Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 0x1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave:
  • The Low-Word contains the CoE profile used (5001).
  • The high word contains the module profile according to the modular device profile.
UINT32
RO
0x00001389 (5001dec)
Index 0x1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EL2521
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
00
Index 0x1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x09D93052 (165228626dec)
1018:03
Revision
Revision number of the EtherCAT slave:
  • The Low Word (bit 0–15) indicates the special terminal number.
  • The High Word (bit 16–31) refers to the device description.
UINT32
RO
0x03F80000 (66584576dec)
1018:04
Serial number
Serial number of the EtherCAT slave:
  • Low Word
    • The Low Byte (bit 0–7) of the Low Word contains the year of production.
    • The High Byte (bit 8–15) of the Low Word contains the week of production.
  • The High Word (bit 16–31) is 0.
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 0x1400 RxPDO-Par
Index (hex)
Meaning
Data type
Flags
Default
1400:0
RxPDO-Par
PDO Parameter RxPDO 1
UINT8
RO
0x06 (6dec)
1400:06
Exclude RxPDOs
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 1.
OCTET-STRING[10]
RO
01 16 04 16 07 16 02 16 05 16
Index 0x1401 PTO RxPDO-Par Control
Index (hex)
Meaning
Data type
Flags
Default
1401:0
PDO Parameter RxPDO 2
UINT8
RO
0x06 (6dec)
1401:06
Exclude RxPDOs
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 2.
OCTET-STRING[10]
RO
00 16 00 00 00 00 00 00 00 00
Index 0x1402 ENC RxPDO-Par Control compact
Index (hex)
Meaning
Data type
Flags
Default
1402:0
PDO Parameter RxPDO 3
UINT8
RO
0x06 (6dec)
1402:06
Exclude RxPDOs
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 3.
OCTET-STRING[10]
RO
00 16 05 16 07 16 00 00 00 00
Index 0x1404 PTO RxPDO-Par Target compact
Index (hex)
Meaning
Data type
Flags
Default
1404:0
PDO Parameter RxPDO 5
UINT8
RO
0x06 (6dec)
1404:06
Exclude RxPDOs
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 5.
OCTET-STRING[10]
RO
Index 0x1405 ENC RxPDO-Par Control
Index (hex)
Meaning
Data type
Flags
Default
1405:0
PDO Parameter RxPDO 6
UINT8
RO
0x06 (6dec)
1405:06
Exclude RxPDOs
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 6.
OCTET-STRING[10]
RO
00 16 02 16 04 16 00 00 00 00
Index 0x1407 PTO RxPDO-Par Target
Index (hex)
Meaning
Data type
Flags
Default
1407:0
PDO Parameter RxPDO 8
UINT8
RO
0x06 (6dec)
1407:06
Exclude RxPDOs
Specifies the RxPDOs (index (hex) of RxPDO mapping objects) that must not be transferred together with RxPDO 8.
OCTET-STRING[10]
RO
Index 0x1600 RxPDO-Map
Index (hex)
Meaning
Data type
Flags
Default
1600:0
RxPDO-Map
PDO Mapping RxPDO 1
UINT8
RO
0x02 (2dec)
1600:01
SubIndex 001
1. PDO Mapping entry (object 0x7000 (Outputs), entry 0x01 (Ctrl))
UINT32
RO
0x7000:01, 16
1600:02
SubIndex 002
2. PDO Mapping entry (object 0x7000 (Outputs), entry 0x02 (Data Out))
UINT32
RO
0x7000:02, 16
Index 0x1601 PTO RxPDO-Map Control
Index (hex)
Meaning
Data type
Flags
Default
1601:0
PDO Mapping RxPDO 2
UINT8
RO
0x06 (6dec)
1601:01
SubIndex 001
1. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x01 (Frequency select))
