Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 0x1000 Device type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1000:0 |
Device type |
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. |
UINT32 |
RO |
0x00001389 (5001dec) |
Index 0x1008 Device name
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
STRING |
RO |
EL2521 |
Index 0x1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
05 |
Index 0x100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
06 |
Index 0x1018 Identity
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1018:0 |
Identity |
Information for identifying the slave |
UINT8 |
RO |
0x04 (4dec) |
1018:01 |
Vendor ID |
Vendor ID of the EtherCAT slave |
UINT32 |
RO |
0x00000002 (2dec) |
1018:02 |
Product code |
Product code of the EtherCAT slave |
UINT32 |
RO |
0x09D93052 (165228626dec) |
1018:03 |
Revision |
Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description |
UINT32 |
RO |
0x03F80000 (66584576dec) |
1018:04 |
Serial number |
Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0 |
UINT32 |
RO |
0x00000000 (0dec) |
Index 0x10F0 Backup parameter handling
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardized loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum across all backup entries of the EtherCAT slave |
UINT32 |
RO |
0x00000000 (0dec) |
Index 0x1400 RxPDO-Par
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1400:0 |
RxPDO-Par |
PDO Parameter RxPDO 1 |
UINT8 |
RO |
0x06 (6dec) |
1400:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 1 |
OCTET-STRING[10] |
RO |
01 16 04 16 07 16 02 16 05 16 |
Index 0x1401 PTO RxPDO-Par Control
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1401:0 |
PTO RxPDO-Par Control |
PDO Parameter RxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1401:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 2 |
OCTET-STRING[10] |
RO |
00 16 00 00 00 00 00 00 00 00 |
Index 0x1402 ENC RxPDO-Par Control compact
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1402:0 |
ENC RxPDO-Par Control compact |
PDO Parameter RxPDO 3 |
UINT8 |
RO |
0x06 (6dec) |
1402:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 3 |
OCTET-STRING[10] |
RO |
00 16 05 16 07 16 00 00 00 00 |
Index 0x1404 PTO RxPDO-Par Target compact
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1404:0 |
PTO RxPDO-Par Target compact |
PDO Parameter RxPDO 5 |
UINT8 |
RO |
0x06 (6dec) |
1404:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 5 |
OCTET-STRING[10] |
RO |
Index 0x1405 ENC RxPDO-Par Control
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1405:0 |
ENC RxPDO-Par Control |
PDO Parameter RxPDO 6 |
UINT8 |
RO |
0x06 (6dec) |
1405:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 6 |
OCTET-STRING[10] |
RO |
00 16 02 16 04 16 00 00 00 00 |
Index 0x1407 PTO RxPDO-Par Target
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1407:0 |
PTO RxPDO-Par Target |
PDO Parameter RxPDO 8 |
UINT8 |
RO |
0x06 (6dec) |
1407:06 |
Exclude RxPDOs |
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 8 |
OCTET-STRING[10] |
RO |
Index 0x1600 RxPDO-Map
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1600:0 |
RxPDO-Map |
PDO Mapping RxPDO 1 |
UINT8 |
RO |
0x02 (2dec) |
1600:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7000 (Outputs), entry 0x01 (Ctrl)) |
UINT32 |
RO |
0x7000:01, 16 |
1600:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7000 (Outputs), entry 0x02 (Data Out)) |
