Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 0x1000 Device type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1000:0 |
Device type |
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. |
UINT32 |
RO |
0x00001389 (5001dec) |
Index 0x1008 Device name
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
STRING |
RO |
EL2522 |
Index 0x1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
00 |
Index 0x100A Software version
100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO | 06 |
Index 0x1011 Restore default parameters
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1011:0 |
Restore default parameters |
Restore default settings |
UINT8 |
RO |
0x01 (1dec) |
1011:01 |
SubIndex 001 |
If this object is set to "0x64616F6C" in the Set Value Dialog, all backup objects are reset to their delivery state. |
UINT32 |
RW |
0x00000000 (0dec) |
Index 0x1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x09DA3052 (165294162dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description | UINT32 | RO | 0x00000000 (0dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
Index 0x10F0 Backup parameter handling
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardized loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum across all backup entries of the EtherCAT slave |
UINT32 |
RO |
0x00000000 (0dec) |
Index 0x1400 PTO RxPDO-Par Control Ch.1
1400:0 | PTO RxPDO-Par Control Ch.1 | PDO Parameter RxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1400:06 | Exclude RxPDOs | Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 1 | OCTET-STRING[6] | RO | 01 16 04 16 00 00 |
Index 0x1401 PTO RxPDO-Par Control Position Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1401:0 |
PTO RxPDO-Par Control Position Ch.1 |
PDO Parameter RxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1401:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 2 |
OCTET-STRING[6] |
RO |
00 16 02 16 03 16 |
Index 0x1402 PTO RxPDO-Par Target compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1402:0 |
PTO RxPDO-Par Target compact Ch.1 |
PDO Parameter RxPDO 3 |
UINT8 |
RO |
0x06 (6dec) |
1402:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 3 |
OCTET-STRING[6] |
RO |
01 16 03 16 00 00 |
Index 0x1403 PTO RxPDO-Par Target Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1403:0 |
PTO RxPDO-Par Target Ch.1 |
PDO Parameter RxPDO 4 |
UINT8 |
RO |
0x06 (6dec) |
1403:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 4 |
OCTET-STRING[6] |
RO |
01 16 02 16 00 00 |
Index 0x1404 PTO RxPDO-Par Arrival Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1404:0 |
PTO RxPDO-Par Arrival Ch.1 |
PDO Parameter RxPDO 5 |
UINT8 |
RO |
0x06 (6dec) |
1404:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 5 |
OCTET-STRING[6] |
RO |
00 16 02 16 03 16 |
Index 0x1405 PTO RxPDO-Par Control Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1405:0 |
PTO RxPDO-Par Control Ch.2 |
PDO Parameter RxPDO 6 |
UINT8 |
RO |
0x06 (6dec) |
1405:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 6 |
OCTET-STRING[6] |
RO |
06 16 09 16 00 00 |
Index 0x1406 PTO RxPDO-Par Control Position Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1406:0 |
PTO RxPDO-Par Control Position Ch.2 |
PDO Parameter RxPDO 7 |
UINT8 |
RO |
0x06 (6dec) |
1406:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 7 |
OCTET-STRING[6] |
RO |
05 16 07 16 08 16 |
Index 0x1407 PTO RxPDO-Par Target compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1407:0 |
