Objects for parameterization
Index 8000 FB Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8000:0
FB Settings Ch.1
UINT8
RO
0x1C (28dec)
8000:11
Device type
UINT32
RW
0x00000005 (5dec)
8000:12
Singleturn bits
Number of single-turn bits in the position display (process data, CoE). The sum of the single-turn bits and multi-turn bits must be 32.
Note: This parameter only influences the display and is independent of the physical resolution of the position sensor.
UINT8
RW
0x14 (20dec)
8000:13
Multiturn bits
Number of multi-turn bits in the position display (process data, CoE). The sum of the single-turn bits and multi-turn bits must be 32.
UINT8
RW
0x0C (12dec)
8000:14
Observer bandwidth
Bandwidth of the speed observer [Hz]
UINT16
RW
0x00C8 (200dec)
8000:15
Observer feed-forward
Load ratio [%] between internal rotor inertia of the motor and the total inertia of the driven system.
Load ratio = internal moment of inertia / (internal moment of inertia + mass moment of inertia of the load).
Examples:
  • 100% = load-free
  • 50 % = moments of inertia of input and output are equal
UINT8
RW
0x64 (100dec)
8000:17
Position offset
The Position offset is subtracted from the raw position of the encoder.
It can only be written with the axis stopped.
UINT32
RW
0x00000000 (0dec)
8000:18
Secondary position offset
The Secondary Position Offset is subtracted from the "Secondary Position".
UINT32
RW
0x00000000 (0dec)
8000:19
Gear ratio motor shaft revolutions
These parameters are used to scale all positions and velocities from the motor side to the load side of a gear unit.
“Gear ratio motor shaft revolutions” describes the number of motor revolutions required to achieve the number of load revolutions configured in “Gear ratio driving shaft revolutions”.
Example: For a reduction gear in which 5 motor revolutions result in 2 load revolutions, set the parameters as follows:
  • Motor shaft revolutions = 5
  • Driving shaft revolutions = 2
UINT32
RW
0x00000001 (1dec)
8000:1A
UINT32
RW
0x00000001 (1dec)
Index (hex)
Meaning
Data type
Flags
Default
8000:1B
Min position range limit
Lowest value for the position display of setpoints and actual values. If the value falls below this, an underflow to the value “Max position range limit” occurs.
“Min position range limit” must always be lower than “Max position range limit”.
UINT32
RW
0x00000000 (0dec)
8000:1C
Highest value for the position display of setpoints and actual values. If this is exceeded, an overflow to the value “Min position range limit” occurs.
“Max position range limit” must always be higher than “Min position range limit”.
UINT32
RW
0xFFFFFFFF (4294967295dec)
Index 8001 FB Touch probe Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8001:0
UINT8
RO
0x16 (22dec)
8001:11
Touch probe 1 source
Selection of the input signal for Touch probe 1. Permitted values:
  • 1: Touch probe input 1
  • 5: Hardware zero impulse
INT16
RW
0x0001 (1dec)
8001:12
Touch probe 2 source
Selection of the input signal for Touch probe 2. Permitted values:
  • 2: Touch probe input 2
INT16
RW
0x0002 (2dec)
8001:15
Touch probe 1 position source
Selection of the position held by Touch probe 1. Permitted values:
  • 0: FB Position
  • 1: FB Secondary Position
INT16
RW
0x0000 (0dec)
8001:16
Touch probe 2 position source
Selection of the position held by Touch probe 2. Permitted values:
  • 0: FB Position
INT16
RW
0x0000 (0dec)
Index 8008 FB Settings ENC Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8008:0
UINT8
RO
0x13 (19dec)
8008:01
Invert feedback direction
Changes the counting direction of the encoder.
This parameter can be used to adapt the encoder direction of rotation to the motor direction of rotation.
BOOLEAN
RW
0x00 (0dec)
8008:12
Encoder type
permitted values:
  • 0: disabled
  • 1: RS422 differential
  • 2: TTL single ended
  • 6: TTL single ended - input filters disabled
  • 7: open collector
UINT16
RW
0x0000 (0dec)
8008:13
Encoder Increments per Revolution
Resolution of the encoder after 4-fold evaluation.
