Connection and LEDs
WARNING
Risk of injury through electric shock and damage to the device!
Bring the bus terminal system into a safe, de-energized state before beginning to mount, disassemble, or wire the bus terminals!
Connection and LEDs 1:
Fig.4: ED3074 – Connection
Connection
Terminal point
Internally connected with connection
Max.
current carrying capacity *)
Abbreviation
No.
Ch1U
1
Channel 1, voltage measurement, positive input
Not applicable (voltage inputs)
Ch2U
2
Channel 2, voltage measurement, positive input
Ch3U
3
Channel 3, voltage measurement, positive input
Ch4U
4
Channel 4, voltage measurement, positive input
+24 V DC
5
+24 V
6, 7, 8, positive power contact
1 A
+24 V DC
6
+24 V
5, 7, 8, positive power contact
1 A
+24 V DC
7
+24 V
5, 6, 8, positive power contact
1 A
+24 V DC
8
+24 V
5, 6, 7, positive power contact
1 A
GND
9
Signal ground for channel 1
10, 11, 12, negative power contact (observe current carrying capacity)
100 mA
GND
10
Signal ground for channel 2
9, 11, 12, negative power contact (observe current carrying capacity)
100 mA
GND
11
Signal ground for channel 3
9, 10, 12, negative power contact (observe current carrying capacity)
100 mA
GND
12
Signal ground for channel 4
9, 10, 11, negative power contact (observe current carrying capacity)
100 mA
Ch1I
13
Channel 1, current measurement, input
50 mA (see note “Overcurrent protection of the 20 mA inputs”)
Ch2I
14
Channel 2, current measurement, input
Ch3I
15
Channel 3, current measurement, input
Ch4I
16
Channel 4, current measurement, input
Notice *) Continuous current; short-term higher currents are to be prevented and can cause thermal overload (damage)
Notice
Cable lengths > 30 m
For cable lengths > 30 m, suitable overvoltage protection (surge protection) must be provided (e g. EL9540-0010) if corresponding interference could affect the signal cable.
Connection and LEDs 2:
The current inputs are protected against damage due to overcurrent by an internal electronic overcurrent detection with self-resetting current path separation.
The overcurrent is caused by an occasionally excessive sensor voltage. Depending on the duration and level of the voltage applied, currents > 200 mA can also occur briefly (tripping time: µs range) until the current path separation becomes effective.
Approximately 1 second after an overcurrent detection and the resulting current path separation, the current path is closed again. If the excessive sensor voltage is still present, an overcurrent is detected again and the current path is opened. This process is repeated as long as the excessive voltage is present (auto-retry).
  • To ensure that the current path separation is not overloaded, the dielectric strength in the current measuring range must be observed (see technical data).
  • Overcurrent is indicated in the process image as "Overrange".
  • After it occurs, the error condition must be eliminated immediately.
LEDs
Connection and LEDs 3:
Fig.5: ED3074 – LEDs
No.
Color
Meaning
Run
1
green
This LED indicates the terminal’s operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings are applied
single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state;
mailbox and process data communication is possible
flickering
State of the EtherCAT State Machine: BOOTSTRAP = Function for
Firmware updates of the terminal
Error Ch. 1
Error Ch 4
9,
12
red
off
No error
On
Error is present, corresponds to PDO “Error”