Diagnostics per channel
Open Load (Index 0x60n1:02)
The open load detection shows that no load is connected when the output is switched on.
The "Open Load" bit (index 0x60n1:02) is set to TRUE if the output is TRUE and the output current is less than typ. 0.8 mA.
Short Circuit to 24V (Index 0x60n1:04)
A short circuit to 24 V is detected if the output is FALSE, but nevertheless a voltage of more than typ. 10 V is present. The “Short Circuit to 24V” bit (index 0x60n1:04) is set to TRUE. The corresponding LED flashes red.
Overtemperature (index: 0x60n1:01) – overcurrent (index:0x60n1:03)
The “Overcurrent” bit (index: 0x60n1:03) is set in case of an overload. The LED lights up red. The channel heats up, so that the “Overtemperature” bit (index: 0x60n1:01) is set on reaching an upper limit temperature (see fig. Overload current limitation).
In the case of a short-circuit the channel overheats very quickly, leading to it being switched off. Once the temperature has cooled down to below a lower limit value following the switch-off, the output is switched on again. The temperature, however, is then still so high that the “Overtemperature” bit (index: 0x60n1:01) remains set. Thus the LED remains red as long as the short-circuit is present.
Overcurrent diagnostics is no longer possible once the output is switched off. The “Overcurrent” bit (index: 0x60n1:03) is only set to TRUE when the output is switched on again (see fig. Schematic illustration of the thermal switch-off in case of overload).