UINT32
RO
0x7010:01, 1
1601:02
SubIndex 002
2. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x02 (Disable ramp))
UINT32
RO
0x7010:02, 1
1601:03
SubIndex 003
3. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x03 (Go counter))
UINT32
RO
0x7010:03, 1
1601:04
SubIndex 004
4. PDO Mapping entry (5 bits align)
UINT32
RO
0x0000:00, 5
1601:05
SubIndex 005
5. PDO Mapping entry (8 bits align)
UINT32
RO
0x0000:00, 8
1601:06
SubIndex 006
6. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x11 (Frequency value))
UINT32
RO
0x7010:11, 16
Index 0x1602 ENC RxPDO-Map Control compact
Index (hex)
Meaning
Data type
Flags
Default
1602:0
PDO Mapping RxPDO 3
UINT8
RO
0x05 (5dec)
1602:01
SubIndex 001
1. PDO Mapping entry (2 bits align)
UINT32
RO
0x0000:00, 2
1602:02
SubIndex 002
2. PDO Mapping entry (object 0x7020 (ENC Outputs), entry 0x03 (Set counter))
UINT32
RO
0x7020:03, 1
1602:03
SubIndex 003
3. PDO Mapping entry (5 bits align)
UINT32
RO
0x0000:00, 5
1602:04
SubIndex 004
4. PDO Mapping entry (8 bits align)
UINT32
RO
0x0000:00, 8
1602:05
SubIndex 005
5. PDO Mapping entry (object 0x7020 (ENC Outputs), entry 0x11 (Set counter value))
UINT32
RO
0x7020:11, 16
Index 0x1604 PTO RxPDO-Map Target compact
Index (hex)
Meaning
Data type
Flags
Default
1604:0
PDO Mapping RxPDO 5
UINT8
RO
0x01 (1dec)
1604:01
SubIndex 001
1. PDO Mapping entry (object 0x7010 (PTO Outputs), entry 0x12 (Target counter value))
UINT32
RO
0x7010:12, 16
Index 0x1605 ENC RxPDO-Map Control
Index (hex)
Meaning
Data type
Flags
Default
1605:0
PDO Mapping RxPDO 6
UINT8
RO
0x05 (5dec)
1605:01
SubIndex 001
UINT32
RO
0x0000:00, 2
1605:02
SubIndex 002
UINT32
RO
0x7020:03, 1
1605:03
SubIndex 003
UINT32
RO
0x0000:00, 5
1605:04
SubIndex 004
UINT32
RO
0x0000:00, 8
1605:05
SubIndex 005
UINT32
RO
0x7020:11, 32
Index 0x1607 PTO RxPDO-Map Target
Index (hex)
Meaning
Data type
Flags
Default
1607:0
PDO Mapping RxPDO 8
UINT8
RO
0x01 (1dec)
1607:01
SubIndex 001
UINT32
RO
0x7010:12, 32
Index 0x1800 TxPDO-Par
Index (hex)
Meaning
Data type
Flags
Default
1800:0
TxPDO-Par
PDO parameter TxPDO 1
UINT8
RO
0x06 (6dec)
1800:06
Exclude TxPDOs
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 1.
OCTET-STRING[6]
RO
01 1A 02 1A 05 1A
Index 0x1801 PTO TxPDO-Par Status
Index (hex)
Meaning
Data type
Flags
Default
1801:0
PDO parameter TxPDO 2
UINT8
RO
0x09 (9dec)
1801:06
Exclude TxPDOs
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 2.
OCTET-STRING[6]
RO
00 1A 00 00 00 00
1801:09
TxPDO Toggle
The TxPDO toggle is toggled with each update the corresponding input data.
BOOLEAN
RO
0x00 (0dec)
Index 0x1802 ENC TxPDO-Par Status compact
Index (hex)
Meaning
Data type
Flags
Default
1802:0
PDO parameter TxPDO 3
UINT8
RO
0x09 (9dec)
1802:06
Exclude TxPDOs
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 3.
OCTET-STRING[6]
RO
05 1A 00 1A 00 00
1802:09
TxPDO Toggle
BOOLEAN
RO
0x00 (0dec)
Index 0x1805 ENC TxPDO-Par Status
Index (hex)
Meaning
Data type
Flags
Default
1805:0
PDO parameter TxPDO 6
UINT8
RO
0x09 (9dec)
1805:06
Exclude TxPDOs
Specifies the TxPDOs (index (hex) of TxPDO mapping objects) that must not be transferred together with TxPDO 6.