PTO RxPDO-Par Target compact Ch.2 |
PDO Parameter RxPDO 8 |
UINT8 |
RO |
0x06 (6dec) |
1407:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 8 |
OCTET-STRING[6] |
RO |
06 16 08 16 00 00 |
Index 0x1408 PTO RxPDO-Par Target Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1408:0 |
PTO RxPDO-Par Target Ch.2 |
PDO Parameter RxPDO 9 |
UINT8 |
RO |
0x06 (6dec) |
1408:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 9 |
OCTET-STRING[6] |
RO |
06 16 07 16 00 00 |
Index 0x1409 PTO RxPDO-Par Arrival Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1409:0 |
PTO RxPDO-Par Arrival Ch.2 |
PDO Parameter RxPDO 10 |
UINT8 |
RO |
0x06 (6dec) |
1409:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 10 |
OCTET-STRING[6] |
RO |
05 16 07 16 08 16 |
Index 0x140A ENC RxPDO-Par Control compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
140A:0 |
ENC RxPDO-Par Control compact Ch.1 |
PDO Parameter RxPDO 11 |
UINT8 |
RO |
0x06 (6dec) |
140A:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 11 |
OCTET-STRING[6] |
RO |
0B 16 00 00 00 00 |
Index 0x140B ENC RxPDO-Par Control Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
140B:0 |
ENC RxPDO-Par Control Ch.1 |
PDO Parameter RxPDO 12 |
UINT8 |
RO |
0x06 (6dec) |
140B:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 12 |
OCTET-STRING[6] |
RO |
0A 16 00 00 00 00 |
Index 0x140C ENC RxPDO-Par Control compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
140C:0 |
ENC RxPDO-Par Control compact Ch.2 |
PDO Parameter RxPDO 13 |
UINT8 |
RO |
0x06 (6dec) |
140C:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 13 |
OCTET-STRING[6] |
RO |
0D 16 00 00 00 00 |
Index 0x140D ENC RxPDO-Par Control Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
140D:0 |
ENC RxPDO-Par Control Ch.2 |
PDO Parameter RxPDO 14 |
UINT8 |
RO |
0x06 (6dec) |
140D:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index 0x of RxPDO mapping objects) that must not be transferred together with RxPDO 14 |
OCTET-STRING[6] |
RO |
0C 16 00 00 00 00 |
Index 0x1600 PTO RxPDO-Map Control Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1600:0 |
PTO RxPDO-Map Control Ch.1 |
PDO Mapping RxPDO 1 |
UINT8 |
RO |
0x05 (5dec) |
1600:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x01 (Frequency select)) |
UINT32 |
RO |
0x7000:01, 1 |
1600:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x02 (Disable ramp)) |
UINT32 |
RO |
0x7000:02, 1 |
1600:03 |
SubIndex 0x003 |
3. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x03 (Go counter)) |
UINT32 |
RO |
0x7000:03, 1 |
1600:04 |
SubIndex 0x004 |
4. PDO Mapping entry (13 bits align) |
UINT32 |
RO |
0x0000:00, 13 |
1600:05 |
SubIndex 0x005 |
5. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x11 (Frequency value)) |
UINT32 |
RO |
0x7000:11, 16 |
Index 0x1601 PTO RxPDO-Map Control Position Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1601:0 |
PTO RxPDO-Map Control Position Ch.1 |
PDO Mapping RxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1601:01 |
SubIndex 0x001 |
1. PDO Mapping entry (3 bits align) |
UINT32 |
RO |
0x0000:00, 3 |
1601:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x04 (Automatic direction)) |
UINT32 |
RO |
0x7000:04, 1 |
1601:03 |
SubIndex 0x003 |
3. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x05 (Forward)) |
UINT32 |
RO |
0x7000:05, 1 |
1601:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x06 (Reward)) |
