Setting the PWM state in the event of a watchdog trigger
The watchdog behavior can be configured for the following cases:
  1. in the event of a bus error via index 0x80n0:05 “Watchdog”
  2. in the event of PLC inactivity, via index 0x80n0:0C “Enable Output Cycle Counter Watchdog”
Setting the PWM state in the event of a watchdog trigger 1:
A loss of supply voltages is not a watchdog event
Please note that the loss of supply voltages via the E-bus, the power contacts, and the externally supplied voltage does not represent a watchdog event.
Setting the PWM state in the event of a watchdog trigger 2:
Notes on the switching behavior of the outputs
  • With an inductive load:
    The switching behavior of the output with inductive loads deviates from the specified switching times due to the inductance of the selected load.
  • In tristate mode:
    Internal circuit causes a leakage current in tristate mode, which pulls the potential toward ground. This corresponds to a pull-down resistance in the range of typically < 4 kOhm.
  • When switching via a PLC variable:
    If the output is switched via a PLC variable, the delays caused by the PLC cycle time must also be taken into account in addition to the TON/TOFF.
CAUTION
Watchdog settings
Changes to the watchdog settings can lead to unwanted system behavior or damage to devices.
  • Observe the information in the chapter “Notes on watchdog settings” in the EtherCAT system documentation before making any changes to the watchdog settings!