Technical data
Analog input | |||
Technical data | EL3008-0003 | EL3008‑0005 | |
Analog inputs | 8 | ||
Function | Voltage measurement | ||
Wiring | 2-wire | ||
Ground reference | Cascaded channels | ||
Max. sampling rate | min. 2 ms (max. 500 sps) per channel 1) | ||
Sampling type | Multiplex Ch. 1..8, each approx. 125 µs delay between Ch n/n+1 | ||
Internal resistance | > 8 MΩ | ||
Input filter cut-off frequency | 1.5 kHz (-3 dB, 1st order low-pass) | ||
Settling time | Filter IIR8 (default): 1 sec typ. (0...90 %) Filter disabled: 2 ms typ. (0…90 %) | ||
Dielectric strength | max. ±13 V per channel against AGND (temporary and permanent) | max. ±24 V per channel against AGND (temporary and permanent) | |
Measuring range, nominal (FSVnom) | -3 V … +3 V | -5 V … +5 V | |
Measuring range, technical (FSVtechn) | -3.22 V … +3.22 V | -5.35 V … +5.35 V | |
Resolution | 16 bit (including sign) | ||
Conversion method | SAR | ||
Measuring error/ uncertainty | < ±0.1 %FSV typ. (at 25°C ±5°C, otherwise < ±0.2 %) 1) | ||
Temperature coefficient TkGain | 35 ppmFSV/K typ. 1) | ||
Temperature coefficient TkOffset | Tbd. | ||
Noise | ±0.2 mV / 66 ppmFSV (with IIR8 filter) 1) | ||
Channel crosstalk | typ. < -70 dB 1) | ||
Largest short-term deviation during a specified electrical interference test | ±1 %FSV typ. | ||
Electrical isolation channel/channel | no | ||
1) Preliminary information |
General | |
Technical data | EL3008-0003, EL3008-0005 |
Power supply | via the E-bus |
Distributed clocks | – |
Electrical isolation channel/E-bus | Reinforced insulation in accordance with EN 61010-2-030, EN 60664-1 Production test 6 kV DC Type test: 6.4 kV DC / 1 min; 7.4 kV DC / 5 sec |
Electrical isolation channel/SGND | - (SGND not available) |
Measurement category / overvoltage category | 300 V CAT II; with contact protection cover 1500 V CAT II; according to EN 61010-2-030 Notes:
Current consumption via E-bus | 190 mA typ. |
Current consumption of power contacts | not present |
Min. EtherCAT cycle time | 100 µs |
Special features | Cascaded channels, extended range 107 %, FIR/IIR filter can be enabled |
EMC immunity/emission | conforms to EN 61000-6-2 / EN 61000-6-4 |
Configuration | Via the EtherCAT master, e.g. TwinCAT |
Approvals/markings*) | CE, |
Mechanical properties | |
Connection type | 10-pin PushIn connector plug, service plug (25 mating cycles) Solid/stranded wire 0.14...1.5 mm², strip length 8 mm with ferrule 0.28...1.0 mm² No pulling/plugging under voltage permitted |
Weight | approx. 90 g |
on 35 mm mounting rail, conforms to EN 60715 | |
Operating temperature | 0 °C…+55 °C |
Storage temperature | -25 °C…+85 °C |
Relative humidity | 95%, no condensation |
Protection rating | IP20 |
Vibration/shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Mounting note | 10-pin plug included in the scope of delivery Contact protection cover ZS9100-0005 included in the scope of delivery |
Permissible operating altitude range | 0 to 2000 m (according to EN 61010-1) |
Pollution degree | 2 or better (according to EN 61010-1) |