UINT32 |
RO |
0x7000:06, 1 |
1601:05 |
SubIndex 0x005 |
5. PDO Mapping entry (10 bits align) |
UINT32 |
RO |
0x0000:00, 10 |
1601:06 |
SubIndex 0x006 |
6. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x12 (Target counter value)) |
UINT32 |
RO |
0x7000:12, 32 |
Index 0x1602 PTO RxPDO-Map Target compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1602:0 |
PTO RxPDO-Map Target compact Ch.1 |
PDO Mapping RxPDO 3 |
UINT8 |
RO |
0x01 (1dec) |
1602:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x7000 (PTO outputs Ch.1), entry 0x12 (Target counter value)) |
UINT32 |
RO |
0x7000:12, 16 |
Index 0x1603 PTO RxPDO-Map Target Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1603:0 |
PTO RxPDO-Map Target Ch.1 |
PDO Mapping RxPDO 4 |
UINT8 |
RO |
0x01 (1dec) |
1603:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x7000:12, 32 |
Index 0x1604 PTO RxPDO-Map Arrival Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1604:0 |
PTO RxPDO-Map Arrival Ch.1 |
PDO Mapping RxPDO 5 |
UINT8 |
RO |
0x01 (1dec) |
1604:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x7000 (PTO Outputs Ch.1), entry 0x13 (Target arrival time)) |
UINT32 |
RO |
0x7000:13, 64 |
Index 0x1605 PTO RxPDO-Map Control Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1605:0 |
PTO RxPDO-Map Control Ch.2 |
PDO Mapping RxPDO 6 |
UINT8 |
RO |
0x05 (5dec) |
1605:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x01 (Frequency select)) |
UINT32 |
RO |
0x7010:01, 1 |
1605:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x02 (Disable ramp)) |
UINT32 |
RO |
0x7010:02, 1 |
1605:03 |
SubIndex 0x003 |
3. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x03 (Go counter)) |
UINT32 |
RO |
0x7010:03, 1 |
1605:04 |
SubIndex 0x004 |
UINT32 |
RO |
0x0000:00, 13 |
1605:05 |
SubIndex 0x005 |
5. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x11 (Frequency value)) |
UINT32 |
RO |
0x7010:11, 16 |
Index 0x1606 PTO RxPDO-Map Control Position Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1606:0 |
PTO RxPDO-Map Control Position Ch.2 |
PDO Mapping RxPDO 7 |
UINT8 |
RO |
0x06 (6dec) |
1606:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 3 |
1606:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x04 (Automatic direction)) |
UINT32 |
RO |
0x7010:04, 1 |
1606:03 |
SubIndex 0x003 |
3. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x05 (Forward)) |
UINT32 |
RO |
0x7010:05, 1 |
1606:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x06 (Reward)) |
UINT32 |
RO |
0x7010:06, 1 |
1606:05 |
SubIndex 0x005 |
UINT32 |
RO |
0x0000:00, 10 |
1606:06 |
SubIndex 0x006 |
6. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x12 (Target counter value)) |
UINT32 |
RO |
0x7010:12, 32 |
Index 0x1607 PTO RxPDO-Map Target compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1607:0 |
PTO RxPDO-Map Target compact Ch.2 |
PDO Mapping RxPDO 8 |
UINT8 |
RO |
0x01 (1dec) |
1607:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x12 (Target counter value)) |
UINT32 |
RO |
0x7010:12, 16 |
Index 0x1608 PTO RxPDO-Map Target Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1608:0 |
PTO RxPDO-Map Target Ch.2 |
PDO Mapping RxPDO 9 |
UINT8 |
RO |
0x01 (1dec) |
1608:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x7010:12, 32 |
Index 0x1609 PTO RxPDO-Map Arrival Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1609:0 |
PTO RxPDO-Map Arrival Ch.2 |
PDO Mapping RxPDO 10 |
UINT8 |
RO |
0x01 (1dec) |
