Configuration data
Index 80n0 AI Settings for  0 ≤ n ≤ 4 (Ch. 1 - 5, dependent on the number of channels)
Configuration data 1:
The filter characteristics are set via index 0x8000:15
The filter frequencies are set for all channels of the module centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT‑compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set.
Index (hex)
Meaning
Data type
Flags
Default
80n0:0
AI Settings
Maximum subindex
UINT8
RO
0x1C (28dec)
80n0:01
Enable user scale
Enablement of the user scaling
BOOLEAN
RW
0x00 (0dec)
80n0:05
Siemens bits
The S5 bits are shown in the three low-order bits (value 0x60n0:11)
Bit 0 = 1 (“overrange” or “underrange”)
Bit 1 (not used)
Bit 2 (not used)
BOOLEAN
RW
0x00 (0dec)
80n0:06
Enable filter
Enable filter, which makes PLC‑cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x00 (0dec)
80n0:07
Enable limit 1
The status bits are set in relation to Limit 1.
BOOLEAN
RW
0x00 (0dec)
80n0:08
Enable limit 2
The status bits are set in relation to Limit 2.
BOOLEAN
RW
0x00 (0dec)
80n0:0A
Enable user calibration
Enabling of the user calibration
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Enable vendor calibration
Enabling of the vendor calibration
BOOLEAN
RW
0x01 (1dec)
80n0:0E
Swap limit bits
Swap limit bits
BOOLEAN
RW
0x01 (1dec)
80n0:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
80n0:12
User scale gain
This is the user scaling gain.
The gain is represented in fixed-point format, with the factor 2-16.
The value 1 corresponds to 65535 (0x00010000).
INT32
RW
0x00010000 (65536dec)
80n0:13
Limit 1
First limit value for setting the status bits (resolution 0.1°C)
INT16
RW
0x0000 (0dec)
80n0:14
Limit 2
Second limit value for setting the status bits (resolution 0.1°C)
INT16
RW
0x0000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
80n0:15
Filter settings
This object determines the digital filter settings, if it is active via “Enable filter” (index 0x80n0:06).
The possible settings are sequentially numbered.
see note "Setting the filter characteristics via Index 0x8000:15"
0: 50 Hz
1: 60 Hz
2: IIR1 (400 Hz)
3: IIR2 (500 Hz)
4: IIR3 (100 Hz)
5: IIR4 (50 Hz)
6: IIR5 (24 Hz)
7: IIR6 (12 Hz)
8: IIR7 (6.2 Hz)
9: IIR8 (3.0 Hz)
UINT16
RW
0x0000 (0dec)
80n0:17
User calibration offset
INT16
RW
0x0000 (0dec)
80n0:18
User calibration gain
User gain calibration
UINT16
RW
0x4000 (16384dec)
80n0:1C
Linearization
Linearization for potentiometer values ≥ 25 kΩ:
0 = off (up to 10 kΩ),
1 = 25 kΩ,
2 = 50 kΩ,
INT16
RW
0x0000 (0dec)
Index 8047 AI Device Settings
Index (hex)
Meaning
Data type
Flags
Default
8047:0
AI Device Settings
Max. Subindex
UINT8
RO
0x11 (17dec)
8047:11
Wire breakage detection
0: sensor/load/supply monitoring
1: load/supply monitoring
2: supply monitoring
3: off
ENUM16
RW
0x0000 (0dec)