Technical data
Analog inputs
EJ3314-0090
Number of inputs
4 x TC
2 x PT1000 for cold junction compensation
Thermocouple sensor types
Type B, C, E, J, K, L, N, R, S, T, U (pre‑set type K), mV measurement
Connection technology
2-wire
Maximum cable length to the sensor
30 m (see note)
Resolution
16 bits, display adjustable:0.1/ 0.01°C per digit or
1/ 2/4 µV per digit
Input filter limit frequency
Typ. 1 kHz; depending on sensor length, conversion time, sensor type
Conversion time
approx. 2.5 s up to 20 ms, depending on configuration and filter setting, pre‑set approx. 250 ms
Wire break detection
yes
Special features
  • Channel-by-channel wire break detection
  • Internal and external cold junction
  • Error detection of the external cold junction compensation (CJC)
  • Adjustable firmware filter
  • TwinSAFE SC
MTBF (+55°C)
> 1,300,000 h
Voltage measurement
EJ3314-0090
Measuring range, technically available
approx. ±78 mV
Measuring ranges (nominal) and resolution
±30 mV (1 µV per digit, thus max. 32.768 mV can be displayed)
±60 mV (2 µV per digit, thus max. 65.536 mV can be displayed)
±75 mV (4 µV per digit, thus max. 131 mV can be displayed, note technically available measuring range)
The measuring ranges 30 mV and 60 mV are executed in software to increase the resolution and always use the same electrical measuring range of ±75 mV.
Measurement uncertainty
at 23°C ambient temperature:
< ±0.14% (relative to the full scale value);
for further information, see chapter "Measurement ±30 mV, ±60 mV, ±75 mV"
Temperature measurement
EJ3314-0090
Electrical measuring range used
±75 mV
Measuring ranges
Type B: +200...+1820°C
Type C: 0...+2320°C
Type E: -270...+1000°C
Type J: -210...+1200°C
Type K: -270…+1372°C (pre-set)
Type L: -50...+900°C
Type N: -270…+1300°C
Type R: -50...+1768°C
Type S: -50...+1768°C
Type T: -270…+400°C
Type U: -50...+600°C
at 23°C ambient temperature, with reference configuration, according to
Type: B: ±8.5°C;
Type C: ±6.2°C;
Type E: ±2.5°C;
Type J: ±2.7°C;
Type K: ±3°C;
Type L: ±2.3°C;
Type N: ±3°C;
Type R: ±6.7°C;
Type S: ±7.1°C;
Type T: ±2.9°C;
U: ±2.5°C,
for further details, see Chapter "Measurement of thermocouples"
Supply and potentials
EJ3314-0090
Power supply
via the E-bus
Current consumption via E-bus
210 mA
Electrical isolation
500 V (E-bus/signal voltage)
Communication
EJ3314-0090
Distributed clocks
No
Environmental conditions
EJ3314-0090
Permissible ambient temperature range during operation
0°C ... +55°C
Permissible ambient temperature range during storage
-25°C … +85°C
Permissible relative air humidity
95%, no condensation
Operating altitude
max. 2,000 m
General data
EJ3314-0090
Dimensions (W x H x D)
approx. 12 mm x 66 mm x 55 mm
Weight
approx. 30 g
Installation
on signal distribution board
Pollution degree
2
Installation position
Standard
Position of the coding pins
2 and 7
Color coding
green
Standards and approvals
EJ3314-0090
Vibration/shock resistance
conforms to EN 60068-2-6 /EN 60068-2-27 (with corresponding signal distribution board)
EMC immunity/emission
conforms to EN 61000-6-2 /EN 61000-6-4 (with corresponding signal distribution board)
Protection rating
EJ module: IP20
EJ system: dependent on the signal distribution board and housing
Approvals/markings*
CE, UKCA
Technical data 1:
CE approval
The CE Marking refers to the EtherCAT plug‑in module mentioned above.
If the EtherCAT plug-in module is used in the production of a ready-to-use end product (PCB in conjunction with a housing), the manufacturer of the end product must check compliance of the overall system with relevant directives and CE certification.
To operate the EtherCAT plug‑in modules, they must be installed in a housing.
Technical data 2:
Without additional protective measures, the maximum cable length from the EtherCAT Module to the sensor is 30 m. For longer cable lengths, suitable surge protection should be provided.