UINT32
RW
0x00001000 (4096dec)
Index 8010 DRV Amplifier Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8010:0
UINT8
RO
0x73 (115dec)
8010:01
Enable TxPDOToggle
Show TxPDO Toggle in the status word (bit 10).
BOOLEAN
RW
0x00 (0dec)
8010:02
Enable input cycle counter
1: enabled
The Input cycle counter is a two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0.
The low bit is represented in bit 10 and the high bit in bit 14 of the status word.
BOOLEAN
RW
0x00 (0dec)
8010:04
Repeat find commutation
Repeat the commutation angle determination. (Effective for all FOC operation modes).
BOOLEAN
RW
0x01 (1dec)
8010:12
Current loop integral time
Integral component current controller [0.1 ms].
UINT16
RW
0x0032 (50dec)
8010:13
Current loop proportional gain
Proportional component current controller [0.1 V/A]
UINT16
RW
0x0032 (50dec)
8010:14
Velocity loop integral time
Integral component velocity controller [0.1 ms].
UINT32
RW
0x0000001E (30dec)
8010:15
Velocity loop proportional gain
Proportional component velocity controller [mA/(rad/s)].
UINT32
RW
0x00000096 (150dec)
8010:17
Position loop proportional gain
Proportional component position controller [1/s]
UINT32
RW
0x0000000A (10dec)
8010:31
Velocity limitation
Limitation of the drive speed set value [1/min].
(Only effective in the CSV and CSP controller operation modes)
When using a gear ratio, this parameter refers to the load side.
UINT32
RW
0x000186A0 (100000dec)
8010:32
Short-Circuit Brake duration max
Max. duration of armature short circuit brake. [ms]
UINT16
RW
0x0000 (0dec)
8010:33
Stand still window
Tolerance window for standstill monitoring [1/min]
UINT16
RW
0x0001 (1dec)
8010:39
Select info data 1
permitted values:
  • 2: DC link voltage (mV)
  • 4: PCB temperature (0.1°C)
  • 10: Digital inputs
UINT8
RW
0x02 (2dec)
8010:3A
Select info data 2
permitted values:
UINT8
RW
0x04 (4dec)
8010:49
Halt ramp deceleration
Halt ramp deceleration [0.1 rad / s²]
UINT32
RW
0x0000F570 (62832dec)
8010:50
Following error window
Following error monitoring: following error window.
The value 0xFFFFFFFF (4294967295dec) disables the following error monitoring.
UINT32
RW
8010:51
Following error time out
Following error monitoring: timeout [ms].
UINT16
RW
0x0000 (0dec)
8010:52
Fault reaction option code
permitted values:
  • 0: Disable drive function, motor is free to rotate
  • 1: Slow down on slow down ramp
  • 65534dec: Short circuit brake
UINT16
RW
0x0001 (1dec)
8010:54
Feature bits
UINT32
RW
0x00000000 (0dec)
8010:57
Position loop velocity feed forward gain
Scaling factor for velocity feedforward from the position interpolator.
UINT8
RW
0x64 (100dec)
8010:58
Select info data 3
permitted values:
  • 4: PCB temperature (0.1 °C)
UINT8
RW
0x0A (10dec)
Index (hex)
Meaning
Data type
Flags
Default
8010:59
Error suppression mask
UINT32
RW
0x00000000 (0dec)
8010:62
Position loop deadband window
Deadband window of the position controller.
Unit: corresponds to the process data scaling of the set position and actual positions.
UINT32
RW
0x00000000 (0dec)
8010:63
Find commutation time
For field-oriented control (FOC) with an incremental encoder, commutation determination is required, during which rated current is applied to the motor. The "Find commutation time" describes the time used for this.
UINT16
RW
0x000A (10dec)
8010:64
Commutation type
permitted values:
  • 16: Stepper with internal counter
  • 17: Stepper with encoder
  • 18: Stepper FOC with encoder
UINT8
RW
0x10 (16dec)
8010:65
Invert direction of rotation
Inverting the direction of rotation.
This parameter inverts all setpoints and actual values and is used to ensure that the motor rotates in the correct direction for the application.
Note: This parameter is not suitable for adapting the directions of rotation of the encoder and motor to each other. Use 8008:01 "Invert feedback direction" for this purpose.
