Configuration data (0x80n0, 0x80nD)
Index 80n0 AI settings (for  0 ≤ n ≤ 7)
Index (hex)
Meaning
Data type
Flags
Default
80n0:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
80n0:01
Enable user scale
User scale is active.
BOOLEAN
RW
0x00 (0dec)
80n0:02*
Presentation
0: Signed presentation
1: Unsigned presentation
2: Absolute value with MSB as sign
Signed amount representation
BIT3
RW
0x00 (0dec)
80n0:05*
Siemens bits
The S5 bits are displayed in the three low-order bits
BOOLEAN
RW
0x00 (0dec)
80n0:06
Enable filter
Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x00 (0dec)
80n0:07
Enable limit 1
Limit 1 enabled
BOOLEAN
RW
0x00 (0dec)
80n0:08
Enable limit 2
Limit 2 enabled
BOOLEAN
RW
0x00 (0dec)
80n0:0A
Enable user calibration
Enabling of the user calibration
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Enable vendor calibration
Enabling of the vendor calibration
BOOLEAN
RW
0x01 (1dec)
80n0:0E
Swap limit bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
80n0:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
80n0:12
User scale gain
User scaling gain.
The gain is represented in fixed-point format, with the factor 2-16.
The value 1 corresponds to 65535dec (0x00010000hex) and is limited to +/- 0x7FFFF.
INT32
RW
0x00010000 (65536dec)
80n0:13
Limit 1
First limit value for setting the status bits
INT16
RW
0x0000 (0dec)
80n0:14
Limit 2
Second limit value for setting the status bits
INT16
RW
0x0000 (0dec)
80n0:15
Filter settings
This object determines the digital filter settings, if it is active via Enable filter (index 0x80n0:06).
The possible settings are sequentially numbered.
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
Refer to the Note on setting the filter characteristics
UINT16
RW
0x0000 (0dec)
80n0:17
User calibration offset
User offset compensation
INT16
RW
0x0000 (0dec)
80n0:18
User calibration gain
INT16
RW
0x4000 (16384dec)
* EJ3104 only
The filter characteristics are set via index 0x8000:15
The filter frequencies are set for all channels of the module centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT-compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set.
Index 80nD AI Advanced settings (for 0 ≤ n ≤ 7, EJ3108 only)
Index (hex)
Meaning
Data type
Flags
Default
80nD:0
AI Advanced Settings
Maximum subindex
UINT8
RO
0x18 (24dez)
80nD:11
Input Type
Measurement mode, allowed values:
UINT16
RW
0x0002 (2dez)
0x02
-10..+10 V
0x0E
0..10 V
80nD:12
Scaler
Scaling range, allowed values:
UINT16
RW
0x0003 (3dez)
0x00
Extended Range
0x03
0x03 Legacy Range
80nD:17
Low Range Error
Lower threshold for setting the error bit and error led
INT32
RW
Dependent on 80nD:11
80nD:18
High Range Error
Upper threshold for setting the error bit and error led
INT32
RW