1609:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x7010 (PTO Outputs Ch.2), entry 0x13 (Target arrival time)) |
UINT32 |
RO |
0x7010:13, 64 |
Index 0x160A ENC RxPDO-Map Control compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
160A:0 |
ENC RxPDO-Map Control compact Ch.1 |
PDO Mapping RxPDO 11 |
UINT8 |
RO |
0x05 (5dec) |
160A:01 |
SubIndex 0x001 |
1. PDO Mapping entry (2 bits align) |
UINT32 |
RO |
0x0000:00, 2 |
160A:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x7020 (ENC Outputs Ch.1), entry 0x03 (Set counter)) |
UINT32 |
RO |
0x7020:03, 1 |
160A:03 |
SubIndex 0x003 |
3. PDO Mapping entry (12 bits align) |
UINT32 |
RO |
0x0000:00, 12 |
160A:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x7020 (ENC Outputs Ch.1), entry 0x10 (Reserved)) |
UINT32 |
RO |
0x7020:10, 1 |
160A:05 |
SubIndex 0x005 |
5. PDO Mapping entry (object 0x7020 (ENC Outputs Ch.1), entry 0x11 (Set counter value)) |
UINT32 |
RO |
0x7020:11, 16 |
Index 0x160B ENC RxPDO-Map Control Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
160B:0 |
ENC RxPDO-Map Control Ch.1 |
PDO Mapping RxPDO 12 |
UINT8 |
RO |
0x05 (5dec) |
160B:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 2 |
160B:02 |
SubIndex 0x002 |
UINT32 |
RO |
0x7020:03, 1 |
160B:03 |
SubIndex 0x003 |
UINT32 |
RO |
0x0000:00, 12 |
160B:04 |
SubIndex 0x004 |
UINT32 |
RO |
0x7020:10, 1 |
160B:05 |
SubIndex 0x005 |
UINT32 |
RO |
0x7020:11, 32 |
Index 0x160C ENC RxPDO-Map Control compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
160C:0 |
ENC RxPDO-Map Control compact Ch.2 |
PDO Mapping RxPDO 13 |
UINT8 |
RO |
0x05 (5dec) |
160C:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 2 |
160C:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x7030 (ENC Outputs Ch.2), entry 0x03 (Set counter)) |
UINT32 |
RO |
0x7030:03, 1 |
160C:03 |
SubIndex 0x003 |
UINT32 |
RO |
0x0000:00, 12 |
160C:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x7030 (ENC Outputs Ch.2), entry 0x10 (Reserved)) |
UINT32 |
RO |
0x7030:10, 1 |
160C:05 |
SubIndex 0x005 |
5. PDO Mapping entry (object 0x7030 (ENC Outputs Ch.2), entry 0x11 (Set counter value)) |
UINT32 |
RO |
0x7030:11, 16 |
Index 0x160D ENC RxPDO-Map Control Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
160D:0 |
ENC RxPDO-Map Control Ch.2 |
PDO Mapping RxPDO 14 |
UINT8 |
RO |
0x05 (5dec) |
160D:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 2 |
160D:02 |
SubIndex 0x002 |
UINT32 |
RO |
0x7030:03, 1 |
160D:03 |
SubIndex 0x003 |
UINT32 |
RO |
0x0000:00, 12 |
160D:04 |
SubIndex 0x004 |
UINT32 |
RO |
0x7030:10, 1 |
160D:05 |
SubIndex 0x005 |
UINT32 |
RO |
0x7030:11, 32 |
Index 0x1802 ENC TxPDO-Par Status compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1802:0 |
ENC TxPDO-Par Status compact Ch.1 |
PDO parameter TxPDO 3 |
UINT8 |
RO |
0x06 (6dec) |
1802:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index 0x of TxPDO mapping objects) that must not be transferred together with TxPDO 3 |
OCTET-STRING[2] |
RO |
03 1A |
Index 0x1803 ENC TxPDO-Par Status Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1803:0 |
ENC TxPDO-Par Status Ch.1 |
PDO parameter TxPDO 4 |
UINT8 |
RO |
0x06 (6dec) |
1803:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index 0x of TxPDO mapping objects) that must not be transferred together with TxPDO 4 |
OCTET-STRING[2] |
RO |
02 1A |
Index 0x1804 ENC TxPDO-Par Status compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1804:0 |