BOOLEAN
RW
0x00 (0dec)
8010:6D
Torque feed forward gain
Internal torque feedforward: scaling factor
UINT32
RW
0x00000064 (100dec)
8010:6E
Torque feed forward filter time
Internal torque feedforward: filter time. [0.1 ms]
UINT32
RW
0x0000000A (10dec)
8010:6F
Torque offset
Torque offset.
The value is given in thousandths of the rated current.
INT16
RW
0x0000 (0dec)
8010:70
Torque limitation option code
Selection of the behavior in the CST controller operation mode (“Cyclic Synchronous Torque”). Permitted values:
  • 0: VeloLimitHasNoEffect
  • 1: TorqueMightBeReducedToZero
  • 2: TorqueMightBeReducedToRampPosNeg
  • 3: TorqueMightBeReducedToRampPosMaxTorqueNeg
  • 4: TorqueMightBeReducedToMaxTorquePosNeg
INT8
RW
0x00 (0dec)
8010:72
Stand still torque limitation
Only valid for commutation types "Stepper with internal counter" and "Stepper with encoder" (can be set via parameter 8010:64).
Configures a current reduction at standstill, i.e. when the target velocity is within the "Stand still window" (parameter 8010:33).
UINT16
RW
0x7FFF (32767dec)
8010:73
Acceleration limitation
Limits the maximum acceleration or deceleration. [0.1 rad/s²]
UINT32
RW
Index 8011 DRV Motor Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8011:0
UINT8
RO
0x34 (52dec)
8011:12
Rated current
Rated current of the motor [mA] (data sheet value)
Used for scaling "Torque actual value" and "Target torque".
UINT32
RW
0x00000BB8 (3000dec)
8011:16
Torque constant
Force constant of the motor [mNm/A]
UINT32
RW
0x0000012C (300dec)
8011:18
Rotor moment of inertia
Moment of inertia of the motor [g cm²]
UINT32
RW
0x000001EF (495dec)
8011:19
Winding inductance
Winding inductance [0,01 mH]
UINT16
RW
0x0186 (390dec)
8011:1B
Motor speed limitation
Speed limit of the motor [1/min]
When using a gear ratio, this limit still refers to the motor side.
UINT32
RW
8011:2E
Rated speed
Rated speed of the motor [1/min]
UINT32
RW
0x000003E8 (1000dec)
8011:30
Winding resistance
Winding resistance of the motor [mΩ]
UINT32
RW
0x00000578 (1400dec)
8011:31
Voltage constant
Voltage constant of the motor [µV/(1/min)]
UINT32
RW
0x00004E20 (20000dec)
8011:33
Motor fullsteps per revolution
Number of full motor steps per revolution.
UINT32
RW
0x000000C8 (200dec)
8011:34
Configured motor current
Configured motor current [mA]
If this is smaller than the "Rated current", the motor current is limited to the smaller of the two values.
This value is used to distribute the load between the two channels of the terminal.
UINT32
RW
Index 8012 DRV Brake Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8012:0
UINT8
RO
0x14 (20dec)
8012:01
Enable manual override
  • True: The brake state is forced manually via the CoE.
  • False: The brake is automatically controlled by the drive controller.
BOOLEAN
RW
0x00 (0dec)
8012:02
Manual brake state
Permitted values:
  • 0: Release
  • 1: Apply
BIT1
RW
0x00 (0dec)
8012:05
Brake option
Permitted values:
  • 0: Enable output to release brake
    (for brakes that are released in the energized state)
  • 1: Disable output to release brake
    (for brakes that are released in a de-energized state)
BIT4
RW
0x00 (0dec)
8012:09
External override
Enables the brake to be released via an external hardware signal.
The brake can only be released via the external signal, not applied.
You can select which hardware input (Touch probe 1 / Touch probe 2) is used for this. It is also possible to restrict whether this configuration is always active or only in the EtherCAT states INIT/PREOP/SAFEOP, i.e. when the drive is not fully operational (e.g. during maintenance work)
Permitted values:
  • 0: Disabled
  • 2: Digital Input 1
  • 3: Digital Input 1 (only INIT/PREOP/SAFEOP)
  • 4: Digital Input 2
  • 5: Digital Input 2 (only INIT/PREOP/SAFEOP)
UINT8
RW
0x00 (0dec)
8012:11
Release delay
Time required for the holding brake to release after the current has been applied.
