“HWE input (hardware enable)” | ModuleIdent 0x3009C8
This module allows you to enable or disable the PWM output via the digital input.
The status of the binary signal is output via the “HWE Inputs - Input” process data value. The HWE input module provides the following features:
“HWE input (hardware enable)” | ModuleIdent 0x3009C8 1:Fig.32: Settings: Digital input with enable control for the PWM output (hardware enable)
Definition of the PWM output enable level
The PWM output of the respective channel can be enabled via the digital input “Hardware Enable”. Enable is triggered by a rising edge or a falling edge.
0x80n0:04 “Invert Digital Input”
Status at the digital input, “HWE inputs – input”
Output of the PWM output signal
FALSE (default)
1 – TRUE
is enabled
2 – FALSE
is disabled
TRUE
3 – TRUE
is disabled
4 – FALSE
is enabled
“HWE input (hardware enable)” | ModuleIdent 0x3009C8 2:Fig.33: Enabling the PWM output signal via 0x80n0:04 “Invert digital input”
Notice
“Hardware enable” input in case of bus error (watchdog)
The “Hardware Enable” input does not lose its functionality in the event of a bus error (watchdog). If the PWM output has been validly enabled prior to the bus error, this enable status remains in effect even during the bus error.
Parameterizable input characteristics
The digital input can be interpreted as having either a positive switching or ground switching characteristic. This is defined at 0x80n0:11 “Input Type” (n = 1 for DI 1, n = 3 for DI 2, n = 5 for DI 3, n = 7 for DI 4):
Standard digital | Positive switching
0x80n0:11 „Input Type“
Positive Switching (PNP)
Signal voltage “0”
-3…+1.5 V DC
Signal voltage “1”
2.7…28 V DC
Standard digital | Ground switching
Ground Switching (NPN)
Signal voltage “0”
2.5…28 V DC
Signal voltage “1”
-3…+1 V DC
In this operation mode, an additional pull-up resistor is connected to V+.
“HWE input (hardware enable)” | ModuleIdent 0x3009C8 3:
Sensors with open collector output circuits
A sensor with an open collector output circuit corresponds to the “Input Type”: “Ground Switching (NPN)”.
  • In this context, the switching thresholds defined by the manufacturer must be observed to determine whether the input signal should be interpreted as “normally open” or “normally closed”.
Parameterizable filter time
The digital input module provides a parameterizable filter time. This can be used to suppress interference, such as bouncing of a switch signal. Signals with a pulse duration shorter than the set filter time are suppressed.
Filter function sequence
Index 0x80n0:12 “Filter Time”
Meaning
500dec: 500 µs
Signals < 500 µs are suppressed
750dec: 750 µs
Signals < 750 µs are suppressed
1,000dec: 1 ms
Signals < 1 ms are suppressed
3,000dec: 3 ms
Signals < 3 ms are suppressed (default)
10,000dec: 10 ms
Signals < 10 ms are suppressed
20,000dec: 20 ms
Signals < 20 ms are suppressed