Technical data
Bus Terminal Controller
BC9191
BC9191-0100
Number of Bus Terminals
64
Maximum fieldbus byte number
512 bytes input, 512 bytes output
Digital inputs
3, for connecting potential-free contacts (e.g. for window contact, dew point sensor, occupancy sensor)
Digital outputs
1 x LED output, constant current 10 mA , max. 24 V (e.g. for LED occupancy signal)
1 x 230 VAC, 10 A, relay (e.g. for air heater)
3 x 230 VAC, 1 A, relay (e.g. for 3-stage fan)
2 x 230 VAC, 1 A, triac (e.g. for valves for heating and cooling)
Analog inputs
1 x PT/Ni1000 (PT1000: -20...+60 °C, NI1000: -15...+55 °C) for air temperature measurement
1 x resistance measurement for setpoint setting ( 0...10 kOhm)
3 x 0...10 V (e.g. for CO2 sensor, air quality sensor, light sensor)
Analog outputs
2 x 0...10 V (e.g. air volume controller)
Sub-bus systems
1 x K-bus
1 x system bus for KL6583 (EnOcean)
1 x K-bus
1 x RS485 (e.g. Modbus-RTU/DMX)
Dielectric strength
500 V (supply voltage/fieldbus)
Supply voltage
110 ... 240 VAC
Current consumption
typically 80 mA (230 V), max. 220 mA (85 V)
Power loss
max. 15 W, typically 8 W (without 24 V DC consumers and without further bus terminals)
K-bus power supply
max. 200 mA
24VDC power supply
max. 100 mA
Weight
approx. 350 g
Permissible ambient temperature range during operation
0 °C ... +55 °C
Permissible ambient temperature range during storage
-25 °C ... +85 °C
Permissible relative humidity
max. 95 %, no condensation
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Correct installation position
vertically on a mounting rail mounted horizontally on the wall (see chapter Installation position)
Protection class
IP20
Approvals/markings*
CE UKCA, EAC
PLC
BC9191
BC9191-0100
Programming/configuration
with TwinCAT via Ethernet (TwinCAT 2.11 Build 2034 or higher, no TC3)
Program memory
48 kbyte (minus task-configuration minus POUs during online change)
128 kbyte (minus task-configuration minus POUs during online change)
Data memory
32 kbyte
128 kbyte
Source code memory
256 kbyte
Remanent flags
2 kbyte
Persistent data
1000 bytes
INPUT
2 kbyte
OUTPUT
2 kbyte
FLAG
4 kbyte
max. variable size
16 kbyte
Max. POUs
Limited by memory
PLC cycle time for 1,000 commands (without I/O cycle, K-bus)
approx. 0.9 ms
approx. 0.7 ms
Number of runtime systems
1
Programming languages
IEC 6-1131-3 (IL, LD, FBD, ST, SFC)
Online Change
yes
Fieldbus
BC9191
BC9191-0100
Fieldbus
Ethernet
Ethernet connection
2 x RJ45 (internal switch)
Auto-crossing
yes
Data transfer rate
10/100 Mbaud
Protocols
Modbus TCP/IP, Ethernet TCP/IP, Beckhoff ADS via TCP and UDP
Data transfer medium
4 x 2 twisted-pair copper cable; category 3 (10 Mbaud), category 5 (100 Mbaud)
Distance between modules
100 m (distributor hub to BC9191)
Line: max. 100 m between two BC9191
Topology
- star wiring
- line wiring (20 x BC9191 in line maximum)
Number of I/O modules
only limited by the IP address range
Number of I/O points
depending on the higher-level controller
Connections
BC9191
BC9191-0100
Number of ADS connections via TCP/IP
5
Number of ADS connections via UDP/IP
1
Number of ModbusTCP connections
3
SMTP (Simple Mail Transfer Protocol)
yes
SNTP (Simple Network Time Protocol)
yes
BootP/DHCP
yes/yes
UDP socket connections
3
TCP socket connections
3
Technical data 1:
Try using as few TCP/IP connections as possible
The number of TCP/IP connections should be reduced to a minimum. The fewer TCP/IP connections you use, the more time the BC9191 has for its actual task. If possible, use communication via ADS instead of TCP/IP or UDP/IP communication.
Communicate with "reasonable" time intervals for TCP/IP and for UDP/IP connections.
Example:
The task time of the BC9191 is 20 ms. In this case, you should not communicate with the BC9191 more often than every 40 ms.