EK1322 - Configuration by means of the TwinCAT System Manager
TwinCAT tree
Enter the EK1322 EtherCAT P extension as an EtherCAT device in the TwinCAT System Manager in Config mode under Devices. Any Terminals already connected to the network can also be read. This will cause all the Bus Couplers with Bus Terminals and their configurations to be loaded. You can then adapt these to meet your requirements.
EK1322 - Configuration by means of the TwinCAT System Manager 1:Fig.29: TwinCAT tree EK1322
Meaning of the PDO identifier
PDO identifier
Typ
State
Status UP (Undervoltage)
Bit
0
Peripheral voltage for Actors UP >= 19.4 V, no overload/ no case of short circuit
1
Peripheral voltage for Actors UP < 19.4 V or overload/ case of short circuit (output current > 3 A)
Status US (Undervoltage)
Bit
0
System- and Sensor supply US >= 19.4 V, no overload/ no case  of short circuit
1
System- and Sensor supply US < 19.4 V or overload/ case of short circuit (output current > 3 A)
WcState
Bit
0/1
Each datagram of the device indicates its processing state here. This allows monitoring for correct process data communication.
InputToggle
Bit
0/1
Toggles whenever new valid EtherCAT telegram was received
State
UINT
Status display of the “EtherCAT state machine” (see State, Online tab)
To add an EtherCAT P device to one of the two ports of the junction, right - click on the device in the Tree in the subsequently opened context menu "Add New Item...":
EK1322 - Configuration by means of the TwinCAT System Manager 2:
In the window that opens therefore, the component to be inserted and the respective port (X1 or X2) on the right side can be selected:
EK1322 - Configuration by means of the TwinCAT System Manager 3:Fig.30: Add an EtherCAT P device to EK1322 in the TwinCAT tree
EtherCAT P tab
From TwinCAT 3 Build 4020 TwinCAT has the tab „EtherCAT P“. This tab contains a planning tool to calculate voltages, currents and cable lengths of EtherCAT P system. The figure below shows the tab EtherCAT P when no device is connected to the junction device (A).
EK1322 - Configuration by means of the TwinCAT System Manager 4:Fig.31: Tab EtherCAT P: No device connected to junction device
If a device is connected to the junction device (A), you can set the cross-section and the length of the EtherCAT P cable in the tab “EtherCAT P“ of the device. See figure below, B).
EK1322 - Configuration by means of the TwinCAT System Manager 5:Fig.32: Tab EtherCAT P: One device connected to junction device
Are three devices connected to the three ports of the junction device (A), they are displayed as shown in the figure below.
EK1322 - Configuration by means of the TwinCAT System Manager 6:Fig.33: Tab EtherCAT P: Three devices connected to junction device
You can display the topology of your EtherCAT P system.
Wire Gauge
Selection of the wire cross-sectional area of the cable which is to be used
AWG 22 = 0.34 mm²
AWG 24 = 0.22 mm²
EK1322 - Configuration by means of the TwinCAT System Manager 7:
Length (m)
Indication of the cable length which is to be used
Check EtherCAT P System
At least one device is connected to the controller, the connected EtherCAT P system can be checked
Type
Listing of two voltages: Box supply US, Auxiliary voltage UP
Actual Voltage (V)
The respective voltage at which the system is powered, can be entered manually. The default setting is 24.00 V.
Min Voltage (V)
The minimum voltage is preset by the device and described in the ESI file. The EtherCAT P system is to be interpreted after this voltage. It is valid not to fall short this voltage.
Load (A)
The total consumption of the connected sensors / actuators at the device can be specified here, e.g. 100 mA.
Load Type
The characteristic of the load which is connected to the devices can be selected here. Which of the three options is right for the connected load (Sw regulator, LDO, Resistor), must be taken from the datasheet. In case of doubt please select the default value "Sw Regulator".
Sw Regulator: Switching regulators, consume more energy and therefore require an efficient power supply.
LDO: Low drop voltage regulator, the energy demand is often small and the heat dissipation is not a problem, e.g. proximity sensor.
Resistor: electronic, passive components e.g. relay, coil
EK1322 - Configuration by means of the TwinCAT System Manager 8:
If you click on the button “Check EtherCAT P System”, all devices that are attached to your TwinCAT tree are listed as shown in the following figure.
EK1322 - Configuration by means of the TwinCAT System Manager 9:Fig.34: Check EtherCAT P System
No.
The automatically assigned number of the device according to its position in the EtherCAT P strand.
Designation of the device in TwinCAT.
Previous
Number of the previous device in the EtherCAT P strand and the output port used (A/B/C/D).
Us (V), Up (V)
Supply voltage which is present at the input of the device. For device No. 1 You can enter the voltages manually.
Sum Is(A), Sum Ip(A)
Sum currents of the supply voltages at the input of the device.
Us Load, Up Load
Enter here the total load at the IO ports of the device.
The unit of this value is set by the choice of "Us Load Type" and "Up Load Type".
Us Load Type, Up Load Type
Choose here the characteristic of the load, which is connected to the IO ports of the device.
Cable Length (m)
Enter here the length of the EtherCAT P cable, which is connected to the input of the device.
Wire Gauge
Choose here the wire cross-section of the EtherCAT P cable, which is connected to the input of the device.
  • AWG 22 = 0.34 mm²
  • AWG 24 = 0.22 mm²
Example with problem case and troubleshooting
The following figure shows the planning of the EtherCAT P system without a problem. All voltages in the column “Supply Voltage (V)” are highlighted in green.
EK1322 - Configuration by means of the TwinCAT System Manager 10:Fig.35: Check EtherCAT P system without problem
The following figure shows the planning of the EtherCAT P system with a problem. The “Supply Voltage (V)” of Box 5 drops below the “Min. voltage (V)”. The corresponding field is highlighted in red. The error occurs because longer cables (adjustable in “Cable Length (m)”) and also AWG 24 instead of AWG 22 cables (adjustable in “Wire Gauge”) be used.
EK1322 - Configuration by means of the TwinCAT System Manager 11:Fig.36: Check EtherCAT P System with problem
This area offers the following three options to adjust the system so that there is no error:
State, "Online" tab
Indicates the online status of the terminal.
EK1322 - Configuration by means of the TwinCAT System Manager 12:Fig.37: State, "Online" tab
Value
0x___1
Slave in 'INIT' state
0x___2
Slave in 'PREOP' state
0x___3
Slave in 'BOOT' state
0x___4
Slave in 'SAFEOP' state
0x___8
Slave in 'OP' state
0x001_
Slave signals error
0x002_
Invalid vendorId, productCode... read
0x004_
Initialization error occurred
0x010_
Slave not present
0x020_
Slave signals link error
0x040_
Slave signals missing link
0x080_
Slave signals unexpected link
0x100_
Communication port A
0x200_
Communication port B
0x400_
Communication port C
0x800_
Communication port D
Topology of the EtherCAT P system
You can view the topology of your EtherCAT P system, as described in the figure below:
1. In the Click on "Device 1 (EtherCAT)" in the "Solution Explorer"
2. Click on the "EtherCAT" tab
3. Click on the "Topology" button
The topology of your EtherCAT P system is displayed.
EK1322 - Configuration by means of the TwinCAT System Manager 13:Fig.38: Example: Three devices are connected to the three ports of the distributor device.
