Configuration data (0x80n0, 0x80nD)
Index 80n0 AI Settings (for  0 ≤ n ≤ 3, channel 1 to channel 4)
Index (hex)
Meaning
Data type
Flags
Default
80n0:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
80n0:01
Enable user scale
User scaling is enabled.
BOOLEAN
RW
0x00 (0dec)
80n0:06
Enable filter
Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x00 (0dec)
80n0:07
Enable limit 1
Enable limit 1
BOOLEAN
RW
0x00 (0dec)
80n0:08
Enable limit 2
Enable limit 2
BOOLEAN
RW
0x00 (0dec)
80n0:0A
Enable user calibration
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Enable vendor calibration
BOOLEAN
RW
0x01 (1dec)
80n0:0E
Swap limit bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
80n0:11
User scale offset
User scale offset
INT16
RW
0x0000 (0dec)
80n0:12
User scale gain
User scale gain.
The gain has a fixed-point representation with the factor 2-16.
The value 1 corresponds to 65535dec (0x00010000hex) and is limited to +/-0x7FFFF.
INT32
RW
0x00010000 (65536dec)
80n0:13
Limit 1
First limit value for setting the status bits
INT16
RW
0x0000 (0dec)
80n0:14
Limit 2
Second limit value for setting the status bits
INT16
RW
0x0000 (0dec)
80n0:15
Filter settings
This object determines the digital filter settings if it is enabled via “Enable filter” (Index 0x80n0:06).
The possible settings are numbered consecutively.
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
Refer to the Note on setting the filter characteristics
UINT16
RW
0x0000 (0dec)
80n0:17
User calibration offset
INT16
RW
0x0000 (0dec)
80n0:18
User calibration gain
INT16
RW
0x4000 (16384dec)
Configuration data (0x80n0, 0x80nD) 1:
The filter characteristics are set via index 0x8000:15
The filter frequencies are set for all channels of the module centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT-compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set.
Index 80nD AI Advanced settings (for 0 n 3)
Index (hex)
Meaning
Data type
Flags
Default
80nD:0
AI Advanced Settings
UINT8
RO
0x18 (24dec)
80nD:11
Input Type
Measurement mode, permissible values:
UINT16
RW
0x0012 (18dec)
0x11
-20..+20 mA
0x12
0..+20 mA
80nD:12
Scaler
Scaling, permissible values:
UINT16
RW
0x0003 (3dec)
0x00
Extended Range
0x03
Legacy Range
80nD:17
Low Range Error
Lower threshold for error-bit and error-LED
INT32
RW
Depending on 80nD:11
80nD:18
High Range Error
Upper threshold for error-bit and error-LED
INT32
RW