UINT32 |
RO |
0x7000:02, 16 |
Index 0x1601 PTO RxPDO-Map Control
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1601:0 |
PTO RxPDO-Map Control |
PDO Mapping RxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1601:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x01 (Frequency select)) |
UINT32 |
RO |
0x7010:01, 1 |
1601:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x02 (Disable ramp)) |
UINT32 |
RO |
0x7010:02, 1 |
1601:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x03 (Go counter)) |
UINT32 |
RO |
0x7010:03, 1 |
1601:04 |
SubIndex 004 |
4. PDO Mapping entry (5 bits align) |
UINT32 |
RO |
0x0000:00, 5 |
1601:05 |
SubIndex 005 |
5. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
1601:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x11 (Frequency value)) |
UINT32 |
RO |
0x7010:11, 16 |
Index 0x1602 ENC RxPDO-Map Control compact
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1602:0 |
ENC RxPDO-Map Control compact |
PDO Mapping RxPDO 3 |
UINT8 |
RO |
0x05 (5dec) |
1602:01 |
SubIndex 001 |
1. PDO Mapping entry (2 bits align) |
UINT32 |
RO |
0x0000:00, 2 |
1602:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x7020 (ENC Outputs), entry 0x03 (Set counter)) |
UINT32 |
RO |
0x7020:03, 1 |
1602:03 |
SubIndex 003 |
3. PDO Mapping entry (5 bits align) |
UINT32 |
RO |
0x0000:00, 5 |
1602:04 |
SubIndex 004 |
4. PDO Mapping entry (8 bits align) |
UINT32 |
RO |
0x0000:00, 8 |
1602:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x7020 (ENC Outputs), entry 0x11 (Set counter value)) |
UINT32 |
RO |
0x7020:11, 16 |
Index 0x1604 PTO RxPDO-Map Target compact
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1604:0 |
PTO RxPDO-Map Target compact |
PDO Mapping RxPDO 5 |
UINT8 |
RO |
0x01 (1dec) |
1604:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x12 (Target counter value)) |
UINT32 |
RO |
0x7010:12, 16 |
Index 0x1605 ENC RxPDO-Map Control
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1605:0 |
ENC RxPDO-Map Control |
PDO Mapping RxPDO 6 |
UINT8 |
RO |
0x05 (5dec) |
1605:01 |
SubIndex 001 |
UINT32 |
RO |
0x0000:00, 2 |
1605:02 |
SubIndex 002 |
UINT32 |
RO |
0x7020:03, 1 |
1605:03 |
SubIndex 003 |
UINT32 |
RO |
0x0000:00, 5 |
1605:04 |
SubIndex 004 |
UINT32 |
RO |
0x0000:00, 8 |
1605:05 |
SubIndex 005 |
UINT32 |
RO |
0x7020:11, 32 |
Index 0x1607 PTO RxPDO-Map Target
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1607:0 |
PTO RxPDO-Map Target |
PDO Mapping RxPDO 8 |
UINT8 |
RO |
0x01 (1dec) |
1607:01 |
SubIndex 001 |
UINT32 |
RO |
0x7010:12, 32 |
Index 0x1800 TxPDO-Par
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1800:0 |
TxPDO-Par |
PDO parameter TxPDO 1 |
UINT8 |
RO |
0x06 (6dec) |
1800:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 1 |
OCTET-STRING[6] |
RO |
01 1A 02 1A 05 1A |
Index 0x1801 PTO TxPDO-Par Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1801:0 |
PTO TxPDO-Par Status |
PDO parameter TxPDO 2 |
UINT8 |
RO |
0x09 (9dec) |
1801:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 2 |
OCTET-STRING[6] |
RO |
00 1A 00 00 00 00 |
1801:09 |
TxPDO Toggle |
The TxPDO toggle is toggled with each update the corresponding input data |
BOOLEAN |
RO |
0x00 (0dec) |
Index 0x1802 ENC TxPDO-Par Status compact
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1802:0 |
ENC TxPDO-Par Status compact |
PDO parameter TxPDO 3 |
