EL3074 - Connection, display and diagnostics
EL3074 – connection
Terminal point | Description | Internally connected | Max. current carrying capacity *) | |
Name | No. | |||
Ch 1 U+ | 1 | Channel 1, voltage measurement, positive input | - | not applicable (voltage inputs) |
Ch 2 U+ | 2 | Channel 2, voltage measurement, positive input | - | |
Ch 3 U+ | 3 | Channel 3, voltage measurement, positive input | - | |
Ch 4 U+ | 4 | Channel 4, voltage measurement, positive input | - | |
+24 V | 5 | +24 V | 5, 6, 7, 8; positive power contact | 1 A |
+24 V | 6 | +24 V | 5, 6, 7, 8; positive power contact | 1 A |
+24 V | 7 | +24 V | 5, 6, 7, 8; positive power contact | 1 A |
+24 V | 8 | +24 V | 5, 6, 7, 8; positive power contact | 1 A |
GND | 9 | Signal ground for channel 1 | Negative power contact (observe current carrying capacity) | 100 mA |
GND | 10 | Signal ground for channel 2 | Negative power contact (observe current carrying capacity) | 100 mA |
GND | 11 | Signal ground for channel 3 | Negative power contact (observe current carrying capacity) | 100 mA |
GND | 12 | Signal ground for channel 4 | Negative power contact (observe current carrying capacity) | 100 mA |
Ch1 I- | 13 | Channel 1, current measurement, input | - | 50 mA (see note "Overcurrent protection of the 20 mA inputs“) |
Ch2 I- | 14 | Channel 2, current measurement, input | - | |
Ch3 I- | 15 | Channel 3, current measurement, input | - | |
Ch4 I- | 16 | Channel 4, current measurement, input | - | |
*) Constant current; short-term higher currents are to be avoided and can cause thermal overload (damage) | ||||
![]() | Overcurrent protection of the 20 mA inputs The current inputs are protected against damage due to overcurrent by an internal electronic overcurrent detection with self-resetting current path separation. The overcurrent is caused by an occasionally excessive sensor voltage. Depending on the duration and level of the voltage applied, currents > 200 mA can also occur briefly (tripping time: µs range) until the current path separation becomes effective. Approximately 1 second after an overcurrent detection and the resulting current path separation, the current path is closed again. If the excessive sensor voltage is still present, an overcurrent is detected again and the current path is opened. This process is repeated as long as the excessive voltage is present (auto-retry).
EL3074 - LEDs
LEDs
LED | Color | Meaning | |
RUN *) | green | These LEDs indicate the terminal's operating state: | |
off | State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for terminal firmware updates | ||
flashing | State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set | ||
Single flash | State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks. | ||
on | State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible | ||
Error**) | red | off | No error |
on | Error is present, corresponds to PDO Error | ||
*) If several RUN LEDs are present, all of them have the same function. | |||