UINT16
RW
0x0000 (0dec)
8012:12
Application delay
Time required for the holding brake to apply after the current was switched off.
UINT16
RW
0x0000 (0dec)
8012:13
Emergency application timeout
Time that the amplifier waits for the speed to reach the standstill limit after a stop request.
If the waiting time is exceeded, the holding brake is triggered, regardless of the speed.
Note: This parameter must be set at least to the longest time the axis needs to come to a standstill after it has been switched torque-free.
For vertical axes, this parameter should be set to a low value to prevent the axis or load from falling very far.
Unit: ms
UINT16
RW
0x0000 (0dec)
8012:14
Brake moment of inertia
Moment of inertia of the brake.
Unit: g cm²
UINT16
RW
0x0000 (0dec)
Index 8013 DRV Filter Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8013:0
UINT8
RO
0x19 (25dec)
8013:10
Low pass frequency 1
REAL32
RW
0x00000000 (0dec)
8013:11
Low pass damping 1
REAL32
RW
0x00000000 (0dec)
8013:12
High pass frequency 1
REAL32
RW
0x00000000 (0dec)
8013:13
High pass damping 1
REAL32
RW
0x00000000 (0dec)
8013:14
Filter type 1
permitted values:
  • 0: No_Filter
  • 1: Low_pass_filter_1_order
  • 2: Phase_correction_filter_1_order
  • 3: Low_pass_filter_2_order
  • 4: Phase_correction_filter_2_order
  • 5: Notch_filter
INT16
RW
0x0000 (0dec)
8013:15
Low pass frequency 2
REAL32
RW
0x00000000 (0dec)
8013:16
Low pass damping 2
REAL32
RW
0x00000000 (0dec)
8013:17
High pass frequency 2
REAL32
RW
0x00000000 (0dec)
8013:18
High pass damping 2
REAL32
RW
0x00000000 (0dec)
8013:19
Filter type 2
permitted values:
  • 0: No_Filter
  • 5: Notch_filter
INT16
RW
0x0000 (0dec)
Index 801F DRV Vendor data Ch.1
Index (hex)
Meaning
Data type
Flags
Default
801F:0
UINT8
RO
0x1C (28dec)
801F:12
Amplifier rated current
Maximum current per channel (without fan).
UINT32
RW
0x00001388 (5000dec)
801F:14
Amplifier overcurrent threshold
Switching threshold for the overcurrent switch-off.
UINT32
RW
0x00002710 (10000dec)
801F:15
Max rotary field frequency
UINT16
RW
0x0257 (599dec)
801F:17
Amplifier rated current with fan
Maximum current per channel (with fan)
UINT32
RW
0x00001770 (6000dec)
801F:18
Vendor feature bits
UINT32
RW
0x00000000 (0dec)
801F:1A
Amplifier Rated Sum Current
Maximum sum current for all channels (without fan)
UINT32
RW
801F:1C
Amplifier Rated Sum Current with Fan
Maximum sum current for all channels (with fan)
UINT32
RW
Index 8060 DMC Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8060:0
DMC Settings Ch.1
UINT8
RO
0x17 (23dec)
8060:07
Emergency deceleration
Deceleration for the emergency stop ramp. (In ms from motor rated speed to standstill)
Unit: 1 ms
UINT16
RW
0x0064 (100dec)
8060:08
Calibration position
If homing is successful, the "Actual position" is set to this value.
INT64
RW
8060:09
Calibration velocity (towards plc cam)
Velocity when hitting the cam in 10000ths of the rated motor speed.
INT16
RW
0x0064 (100dec)
8060:0A
Calibration Velocity (off plc cam)
Velocity when driving off the cam in 10000ths of the rated motor speed.
INT16
RW
0x000A (10dec)
8060:0E
Modulo factor
Feedback increments for one mechanical revolution.
INT64
RW
8060:12
Block calibration torque limit
Torque limitation for approaching the end stop. In parts per thousand of the rated motor current.
