Set counter value
The counter value can be set to a predefined value at runtime and thus be used for synchronization with other processes. The preset can be activated in the following ways:
Set counter value 1:
Multiple activation of “Set counter on ...”
If several commands are activated to accept the preset counter value, only the command that is set first is accepted by the terminal. All other commands are ignored but remain activated, depending on the system.
  • The counter value is set to the preset counter value at the first activated event and confirmed by the bit in process data “Set counter done” (0x60n0:03).
  • The counter value specification cannot be reactivated until all activated commands for the transfer of the counter value have been deactivated. This is confirmed by setting the bit in process data “Set counter done” (0x60n0:03) to FALSE.
Set counter value via a PLC variable (Set counter value)
The counter value can be set to a predefined value during runtime via the process data “Set counter” (0x70n0:03). In the PLC this bit can be linked to a digital input, for example, or used directly as a variable.
Set counter value via input zero pulse C (Set counter on latch C)
The counter value can be set to a preset value during runtime via the process data by means of the zero pulse C.
Set counter via the “Latch extern” input (Set counter on latch extern on positive/negative edge)
The counter value can be set to a preset value during runtime via the process data by the positive or negative edge at the “Latch extern” input.