Technical data
General | ED3078 |
Number of channels | Total | 8 |
Internal communication protocol | EtherCAT |
Minimum cycle time | 100 µs |
Analog input | ED3078 |
Voltage | |
Number of channels | max. 8 |
Connection technology | 2-wire |
Resolution | Technical | 16 bit, including sign |
Resolution | Process data | 327.67… µV in Extended Range |
Representation | Process data | REAL32, INT16 |
ADC conversion method | SAR |
Conversion type | multiplex, approx. 60 µs delay between channels |
Conversion time | min. 500 µs per channel |
Conversion rate | max. 2 ksps per channel |
Signal range | Nominal | -10…+10 V, 0…10 V |
Signal range | Technical | -10.73…+10.73 V |
Signal range | Full scale value (FSV) | 10 V |
Internal resistance/impedance | typ. > 220 kΩ |
Ground reference | single-ended |
Frequency range | Input signal | variable |
Input filter cut-off frequency | 1 kHz (-3 dB) |
Dielectric strength | ±30 V against 0 V |
Accuracy/uncertainty | Of the FSV (23°C) | < ±0.2% |
Accuracy/uncertainty | Of the FSV (0…55°C) | < ±0.3% |
Accuracy/uncertainty | Of the FSV (-25…+55°C) | < ±0.35% |
Accuracy/uncertainty | Of the FSV (-25…+60°C) | < ±0.35% |
Temperature coefficient | < ±30 ppm/K |
Wire break detection | no |
Current | |
Connection technology | 2-wire, 3-wire, 4-wire |
Resolution | Process data | 655.35…nA in Extended Range |
Signal range | Nominal | -20…+20 mA, 0…20 mA, 4…20 mA |
Signal range | Technical | -21.47…+21.47 mA |
Signal range | Full scale value (FSV) | 20 mA |
Internal resistance/impedance | typ. 50 Ω |
Overcurrent protection | typ. 50 mA |
Supply and electrical isolation | ED3078 |
Electronics | Supply voltage | via E-bus |
E-bus | Current consumption | typ. 100 mA |
Power contacts | Input voltage | 24 V DC (+20%) (not used by the terminal) |
Power contacts | Current carrying capacity | max. 10 A |
Power contacts | Current consumption | – |
Power contacts | Output voltage | corresponds to Power contacts | Input voltage |
Electrical isolation | Channel/channel | no |
Electrical isolation | Channel/bus | functional, 707 V DC type test |
Environmental conditions | ED3078 |
Operating temperature | -25…+60°C |
Storage temperature | -40…+85°C |
Relative humidity | 95%, no condensation |
Standards and approvals | ED3078 |
Vibration resistance | conforms to EN 60068-2-6 |
Shock resistance | conforms to EN 60068-2-27 |
EMC immunity | conforms to EN 61000-6-2 |
EMC emission | conforms to EN 61000-6-4 |
Markings*) | CE |
Approvals*) | |
*) Real applicable approvals/markings, see name plate on the side (product labeling) | |
Housing data | ED-12-16pin |
Weight | approx. 60 g |
Protection rating | IP20 |
Material | polycarbonate |
Dimensions | Width (single) | 15 mm |
Dimensions | Width (stacked) | 12 mm |
Dimensions | Height | 100 mm |
Dimensions | Depth | 65 mm |
Installation | Terminal/back wall | DIN rail, 35 mm (EN 60715) |
Installation | Terminal/terminal | double slot and key connection |
Pluggable wiring level | no |
Connection mechanism | push-in |
Connection cross-section | Solid wire | 0.08…1.5 mm² |
Connection cross-section | Stranded wire | 0.25…1.5 mm² |
Connection cross-section | With ferrule | 0.14…0.75 mm² |
Connection cross-section AWG | Solid wire | AWG28…16 |
Connection cross-section AWG | Stranded wire | AWG22…16 |
Connection cross-section AWG | With ferrule | AWG26…19 |
Stripping length | 8…9 mm |
Power contact | "+" (left) | yes |
Power contact | "+" (right) | yes |
Power contact | "-" (left) | yes |
Power contact | "-" (right) | yes |
Power contact | "⏚" (left) | no |
Power contact | "⏚" (right) | no |
Insertion lock for power contact "⏚" | yes |