UINT8 |
RO |
0x09 (9dec) |
1802:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 3 |
OCTET-STRING[6] |
RO |
05 1A 00 1A 00 00 |
1802:09 |
TxPDO Toggle |
BOOLEAN |
RO |
0x00 (0dec) |
Index 0x1805 ENC TxPDO-Par Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1805:0 |
ENC TxPDO-Par Status |
PDO parameter TxPDO 6 |
UINT8 |
RO |
0x09 (9dec) |
1805:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 6 |
OCTET-STRING[6] |
RO |
02 1A 00 1A 00 00 |
1805:09 |
TxPDO Toggle |
BOOLEAN |
RO |
0x00 (0dec) |
Index 0x1A00 TxPDO-Map
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A00:0 |
TxPDO-Map |
PDO Mapping TxPDO 1 |
UINT8 |
RO |
0x02 (2dec) |
1A00:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6000 (Inputs), entry 0x01 (Status)) |
UINT32 |
RO |
0x6000:01, 16 |
1A00:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6000 (Inputs), entry 0x02 (Data In)) |
UINT32 |
RO |
0x6000:02, 16 |
Index 0x1A01 PTO TxPDO-Map Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A01:0 |
PTO TxPDO-Map Status |
PDO Mapping TxPDO 2 |
UINT8 |
RO |
0x0A (10dec) |
1A01:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x01 (Sel. Ack/End counter)) |
UINT32 |
RO |
0x6010:01, 1 |
1A01:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x02 (Ramp active)) |
UINT32 |
RO |
0x6010:02, 1 |
1A01:03 |
SubIndex 003 |
3. PDO Mapping entry (2 bits align) |
UINT32 |
RO |
0x0000:00, 2 |
1A01:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x05 (Status of input target)) |
UINT32 |
RO |
0x6010:05, 1 |
1A01:05 |
SubIndex 005 |
5. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x06 (Status of input zero)) |
UINT32 |
RO |
0x6010:06, 1 |
1A01:06 |
SubIndex 006 |
6. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x07 (Error)) |
UINT32 |
RO |
0x6010:07, 1 |
1A01:07 |
SubIndex 007 |
7. PDO Mapping entry (6 bits align) |
UINT32 |
RO |
0x0000:00, 6 |
1A01:08 |
SubIndex 008 |
8. PDO Mapping entry (object 0x1C32 (SM output parameter), entry 0x20 (Sync error)) |
UINT32 |
RO |
0x1C32:20, 1 |
1A01:09 |
SubIndex 009 |
9. PDO Mapping entry (1 bits align) |
UINT32 |
RO |
0x0000:00, 1 |
1A01:0A |
SubIndex 010 |
10. PDO Mapping entry (object 0x1801 (PTO TxPDO-Par Status), entry 0x09 (TxPDO-Toggle)) |
UINT32 |
RO |
0x1801:09, 1 |
Index 0x1A02 ENC TxPDO-Map Status compact
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A02:0 |
ENC TxPDO-Map Status compact |
PDO Mapping TxPDO 3 |
UINT8 |
RO |
0x0A (10dec) |
1A02:01 |
SubIndex 001 |
UINT32 |
RO |
0x0000:00, 2 |
1A02:02 |
SubIndex 002 |
2. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x03 (Set counter done)) |
UINT32 |
RO |
0x6020:03, 1 |
1A02:03 |
SubIndex 003 |
3. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x04 (Counter underflow)) |
UINT32 |
RO |
0x6020:04, 1 |
1A02:04 |
SubIndex 004 |
4. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x05 (Counter overflow)) |
UINT32 |
RO |
0x6020:05, 1 |
1A02:05 |
SubIndex 005 |
5. PDO Mapping entry (3 bits align) |
UINT32 |
RO |
0x0000:00, 3 |
1A02:06 |
SubIndex 006 |
6. PDO Mapping entry (5 bits align) |
UINT32 |
RO |
0x0000:00, 5 |
1A02:07 |
SubIndex 007 |
7. PDO Mapping entry (object 0x1C32 (SM output parameter), entry 0x20 (Sync error)) |
UINT32 |
RO |
0x1C32:20, 1 |
1A02:08 |
SubIndex 008 |
8. PDO Mapping entry (1 bits align) |
UINT32 |
RO |
0x0000:00, 1 |
1A02:09 |
SubIndex 009 |
9. PDO Mapping entry (object 0x1802 (ENC TxPDO-Par Status compact), entry 0x09 (TxPDO-Toggle)) |
