs of a EL3xx2
For all channels within the terminal Vcm-max must not be exceeded.
Configuration of 0/4..20 mA differential inputs 3:
Vcm for 0/4..20 mA inputs
If Vcm of an analog input channel is exceeded, internal equalizing currents result in erroneous measurements.
For 1 and 2 channel terminals the internal GND is therefore fed out to a terminal point, so that the Vcm specification can be met through application-specific configuration of this GND point, even in cases of atypical sensor configuration.
Example 1
The 2-channel EL3012 is connected to 2 sensors, which are supplied with 5 and 24 V. Both current measurements are executed as low-side measurements. This connection type is permitted, because at Imax CMPch1 and CMPch2 are approx. 330 mV above 0 V, which means that Vcm is always < 0.5 V. The requirement of Vcm < 10 V (applicable to EL30xx) is therefore adhered to.
Configuration of 0/4..20 mA differential inputs 4:
Example 1: low-side measurement
If the EL30x1/EL30x2 or EL31x1/EL31x2 terminals have no external GNDint connection, the GNDint potential can adjust itself as required (referred to as "floating"). Please note that for this mode reduced measuring accuracy is to be expected.
Example 1a
Accordingly, this also applies if the floating point GNDINT is connected to another potential.
Configuration of 0/4..20 mA differential inputs 5:
Example 1a, high-side measurement
Example 2
The same EL3012 is now again connected with the two 20 mA sensors, although this time with one low-side measurement at 5 V and one high-side measurement at 12 V. This results in significant potential differences Vcm > 10 V (applicable to EL30xx) between the two channels, which is not permitted.
Configuration of 0/4..20 mA differential inputs 6:
Example 2, high-side/low-side measurement
To rectify this, GNDint can in this case be connected externally with an auxiliary potential of 6 V relative to "0 V". The resulting A/GNDint will be in the middle, i.e. approx. 0.3 V or 11.6 V.
Example 3
In the EL3xx4 terminals GNDint is internally connected with the negative power contact. The choice of potential is therefore limited.
Configuration of 0/4..20 mA differential inputs 7:
Invalid EL3xx4 configuration
The resulting CMP is 23.6 V, i.e. >> 10 V (applicable to EL30xx). The EL30x4/EL31x4 terminals should therefore be configured such that CMP is always less than Vcm,max.
Summary
This results in certain concrete specifications for external connection with 0/4..20 mA sensors:
If the sensor cable is shielded, the shield should not be connected with the GNDint terminal point but with a dedicated low-impedance shield point.
Configuration of 0/4..20 mA differential inputs 8:
Connection of GNDint
In the EL30x1/EL30x2 and EL31x1/EL31x2 terminals the internal GND, GNDint connection is fed out to terminal contacts.
To achieve a precise measurement result GNDint should be connected to a suitable external low-impedance potential, taking account the specifications for Vcm.