ENC TxPDO-Par Status compact Ch.2 |
PDO parameter TxPDO 5 |
UINT8 |
RO |
0x06 (6dec) |
1804:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index 0x of TxPDO mapping objects) that must not be transferred together with TxPDO 5 |
OCTET-STRING[2] |
RO |
05 1A |
Index 0x1805 ENC TxPDO-Par Status Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1805:0 |
ENC TxPDO-Par Status Ch.2 |
PDO parameter TxPDO 6 |
UINT8 |
RO |
0x06 (6dec) |
1805:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index 0x of TxPDO mapping objects) that must not be transferred together with TxPDO 6 |
OCTET-STRING[2] |
RO |
04 1A |
Index 0x1A00 PTO TxPDO-Map Status Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A00:0 |
PTO TxPDO-Map Status Ch.1 |
PDO Mapping TxPDO 1 |
UINT8 |
RO |
0x0A (10dec) |
1A00:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x6000 (PTO inputs Ch.1), entry 0x01 (Sel. Ack/End counter)) |
UINT32 |
RO |
0x6000:01, 1 |
1A00:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x6000 (PTO Inputs Ch.1), entry 0x02 (Ramp active)) |
UINT32 |
RO |
0x6000:02, 1 |
1A00:03 |
SubIndex 0x003 |
3. PDO Mapping entry (4 bits align) |
UINT32 |
RO |
0x0000:00, 4 |
1A00:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x6000 (PTO Inputs Ch.1), entry 0x07 (Error)) |
UINT32 |
RO |
0x6000:07, 1 |
1A00:05 |
SubIndex 0x005 |
5. PDO Mapping entry (6 bits align) |
UINT32 |
RO |
0x0000:00, 6 |
1A00:06 |
SubIndex 0x006 |
6. PDO Mapping entry (object 0x6000 (PTO Inputs Ch.1), entry 0x0E (Sync error)) |
UINT32 |
RO |
0x6000:0E, 1 |
1A00:07 |
SubIndex 0x007 |
7. PDO Mapping entry (1 bits align) |
UINT32 |
RO |
0x0000:00, 1 |
1A00:08 |
SubIndex 0x008 |
8. PDO Mapping entry (object 0x6000 (PTO Inputs Ch.1), entry 0x10 (TxPDO Toggle)) |
UINT32 |
RO |
0x6000:10, 1 |
1A00:09 |
SubIndex 0x009 |
9. PDO Mapping entry (object 0x6000 (PTO Inputs Ch.1), entry 0x11 ()) |
UINT32 |
RO |
0x6000:11, 1 |
1A00:0A |
SubIndex 0x010 |
10. PDO Mapping entry (15 bits align) |
UINT32 |
RO |
0x0000:00, 15 |
Index 0x1A01 PTO TxPDO-Map Status Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A01:0 |
PTO TxPDO-Map Status Ch.2 |
PDO Mapping TxPDO 2 |
UINT8 |
RO |
0x0A (10dec) |
1A01:01 |
SubIndex 0x001 |
1. PDO Mapping entry (object 0x6010 (PTO Inputs Ch.2), entry 0x01 (Sel. Ack/End counter)) |
UINT32 |
RO |
0x6010:01, 1 |
1A01:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x6010 (PTO Inputs Ch.2), entry 0x02 (Ramp active)) |
UINT32 |
RO |
0x6010:02, 1 |
1A01:03 |
SubIndex 0x003 |
UINT32 |
RO |
0x0000:00, 4 |
1A01:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x6010 (PTO Inputs Ch.2), entry 0x07 (Error)) |
UINT32 |
RO |
0x6010:07, 1 |
1A01:05 |
SubIndex 0x005 |
UINT32 |
RO |
0x0000:00, 6 |
1A01:06 |
SubIndex 0x006 |
6. PDO Mapping entry (object 0x6010 (PTO Inputs Ch.2), entry 0x0E (Sync error)) |
UINT32 |
RO |
0x6010:0E, 1 |
1A01:07 |
SubIndex 0x007 |
UINT32 |
RO |
0x0000:00, 1 |
1A01:08 |
SubIndex 0x008 |
8. PDO Mapping entry (object 0x6010 (PTO Inputs Ch.2), entry 0x10 (TxPDO Toggle)) |
UINT32 |
RO |
0x6010:10, 1 |
1A01:09 |
SubIndex 0x009 |
9. PDO Mapping entry (object 0x6010 (PTO Inputs Ch.2), entry 0x11 ()) |
UINT32 |
RO |
0x6010:11, 1 |
1A01:0A |
SubIndex 0x010 |
UINT32 |
RO |
0x0000:00, 15 |
Index 0x1A02 ENC TxPDO-Map Status compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A02:0 |
ENC TxPDO-Map Status compact Ch.1 |
PDO Mapping TxPDO 3 |
UINT8 |
RO |
0x09 (9dec) |