UINT32 |
RO |
0x1802:09, 1 |
1A02:0A |
SubIndex 010 |
10. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x11 (Counter value)) |
UINT32 |
RO |
0x6020:11, 16 |
Index 0x1A05 ENC TxPDO-Map Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A05:0 |
ENC TxPDO-Map Status |
PDO Mapping TxPDO 6 |
UINT8 |
RO |
0x0A (10dec) |
1A05:01 |
SubIndex 001 |
UINT32 |
RO |
0x0000:00, 2 |
1A05:02 |
SubIndex 002 |
UINT32 |
RO |
0x6020:03, 1 |
1A05:03 |
SubIndex 003 |
UINT32 |
RO |
0x6020:04, 1 |
1A05:04 |
SubIndex 004 |
UINT32 |
RO |
0x6020:05, 1 |
1A05:05 |
SubIndex 005 |
UINT32 |
RO |
0x0000:00, 3 |
1A05:06 |
SubIndex 006 |
UINT32 |
RO |
0x0000:00, 5 |
1A05:07 |
SubIndex 007 |
UINT32 |
RO |
0x1C32:20, 1 |
1A05:08 |
SubIndex 008 |
UINT32 |
RO |
0x0000:00, 1 |
1A05:09 |
SubIndex 009 |
9. PDO Mapping entry (object 0x1805 (ENC TxPDO-Par Status), entry 0x09 (TxPDO-Toggle)) |
UINT32 |
RO |
0x1805:09, 1 |
1A05:0A |
SubIndex 010 |
UINT32 |
RO |
0x6020:11, 32 |
Index 0x1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the Sync Managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 0x1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x01 (1dec) |
1C12:01 |
SubIndex 001 |
1. allocated RxPDO (contains the index (hex) of the associated RxPDO mapping object) |
UINT16 |
RW |
0x1600 (5632dec) |
1C12:02 |
SubIndex 002 |
2. allocated RxPDO (contains the index (hex) of the associated RxPDO mapping object) |
UINT16 |
RW |
0x0000 (0dec) |
1C12:03 |
SubIndex 003 |
3. allocated RxPDO (contains the index (hex) of the associated RxPDO mapping object) |
UINT16 |
RW |
0x0000 (0dec) |
Index 0x1C13 TxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C13:0 |
TxPDO assign |
PDO Assign Inputs |
UINT8 |
RW |
0x01 (1dec) |
1C13:01 |
SubIndex 001 |
1. allocated TxPDO (contains the index (hex) of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A00 (6656dec) |
1C13:02 |
SubIndex 002 |
2. allocated TxPDO (contains the index (hex) of the associated TxPDO mapping object) |
UINT16 |
RW |
0x0000 (0dec) |
Index 0x1C32 SM output parameter
1C32:0 | SM output parameter | Synchronization parameters for the outputs | UINT8 | RO | 0x20 (32dec) |
1C32:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0001 (1dec) |
1C32:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x001E8480 (2000000dec) |
1C32:03 | Shift time | Time between SYNC0 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0xC007 (49159dec) |
1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00000000 (0dec) |
1C32:06 | Calc and copy time | Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:08 | Command |
The entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C32:09 | Delay time | Time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 0x1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | as 0x1C32:02 | UINT32 | RW | 0x001E8480 (2000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
1C33:05 | Minimum cycle time | as 0x1C32:05 | UINT32 | RO | 0x00000000 (0dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:08 | Command | as 0x1C32:08 | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | as 0x1C32:11 | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | as 0x1C32:12 | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | as 0x1C32:13 | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | as 0x1C32:32 | BOOLEAN | RO | 0x00 (0dec) |