UINT16
RW
0x0064 (100dec)
8060:13
Block calibration stop distance
After reaching the calibration position, the axis moves out of the end position by this distance.
INT64
RW
8060:14
Block calibration lag threshold
When this following error is exceeded, the axis is in the end position.
INT64
RW
8060:15
Target position window
Target position window:
The In-Target bit is set when the axis is within this window for at least the time set in 8060:16.
INT64
RW
8060:16
Target position monitor time
see 8060:15
Unit: ms
UINT16
RW
0x0014 (20dec)
8060:17
Target position timeout
When the setpoint generator has reached its end position and the axis is not in the target window after this time has elapsed, the task is terminated and the in-target bit is not set.
Unit: ms
UINT16
RW
0x1770 (6000dec)
Index 8061 DMC Features Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8061:0
DMC Features Ch.1
UINT8
RO
0x1B (27dec)
8061:13
Invert calibration cam search direction
Invert the direction of movement to search for the limit switch.
Default: FALSE = search with positive direction of rotation.
BOOLEAN
RW
0x00 (0dec)
8061:14
Invert sync impulse search direction
Invert the direction of rotation to exit the limit switch.
Default: TRUE = exit in negative direction of rotation.
BOOLEAN
RW
0x01 (1dec)
8061:19
Calibration cam source
Source for the reference switch.
  • 0: Input 1
  • 1: Input 2
UINT8
RW
0x00 (0dec)
8061:1A
Calibration cam active level
State of the reference switch in the actuated state.
  • 0: Hi
  • 1: Low
UINT8
RW
0x00 (0dec)
8061:1B
Latch source
Source for the latch unit.
  • 0: Input 1
  • 1: Input 2
UINT8
RW
0x00 (0dec)
Index 8100 FB Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8100:0
FB Settings Ch.2
UINT8
RO
0x1C (28dec)
8100:11
Device type
UINT32
RW
0x00000005 (5dec)
8100:12
Singleturn bits
UINT8
RW
0x14 (20dec)
8100:13
Multiturn bits
UINT8
RW
0x0C (12dec)
8100:14
Observer bandwidth
UINT16
RW
0x00C8 (200dec)
8100:15
Examples:
  • 100% = load-free
UINT8
RW
0x64 (100dec)
8100:17
Position offset
UINT32
RW
0x00000000 (0dec)
8100:18
UINT32
RW
0x00000000 (0dec)
8100:19
These parameters are used to scale all positions and speeds from the motor side to the load side of a gear unit.
"Gear ratio motor shaft revolutions" describes the number of motor revolutions required to achieve the number of load revolutions configured in "Gear ratio driving shaft revolutions".
UINT32
RW
0x00000001 (1dec)
8100:1A
UINT32
RW
0x00000001 (1dec)
8100:1B
Lowest value for the position display of setpoints and actual values. If the value falls below this, an underflow to the value "Max position range limit" occurs.
"Min position range limit" must always be lower than "Max position range limit".
UINT32
RW
0x00000000 (0dec)
8100:1C
Highest value for the position display of setpoints and actual values. If this is exceeded, an overflow to the value "Min position range limit" occurs.
"Max position range limit" must always be higher than "Min position range limit".
UINT32
RW
Index 8101 FB Touch probe Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8101:0
UINT8
RO
0x16 (22dec)
8101:11
INT16
RW
0x0001 (1dec)
8101:12
INT16
RW
0x0002 (2dec)
8101:15
  • 0: FB Position
INT16
RW
0x0000 (0dec)
8101:16
  • 0: FB Position
INT16
RW
0x0000 (0dec)
Index 8108 FB Settings ENC Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8108:0
UINT8
RO
0x13 (19dec)
8108:01
BOOLEAN
RW
0x00 (0dec)
8108:12
Encoder type
permitted values:
  • 0: disabled
  • 7: open collector
UINT16
RW
0x0000 (0dec)
8108:13
UINT32
RW
Index 8110 DRV Amplifier Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8110:0
UINT8
RO
0x73 (115dec))
8110:01
Enable TxPDOToggle
BOOLEAN
RW
0x00 (0dec)
8110:02
1: enabled
BOOLEAN
RW
0x00 (0dec)
8110:04
BOOLEAN
RW
0x01 (1dec)
8110:12
UINT16
RW
0x0032 (50dec)
8110:13
UINT16
RW
0x0032 (50dec)
8110:14
UINT32
RW
0x0000001E (30dec)
8110:15
UINT32
RW
0x00000096 (150dec)
8110:17
UINT32
RW
0x0000000A (10dec)
8110:31
Velocity limitation
UINT32
RW
8110:32
UINT16
RW
0x0000 (0dec)
8110:33
Stand still window
UINT16
RW
0x0001 (1dec)
8110:39
Select info data 1
permitted values:
UINT8
RW
0x02 (2dec)
8110:3A
Select info data 2
permitted values:
UINT8
RW
0x04 (4dec)
8110:49
UINT32
RW
8110:50
The value 0xFFFFFFFFFF (4294967295dec) disables the following error monitoring.