1A02:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 2 |
1A02:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x6020 (ENC Inputs Ch.1), entry 0x03 (Set counter done)) |
UINT32 |
RO |
0x6020:03, 1 |
1A02:03 |
SubIndex 0x003 |
3. PDO Mapping entry (object 0x6020 (ENC Inputs Ch.1), entry 0x04 (Counter underflow)) |
UINT32 |
RO |
0x6020:04, 1 |
1A02:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x6020 (ENC Inputs Ch.1), entry 0x05 (Counter overflow)) |
UINT32 |
RO |
0x6020:05, 1 |
1A02:05 |
SubIndex 0x005 |
5. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
1A02:06 |
SubIndex 0x006 |
6. PDO Mapping entry (object 0x6020 (ENC Inputs Ch.1), entry 0x0E (Sync error)) |
UINT32 |
RO |
0x6020:0E, 1 |
1A02:07 |
SubIndex 0x007 |
7. PDO Mapping entry (object 0x6020 (ENC Inputs Ch.1), entry 0x0F (TxPDO State)) |
UINT32 |
RO |
0x6020:0F, 1 |
1A02:08 |
SubIndex 0x008 |
8. PDO Mapping entry (object 0x6020 (ENC Inputs Ch.1), entry 0x10 (TxPDO Toggle)) |
UINT32 |
RO |
0x6020:10, 1 |
1A02:09 |
SubIndex 0x009 |
9. PDO Mapping entry (object 0x6020 (ENC Inputs Ch.1), entry 0x11 (Counter value)) |
UINT32 |
RO |
0x6020:11, 16 |
Index 0x1A03 ENC TxPDO-Map Status Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A03:0 |
ENC TxPDO-Map Status Ch.1 |
PDO Mapping TxPDO 4 |
UINT8 |
RO |
0x09 (9dec) |
1A03:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 2 |
1A03:02 |
SubIndex 0x002 |
UINT32 |
RO |
0x6020:03, 1 |
1A03:03 |
SubIndex 0x003 |
UINT32 |
RO |
0x6020:04, 1 |
1A03:04 |
SubIndex 0x004 |
UINT32 |
RO |
0x6020:05, 1 |
1A03:05 |
SubIndex 0x005 |
UINT32 |
RO |
0x0000:00, 8 |
1A03:06 |
SubIndex 0x006 |
UINT32 |
RO |
0x6020:0E, 1 |
1A03:07 |
SubIndex 0x007 |
UINT32 |
RO |
0x6020:0F, 1 |
1A03:08 |
SubIndex 0x008 |
UINT32 |
RO |
0x6020:10, 1 |
1A03:09 |
SubIndex 0x009 |
UINT32 |
RO |
0x6020:11, 32 |
Index 0x1A04 ENC TxPDO-Map Status compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A04:0 |
ENC TxPDO-Map Status compact Ch.2 |
PDO Mapping TxPDO 5 |
UINT8 |
RO |
0x09 (9dec) |
1A04:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 2 |
1A04:02 |
SubIndex 0x002 |
2. PDO Mapping entry (object 0x6030 (ENC Inputs Ch.2), entry 0x03 (Set counter done)) |
UINT32 |
RO |
0x6030:03, 1 |
1A04:03 |
SubIndex 0x003 |
3. PDO Mapping entry (object 0x6030 (ENC Inputs Ch.2), entry 0x04 (Counter underflow)) |
UINT32 |
RO |
0x6030:04, 1 |
1A04:04 |
SubIndex 0x004 |
4. PDO Mapping entry (object 0x6030 (ENC Inputs Ch.2), entry 0x05 (Counter overflow)) |
UINT32 |
RO |
0x6030:05, 1 |
1A04:05 |
SubIndex 0x005 |
UINT32 |
RO |
0x0000:00, 8 |
1A04:06 |
SubIndex 0x006 |
6. PDO Mapping entry (object 0x6030 (ENC Inputs Ch.2), entry 0x0E (Sync error)) |
UINT32 |
RO |
0x6030:0E, 1 |
1A04:07 |
SubIndex 0x007 |
7. PDO Mapping entry (object 0x6030 (ENC Inputs Ch.2), entry 0x0F (TxPDO State)) |
UINT32 |
RO |
0x6030:0F, 1 |
1A04:08 |
SubIndex 0x008 |
8. PDO Mapping entry (object 0x6030 (ENC Inputs Ch.2), entry 0x10 (TxPDO Toggle)) |
UINT32 |
RO |
0x6030:10, 1 |
1A04:09 |
SubIndex 0x009 |
9. PDO Mapping entry (object 0x6030 (ENC Inputs Ch.2), entry 0x11 (Counter value)) |
UINT32 |
RO |
0x6030:11, 16 |
Index 0x1A05 ENC TxPDO-Map Status Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A05:0 |
ENC TxPDO-Map Status Ch.2 |
PDO Mapping TxPDO 6 |
UINT8 |
RO |
0x09 (9dec) |
1A05:01 |
SubIndex 0x001 |
UINT32 |
RO |
0x0000:00, 2 |
1A05:02 |
SubIndex 0x002 |
UINT32 |
RO |
0x6030:03, 1 |
1A05:03 |
SubIndex 0x003 |
UINT32 |
RO |
