Setting with DIP switches
You can set the IP address for the switched Ethernet interfaces X101/X102 with the DIP switches S101. The DIP switches have no meaning for the Ethernet interface X001.
Setting with DIP switches 1:Fig.8: DIP switch S101, switches 1 to 10.
Right switch position: on "1".
Left switch position: off "0".
You can edit the last byte of the IP address with DIP switches 1 to 8. The DIP switches take priority over the settings in the operating system. The changes are only accepted after restarting the Embedded PC.
Meaning of the DIP switch S101.
DIP switch S101
Meaning
10 on and 9 off.
DHCP active. Standard setting ex factory.
The DIP switches 1 to 8 then have no meaning.
10 off and 9 off.
DHCP inactive.
The fixed IP address 192.168.1.xxx and subnet mask 255.255.255.0 are used as standard.
The last byte of the IP address 192.168.1.xxx is edited with DIP switches 1 to 8.
You can change the first three bytes of the IP address in the operating system or via the web interface (Beckhoff Device Manager). You can edit the last byte of the IP address again with the DIP switches.
10 off and 9 off
1 to 8 all on
The complete IP address is adopted from the operating system or the web interface (Beckhoff Device Manager).
Example
If you wish to set the IP address for the Ethernet interface X101/X102 to 192.168.1.67 using the DIP switches, you have to configure the DIP switches as follows:
DIP 1
DIP 2
DIP 3
DIP 4
DIP 5
DIP 6
DIP 7
DIP 8
DIP 9
DIP 10
On
On
Off
Off
Off
Off
On
Off
off
off
The following value for the last byte of the IP address then results from the switched-on DIP switches:
20 + 21 + 26 = 67
Values for the individual DIP switches.
DIP 1
DIP 2
DIP 3
DIP 4
DIP 5
DIP 6
DIP 7
DIP 8
Value
20
21
22
23
24
25
26
27