UINT32
RW
8110:51
UINT16
RW
0x0000 (0dec)
8110:52
permitted values:
UINT16
RW
0x0001 (1dec)
8110:54
Feature bits
UINT32
RW
0x00000000 (0dec)
8110:57
Scaling factor for velocity pre-control from the position interpolator.
UINT8
RW
0x64 (100dec)
8110:58
Select info data 3
permitted values:
UINT8
RW
0x0A (10dec)
Index (hex)
Meaning
Data type
Flags
Default
8110:59
UINT32
RW
0x00000000 (0dec)
8110:62
UINT32
RW
0x00000000 (0dec)
8110:63
For field-oriented control (FOC) with an incremental encoder, commutation determination is required, during which nominal current is applied to the motor. The "Find commutation time" describes the time used for this.
UINT16
RW
0x000A (10dec)
8110:64
Commutation type
permitted values:
UINT8
RW
0x10 (16dec)
8110:65
BOOLEAN
RW
0x00 (0dec)
8110:6D
Internal torque pre-control: scaling factor
UINT32
RW
0x00000064 (100dec)
8110:6E
Internal torque pre-control: filter time. [0.1 ms]
UINT32
RW
0x0000000A (10dec)
8110:6F
Torque offset
Torque offset.
The value is given in thousandths of the nominal current.
INT16
RW
0x0000 (0dec)
8110:70
INT8
RW
0x00 (0dec)
8110:72
Only valid for commutation types "Stepper with internal counter" and "Stepper with encoder" (can be set via parameter 8110:64).
Configures a current reduction at standstill, i.e. when the target velocity is within the "Stand still window" (parameter 8110:33).
UINT16
RW
0x7FFF (32767dec)
8110:73
UINT32
RW
Index 8111 DRV Motor Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8111:0
UINT8
RO
0x34 (52dec)
8111:12
Rated current
UINT32
RW
8111:16
Torque constant
UINT32
RW
0x0000012C (300dec)
8111:18
UINT32
RW
0x000001EF (495dec)
8111:19
Winding inductance
UINT16
RW
0x0186 (390dec)
8111:1B
UINT32
RW
8111:2E
Rated speed
UINT32
RW
8111:30
Winding resistance
UINT32
RW
8111:31
Voltage constant
UINT32
RW
8111:33
UINT32
RW
0x000000C8 (200dec)
8111:34
UINT32
RW
Index 8112 DRV Brake Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8112:0
UINT8
RO
0x14 (20dec)
8112:01
BOOLEAN
RW
0x00 (0dec)
8112:02
Manual brake state
Permitted values:
  • 0: Release
  • 1: Apply
BIT1
RW
0x00 (0dec)
8112:05
Brake option
Permitted values:
BIT4
RW
0x00 (0dec)
8112:09
External override
Permitted values:
  • 0: Disabled
UINT8
RW
0x00 (0dec)
8112:11
Release delay
UINT16
RW
0x0000 (0dec)
8112:12
Application delay
UINT16
RW
0x0000 (0dec)
8112:13
Unit: ms
UINT16
RW
0x0000 (0dec)
8112:14
Unit: g cm²
UINT16
RW
0x0000 (0dec)
Index 8113 DRV Filter Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8113:0
UINT8
RO
0x19 (25dec)
8113:10
REAL32
RW
0x00000000 (0dec)
8113:11
Low pass damping 1
REAL32
RW
0x00000000 (0dec)
8113:12
REAL32
RW
0x00000000 (0dec)
8113:13
High pass damping 1
REAL32
RW
0x00000000 (0dec)
8113:14
Filter type 1
permitted values:
  • 0: No_Filter
  • 5: Notch_filter
INT16
RW
0x0000 (0dec)
8113:15
REAL32
RW