OCTET-STRING[6]
RO
02 1A 00 1A 00 00
1805:09
TxPDO Toggle
BOOLEAN
RO
0x00 (0dec)
Index 0x1A00 TxPDO-Map
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
TxPDO-Map
PDO Mapping TxPDO 1
UINT8
RO
0x02 (2dec)
1A00:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (Inputs), entry 0x01 (Status))
UINT32
RO
0x6000:01, 16
1A00:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (Inputs), entry 0x02 (Data In))
UINT32
RO
0x6000:02, 16
Index 0x1A01 PTO TxPDO-Map Status
Index (hex)
Meaning
Data type
Flags
Default
1A01:0
PDO Mapping TxPDO 2
UINT8
RO
0x0A (10dec)
1A01:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x01 (Sel. Ack/End counter))
UINT32
RO
0x6010:01, 1
1A01:02
SubIndex 002
2. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x02 (Ramp active))
UINT32
RO
0x6010:02, 1
1A01:03
SubIndex 003
3. PDO Mapping entry (2 bits align)
UINT32
RO
0x0000:00, 2
1A01:04
SubIndex 004
4. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x05 (Status of input target))
UINT32
RO
0x6010:05, 1
1A01:05
SubIndex 005
5. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x06 (Status of input zero))
UINT32
RO
0x6010:06, 1
1A01:06
SubIndex 006
6. PDO Mapping entry (object 0x6010 (PTO Inputs), entry 0x07 (Error))
UINT32
RO
0x6010:07, 1
1A01:07
SubIndex 007
7. PDO Mapping entry (6 bits align)
UINT32
RO
0x0000:00, 6
1A01:08
SubIndex 008
8. PDO Mapping entry (object 0x1C32 (SM output parameter), entry 0x20 (Sync error))
UINT32
RO
0x1C32:20, 1
1A01:09
SubIndex 009
9. PDO Mapping entry (1 bits align)
UINT32
RO
0x0000:00, 1
1A01:0A
SubIndex 010
10. PDO Mapping entry (object 0x1801 (PTO TxPDO‑Par Status), entry 0x09 (TxPDO‑Toggle))
UINT32
RO
0x1801:09, 1
Index 0x1A02 ENC TxPDO-Map Status compact
Index (hex)
Meaning
Data type
Flags
Default
1A02:0
PDO Mapping TxPDO 3
UINT8
RO
0x0A (10dec)
1A02:01
SubIndex 001
UINT32
RO
0x0000:00, 2
1A02:02
SubIndex 002
2. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x03 (Set counter done))
UINT32
RO
0x6020:03, 1
1A02:03
SubIndex 003
3. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x04 (Counter underflow))
UINT32
RO
0x6020:04, 1
1A02:04
SubIndex 004
4. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x05 (Counter overflow))
UINT32
RO
0x6020:05, 1
1A02:05
SubIndex 005
5. PDO Mapping entry (3 bits align)
UINT32
RO
0x0000:00, 3
1A02:06
SubIndex 006
6. PDO Mapping entry (5 bits align)
UINT32
RO
0x0000:00, 5
1A02:07
SubIndex 007
7. PDO Mapping entry (object 0x1C32 (SM output parameter), entry 0x20 (Sync error))
UINT32
RO
0x1C32:20, 1
1A02:08
SubIndex 008
8. PDO Mapping entry (1 bit align)
UINT32
RO
0x0000:00, 1
1A02:09
SubIndex 009
9. PDO Mapping entry (object 0x1802 (ENC TxPDO‑Par Status compact), entry 0x09 (TxPDO‑Toggle))
UINT32
RO
0x1802:09, 1
1A02:0A
SubIndex 010
10. PDO Mapping entry (object 0x6020 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6020:11, 16
Index 0x1A05 ENC TxPDO-Map Status
Index (hex)
Meaning
Data type
Flags
Default
1A05:0
PDO Mapping TxPDO 6
UINT8
RO
0x0A (10dec)
1A05:01
SubIndex 001
UINT32
RO
0x0000:00, 2
1A05:02
SubIndex 002
UINT32
RO
0x6020:03, 1
1A05:03
SubIndex 003
UINT32
RO
0x6020:04, 1
1A05:04
SubIndex 004
UINT32
RO
0x6020:05, 1
1A05:05
SubIndex 005
UINT32
RO
0x0000:00, 3
1A05:06
SubIndex 006
UINT32
RO
0x0000:00, 5
1A05:07
SubIndex 007
UINT32
RO
0x1C32:20, 1
1A05:08
SubIndex 008
8. PDO Mapping entry (1 bits align)
UINT32
RO
0x0000:00, 1
1A05:09
SubIndex 009
9. PDO Mapping entry (object 0x1805 (ENC TxPDO‑Par Status), entry 0x09 (TxPDO‑Toggle))
UINT32
RO
0x1805:09, 1
1A05:0A
SubIndex 010
UINT32
RO
0x6020:11, 32
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the Sync Managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 0x1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x01 (1dec)
1C12:01
SubIndex 001
1. allocated RxPDO (contains the index (hex) of the associated RxPDO mapping object)
