Diagnostics in the CoE
The EL2596 has internal diagnostics. Warnings and errors are also displayed by the LEDs. The diagnostics can be viewed in the CoE objects under 0xA000 “DOX Diag data Ch. 1”.
Diagnostics in the CoE 1:
Fig.231: Diagnostics in the CoE object 0xA000
The warning and error levels for the supply and output voltages can be adjusted in the CoE objects 0x8000:11 – 0x8000:16.
In case of an error, bit 0 “Ready to activate” in the “DOX Status” goes to 0. The LED output can then no longer be set. An error must be rectified and reset via a rising edge on the “Reset” bit in the “DOX Control”. In case of a reset, the “Enable” and “Output” bits under “DOX Control” must be deactivated.
Object
Correction
A000:01
Saturated
Target voltage cannot be reached
Increase Uin or reduce set current
A000:02
Over temperature
Warning at internal temperature of 80 °C
Error at internal temperature of 100 °C
EL2596 must cool down
A000:04
Under voltage (Supply)
Under voltage supply
Increase Uin
A000:05
Over voltage (Supply)
Over voltage supply
Reduce Uin
A000:06
Short circuit
Short circuit has occurred
Check whether the load is connected correctly and is functional. (not detected during voltage control)
A000:07
Open load
Wire breakage detected
A000:09
Misc error
Internal hardware error
A000:0B
Over voltage (Output)
Overvoltage on the digital output
Reduce output voltage