Diagnostic LEDs
The BC9191 and BC9191-0100 have LEDs for status display.
Diagnostic LEDs BC9191 and BC9191-0100 up to HW 4
LEDs BC9191 to HW 4
Diagnostic LEDs BC9191 and BC9191-0100 from HW 5
LEDs BC9191 from HW 5
LEDs for PLC diagnostics
LED
Meaning
PLC
on - PLC running, flashing - cycle time exceeded, off - cycle time permanently exceeded or PLC stopped
TC/DC
on - TwinCAT configuration active, off - Default configuration active, flashing TwinCAT configuration faulty
LEDs for Ethernet diagnostics
LED
Meaning
LINK/ACT (RJ45)
on - LINK available, flashing - LINK available and communication
COM
Communication with controller available
ERROR
flashing - DHCP or BootP active. Waiting for an IP address. short flashing - the source code of the PLC program is loaded and is being checked. No boot project can be created during this check time.
LEDs for power supply diagnostics
LED
Meaning
Power LED Vs
on - internal power supply 5 VDC okay (for hardware version 3 and 4 only visible with unplugged connector X1)
Power LED Vp
on - 24 VDC power supply for external devices okay
LEDs for K-bus diagnostics
LED
Meaning
K-bus RUN
on or flashing - K-bus running
K-bus ERR
flashing (see error code)
Error code for K-bus diagnostics
Error
code
Error
argument
Remedy
flashing continuously
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localized by a restart (by switching the BC9191 off and then on again)
1
0
EEPROM checksum error
Enter factory settings with the KS2000 configuration software
1
Code buffer overflow
Insert fewer Bus Terminals. Too many entries in the table for the programmed configuration
2
Unknown data type
Software update required for the BC9191
2
reserve
3
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4
0
K-bus data error, break behind the Bus Coupler
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary
n
Break behind Bus Terminal n
Check whether the KL9010 bus end terminal is connected
5
n
K-bus error in register communication with Bus Terminal n
Exchange the nth Bus Terminal
6
0
Error at initialization
Exchange Bus Coupler
1
Internal data error
Perform a hardware reset on the BC9191 (switch off and on again)
2
DIP switch changed after a software reset
3
IP address already assigned
Check whether the IP address already exists in the network.
7
0
Note: cycle time was exceeded
Warning: the set cycle time was exceeded. This note (flashing of the LED)
can only be reset by rebooting the BC9191.
Short-term remedy: increase cycle time
9
0
Checksum error in Flash program
Transmit program to the BC again
1
Incorrect or faulty library implemented
Remove the faulty library
10
n
Bus Terminal n is not consistent with the configuration that existed when the boot project was created
Check the nth Bus Terminal. The boot project must be deleted if the insertion of an nth Bus Terminal is intentional.
14
n
nth Bus Terminal has the wrong format
Start the BC9191 again, and if the error occurs again then exchange the Bus Terminal.
15
n
Number of Bus Terminals is no longer correct
Start the BC9191 again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software
16
n
Length of the K-bus data is no longer correct
Start the Bus Coupler again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software