Quick start
No special measures are required for commissioning the EL2212.
The EL2212 can be operated with different types of function. The course of decision making and action of the commissioning is shown below.
For comprehension, refer also to the introductory chapter on the mode of operation and the application notes.
1. Mounting
Install the EL2212 as described in section Mounting and wiring.
2. Configuration
Create a configuration in the TwinCAT System Manager by manually inserting the terminal or scanning it online. Refer to installation chapter TwinCAT Development Environment regarding this.
Quick start 1:
EtherCAT XML Device Description
If the XML description of the EL2212 is not available in your system you can download the latest XML file from the download area of the Beckhoff website (http://www.beckhoff.de/german/default.htm?download/elconfg.htm) and install it according to the installation instructions.
3. Delivery state
The terminal behaves as follows in the delivery state or after scanning in the System Manager:
Quick start 2:Fig.137: Default process data
Only Output needs to be used for the activation of the actuator.
Quick start 3:Fig.138: Default CoE-Parameter
The fast switch-on and switch-off are activated for 1 ms each; the settings for the actuator are: 24 V supply voltage, 1 Ω internal resistance, 5 A boost and 0.5 A holding current.
These settings are to be subsequently adapted to the actuator employed.
4. Distributed Clocks mode
If you wish to use Distributed Clocks mode, change the process data and the mode of operation accordingly.
Quick start 4:Fig.139: Process data for DC mode
Quick start 5:Fig.140: DistributedClocks operating mode
Standard mode is recommended for initial functional tests of the actuator.
5. Calculation of the actuator-specific parameters
The internal resistance of the actuator must be such that the EL2212 reaches the recommended current range [0.2 – 10 A] both in the boost and the holding phase, taking into account the applied supply voltage [24 – 72 V DC].
Example: Actuator with Unom = 12 V, Ri = 8 Ω, Inom = 1.5 A.
A boost current of 4.5 A and a holding current of 0.75 A is selected. A supply voltage of at least 36 V is therefore required for the boost phase - the EL2212 does not generate this supply voltage itself! It must be generated externally and applied to the EL2212.
The durations of the boost-on and boost-off phases are each set to 25 ms. The switch-off threshold for the boost-off phase is set to -200 mA.
Quick start 6:
Accounting for the mechanics
The application notes must be taken into account in the design.
6. Setting the parameters and process data
CoE parameters
The CoE parameters must now be stored in the CoE for each channel.
Quick start 7:
Parameterization via the CoE list (CAN over EtherCAT)
The terminal is parameterized via the CoE - Online tab (double-click on the respective object) or via the Process Data tab (allocation of PDOs). Please note the following general CoE information when using/manipulating the CoE parameters: - Keep a startup list if components have to be replaced - Differentiation between online/offline dictionary, existence of current XML description - Use "CoE reload" for resetting changes
The over-excitation for channel 1 (n=0, activate via index 80n2:01) looks as follows in the CoE:
Quick start 8:Fig.141: Specific CoE setting channel 1
for an orderly process according to
Quick start 9:Fig.142: Current range when switching on and off
as follows:
The control factors (Kp, Ki, index 0x80n1:01; 0x80n1:02) should normally not be changed, because the default setting is sufficient for most applications.
For channel 2 the corresponding values in index 0x8010, 0x8011 and 0x8012 have to be changed.
Different values can be specified for each channel. The settings can also be loaded via the PLC/PLC/task at runtime.
7. Operation
If the actuator is connected, the parameterized current curve is now output with each off/on/off actuation.
The following can be used for diagnostics