0x6030:04, 1 |
1A05:04 |
SubIndex 0x004 |
UINT32 |
RO |
0x6030:05, 1 |
1A05:05 |
SubIndex 0x005 |
UINT32 |
RO |
0x0000:00, 8 |
1A05:06 |
SubIndex 0x006 |
UINT32 |
RO |
0x6030:0E, 1 |
1A05:07 |
SubIndex 0x007 |
UINT32 |
RO |
0x6030:0F, 1 |
1A05:08 |
SubIndex 0x008 |
UINT32 |
RO |
0x6030:10, 1 |
1A05:09 |
SubIndex 0x009 |
UINT32 |
RO |
0x6030:11, 32 |
Index 0x1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the Sync Managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 0x1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x06 (6dec) |
1C12:01 |
Subindex 001 |
1. allocated RxPDO (contains the index 0x of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1600 (5632dec) |
1C12:02 |
Subindex 002 |
2. allocated RxPDO (contains the index 0x of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1603 (5635dec) |
1C12:03 |
Subindex 003 |
3. allocated RxPDO (contains the index 0x of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1605 (5637dec) |
1C12:04 |
Subindex 004 |
4. allocated RxPDO (contains the index 0x of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1608 (5640dec) |
1C12:05 |
Subindex 005 |
5. allocated RxPDO (contains the index 0x of the associated RxPDO mapping object) |
UINT16 |
RW |
0x160B (5643dec) |
1C12:06 |
Subindex 006 |
6. allocated RxPDO (contains the index 0x of the associated RxPDO mapping object) |
UINT16 |
RW |
0x160D (5645dec) |
Index 0x1C13 TxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C13:0 |
TxPDO assign |
PDO Assign Inputs |
UINT8 |
RW |
0x04 (4dec) |
1C13:01 |
Subindex 001 |
1. allocated TxPDO (contains the index 0x of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A00 (6656dec) |
1C13:02 |
Subindex 002 |
2. allocated TxPDO (contains the index 0x of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A01 (6657dec) |
1C13:03 |
Subindex 003 |
3. allocated TxPDO (contains the index 0x of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A03 (6659dec) |
1C13:04 |
Subindex 004 |
4. allocated TxPDO (contains the index 0x of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A05 (6661dec) |
Index 0x1C32 SM output parameter
1C32:0 | SM output parameter | Synchronization parameters for the outputs | UINT8 | RO | 0x20 (32dec) |
1C32:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0001 (1dec) |
1C32:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x000F4240 (1000000dec) |
1C32:03 | Shift time | Time between SYNC0 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0x4C07 (19463dec) |
1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x000186A0 (100000dec) |
1C32:06 | Calc and copy time | Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:07 | Minimum delay time |
1C32:08 | Command |
The entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C32:09 | Maximum delay time | Time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 0x1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | as 0x1C32:02 | UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
1C33:05 | Minimum cycle time | as 0x1C32:05 | UINT32 | RO | 0x000186A0 (100000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Command | as 0x1C32:08 | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | as 0x1C32:11 | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | as 0x1C32:12 | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | as 0x1C32:13 | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | as 0x1C32:32 | BOOLEAN | RO | 0x00 (0dec) |