UINT16
RW
0x1600 (5632dec)
1C12:02
SubIndex 002
2. allocated RxPDO (contains the index (hex) of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:03
SubIndex 003
3. allocated RxPDO (contains the index (hex) of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
Index 0x1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x01 (1dec)
1C13:01
SubIndex 001
1. allocated TxPDO (contains the index (hex) of the associated TxPDO mapping object)
UINT16
RW
0x1A00 (6656dec)
1C13:02
SubIndex 002
2. allocated TxPDO (contains the index (hex) of the associated TxPDO mapping object)
UINT16
RW
0x0000 (0dec)
Index 0x1C32 SM output parameter
Index (hex)
Meaning
Data type
Flags
Default
1C32:0
SM output parameter
Synchronization parameters for the outputs
UINT8
RO
0x20 (32dec)
1C32:01
Sync mode
Current synchronization mode:
  • 0: FreeRun
  • 1: Synchron with SM 2 Event
  • 2: DC-Mode - Synchron with SYNC0 Event
  • 3: DC-Mode - Synchron with SYNC1 Event
UINT16
RW
0x0001 (1dec)
1C32:02
Cycle time
Cycle time (in ns):
  • Free Run: Cycle time of the local timer
  • Synchron with SM 2 Event: Master cycle time
  • DC mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x001E8480 (2000000dec)
1C32:03
Shift time
Time between SYNC0 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:04
Sync modes supported
Supported synchronization modes:
  • Bit 0 = 1: FreeRun is supported
  • Bit 1 = 1: Synchron with SM 2 Event is supported
  • Bit 2–3 = 01: DC mode is supported
  • Bit 4–5 = 10: Output Shift with SYNC1 event (DC mode only)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08)
UINT16
RO
0xC007 (49159dec)
1C32:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
0x00000000 (0dec)
1C32:06
Calc and copy time
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:08
Command
  • 0: Measurement of the local cycle time is stopped
  • 1: Measurement of the local cycle time is started
The entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values.
For a subsequent measurement the measured values are reset
UINT16
RW
0x0000 (0dec)
1C32:09
Delay time
Time between SYNC1 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:0B
SM event missed counter
Number of missed SM events in OPERATIONAL (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0dec)
1C32:0D
Shift too short counter
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only)
BOOLEAN
RO
0x00 (0dec)
Index 0x1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
  • 0: FreeRun
  • 1: Synchron with SM 3 Event (no outputs available)
  • 2: DC - Synchron with SYNC0 Event
  • 3: DC - Synchron with SYNC1 Event
  • 34: Synchron with SM 2 Event (outputs available)
UINT16
RW
0x0022 (34dec)
1C33:02
Cycle time
as 0x1C32:02
UINT32
RW
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:04
  • Bit 0: free run is supported
  • Bit 1: Synchron with SM 2 Event is supported (outputs available)
  • Bit 1: Synchron with SM 3 Event is supported (no outputs available)
  • Bit 4–5 = 01: Input Shift through local event (outputs available)
  • Bit 4–5 = 10: Input Shift with SYNC1 Event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08 or 0x1C33:08)
UINT16
RO
0xC007 (49159dec)
1C33:05
Minimum cycle time
as 0x1C32:05
UINT32
RO
0x00000000 (0dec)
1C33:06
Calc and copy time
Time between reading of the inputs and availability of the inputs for the master (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:08
Command
as 0x1C32:08
UINT16
RW
0x0000 (0dec)
1C33:09
Delay time
Time between SYNC1 event and reading of the inputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:0B
as 0x1C32:11
UINT16
RO
0x0000 (0dec)
1C33:0C
as 0x1C32:12
UINT16
RO
0x0000 (0dec)
1C33:0D
as 0x1C32:13
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
as 0x1C32:32
BOOLEAN
RO
0x00 (0dec)