Connection
WARNING
Risk of injury through electric shock and damage to the device!
Bring the bus terminal system into a safe, de-energized state before beginning to mount, disassemble, or wire the bus terminals!
Connection 1:
Fig.4: ED5112
Terminal point
Abbreviation
No.
1-channel mode 1xABC
2-channel mode 2xAB
Ch1 A
1
Channel 1, encoder input A
Ch1 B
2
Channel 1, encoder input B
Ch1 C/Ch2 A
3
Channel 1, encoder input C
Channel 2, encoder input A
Ch1 DI/Ch2 B
4
Channel 1, digital input
The input “Digital input” is internally connected to 5 V via a pull-up resistor. The encoder alarm output must actively pull the signal against GND.
External power supply is not recommended. If an external supply is used, the maximum permitted voltage is 5 V against GND
Channel 2, encoder input B
Enc supply+
5
Encoder supply (5 V default, parameterizable 12 V, 24 V)
Enc supply-
6
0 V encoder supply
0 V encoder supply
Latch
7
Input “Latch extern”
Gate/Latch combination input for encoder 1
n.c.
8
Do not connect the terminal point
Ch1 A̅
9
Channel 1, encoder input A̅
Ch1 B̅
10
Channel 1, encoder input B̅
Ch1 C̅/ Ch2 A̅
11
Channel 1, encoder input C̅
Channel 2, encoder input A̅
Ch2 B̅
12
Channel 2, encoder input B̅
Enc supply+
13
Enc supply-
14
0 V encoder supply
0 V encoder supply
Gate
15
The Gate input can also be used as Latch extern 2 input
Gate/Latch combination input for encoder 2
n.c.
16
Connection 2:
Setting the encoder supply via index 0x8001:17
The encoder supply is set centrally for both channels via the index 0x8001:17 (channel 1). The corresponding index 0x8011:17 of the second channel has no parameterization function.
Notice
Setting the encoder supply voltage
  • Before switching to a higher voltage, make sure that the connected encoders support the selected voltage range!
  • To write to 0x80n1:17 “Supply voltage” you have to set the value 0x72657375 (ASCII: “user”) in index 0xF008 “Code word”.