0x00000000 (0dec)
8113:16
Low pass damping 2
REAL32
RW
0x00000000 (0dec)
8113:17
REAL32
RW
0x00000000 (0dec)
8113:18
High pass damping 2
REAL32
RW
0x00000000 (0dec)
8113:19
Filter type 2
permitted values:
  • 0: No_Filter
  • 5: Notch_filter
INT16
RW
0x0000 (0dec)
Index 811F DRV Vendor data Ch.2
Index (hex)
Meaning
Data type
Flags
Default
811F:0
UINT8
RO
0x1C (28dec)
811F:12
UINT32
RW
811F:14
UINT32
RW
811F:15
UINT16
RW
0x0257 (599dec)
811F:17
UINT32
RW
811F:18
Vendor feature bits
UINT32
RW
0x00000000 (0dec)
811F:1A
UINT32
RW
811F:1C
UINT32
RW
Index 8160 DMC Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8160:0
DMC Settings Ch.2
UINT8
RO
0x17 (23dec)
8160:07
Deceleration for the emergency stop ramp. (In ms from motor nominal speed to standstill)
Unit: 1 ms
UINT16
RW
0x0064 (100dec)
8160:08
INT64
RW
8160:09
Velocity when hitting the cam in 10000ths of the motor nominal speed.
INT16
RW
0x0064 (100dec)
8160:0A
Velocity when driving off the cam in 10000ths of the motor nominal speed.
INT16
RW
0x000A (10dec)
8160:0E
Modulo factor
INT64
RW
8160:12
Torque limitation for approaching the end stop. In parts per thousand of the nominal motor current.
UINT16
RW
0x0064 (100dec)
8160:13
INT64
RW
8160:14
INT64
RW
8160:15
The In-Target bit is set when the axis is within this window for at least the time set in 8160:16.
INT64
RW
8160:16
see 8160:15
Unit: ms
UINT16
RW
0x0014 (20dec)
8160:17
Unit: ms
UINT16
RW
0x1770 (6000dec)
Index 8161 DMC Features Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8161:0
DMC Features Ch.2
UINT8
RO
0x1B (27dec)
8161:13
BOOLEAN
RW
0x00 (0dec)
8161:14
BOOLEAN
RW
0x01 (1dec)
8161:19
  • 0: Input 1
  • 1: Input 2
UINT8
RW
0x00 (0dec)
8161:1A
  • 0: Hi
  • 1: Low
UINT8
RW
0x00 (0dec)
8161:1B
Latch source
  • 0: Input 1
  • 1: Input 2
UINT8
RW
0x00 (0dec)
Index F800 DRV Amplifier Settings
Index (hex)
Meaning
Data type
Flags
Default
F800:0
UINT8
RO
0x18 (24dec)
F800:10
Nominal DC link voltage
Nominal DC link voltage.
UINT32
RW
0x0000BB80 (48000dec)
F800:11
Min DC link voltage
Min. DC link voltage.
If the value falls below this, a drive error is triggered or an inactive axis cannot be switched on.
UINT32
RW
0x00001A90 (6800dec)
F800:12
Max DC link voltage
Max. DC link voltage.
If this value is exceeded, a drive error is triggered or an inactive axis cannot be switched on.
UINT32
RW
0x0000EA60 (60000dec)
F800:15
Amplifier Temperature warn level
Amplifier temperature warning threshold.
UINT16
RW
0x0320 (800dec)
F800:16
Amplifier Temperature error level
Amplifier temperature error threshold.
UINT16
RW
0x03E8 (1000dec)
F800:17
Feature bits
UINT32
RW
0x00000000 (0dec)
F800:18
Fan Configuration
An external fan can be used to increase the permissible motor current for the terminal.
Permitted values:
  • 0: no fan
  • 1: fan installed
UINT8
RW
0x00 (0dec)