Diagnostic LEDs
BK9050
BK9050 LEDs
LEDs for power supply diagnostics
LED (Power LEDs)
Meaning
Us
off: Bus Coupler has no voltage 24 VDC
Up
off: No 24 VDC power supply connected to the power contacts
LEDs for K-bus diagnostics
LED (K-bus)
Meaning
K-bus RUN
on or flashing: K-bus running
K-bus ERR
flashing: (see error code)
LEDs for Ethernet diagnosis
LED (Ethernet)
Meaning
WD ERR
on: Watchdog error
COM
on or flashing: communication with controller
ERROR
flashing: DHCP or BootP active. Waiting for an IP address
RTE
on: hard real-time with TC is switched on. No ADS communication is possible at the same time. All TCP, UPD and ICMP telegrams (e.g. ping) remain unanswered.
LINK/ACT
on: LINK present
flashing: LINK present and communication active
Error code for K-bus diagnosis
Error
code
Error
argument
Remedy
flashing continuously
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localized by a restart of the coupler (by switching it off and then on again)
1
0
EEPROM checksum error
Enter factory settings with the KS2000 configuration software
1
Code buffer overflow
Insert fewer Bus Terminals. Too many entries in the table for the programmed configuration
2
Unknown data type
Software update required for the Bus Coupler
2
Reserve
3
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4
0
K-bus data error, break behind the Bus Coupler
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
Check whether the Bus End Terminal KL9010 is connected.
5
n
K-bus error in register communication with Bus Terminal n
Exchange the nth bus terminal
6
0
Error at initialization
Exchange Bus Coupler
1
Internal data error
Perform a hardware reset on the Bus Coupler (switch off and on again)
2
IP address already exists
Check the IP address; the coupler has already found its set IP address in the network
4
BootP invalid DIP switch setting
With BootP the DIP switches 1-8 must be all On or all Off
7
0
Note: cycle time was exceeded
Warning: the set cycle time was exceeded. This indication (flashing LEDs) can only be cleared by booting the Bus Coupler again.
Remedy: increase the cycle time
9
0
Checksum error in Flash program
Transmit program to the BC again
1
Incorrect or faulty library implemented
Remove the faulty library
10
n
Bus Terminal n is not consistent with the configuration that existed when the boot project was created
Check the nth Bus Terminal. The boot project must be deleted if the insertion of an nth Bus Terminal is intentional
14
n
nth Bus Terminal has the wrong format
Start the Bus Coupler again, and if the error occurs again then exchange the Bus Terminal
15
n
Number of Bus Terminals is no longer correct
Start the Bus Coupler again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software
16
n
Length of the K-bus data is no longer correct
