Technical data
Bus Terminal Controller | BC9191 | BC9191-0100 |
Number of Bus Terminals | 64 | |
Maximum fieldbus byte number | 512 bytes input, 512 bytes output | |
Digital inputs | 3, for connecting potential-free contacts (e.g. for window contact, dew point sensor, occupancy sensor) | |
Digital outputs | 1 x LED output, constant current 10 mA , max. 24 V (e.g. for LED occupancy signal) | |
Analog inputs | 1 x PT/Ni1000 (PT1000: -20...+60 °C, NI1000: -15...+55 °C) for air temperature measurement | |
Analog outputs | 2 x 0...10 V (e.g. air volume controller) | |
Sub-bus systems | 1 x K-bus | 1 x K-bus |
Dielectric strength | 500 V (supply voltage/fieldbus) | |
Supply voltage | 110 ... 240 VAC | |
Current consumption | typically 80 mA (230 V), max. 220 mA (85 V) | |
Power loss | max. 15 W, typically 8 W (without 24 V DC consumers and without further bus terminals) | |
K-bus power supply | max. 200 mA | |
24VDC power supply | max. 100 mA | |
Weight | approx. 350 g | |
Permissible ambient temperature range during operation | 0 °C ... +55 °C | |
Permissible ambient temperature range during storage | -25 °C ... +85 °C | |
Permissible relative humidity | max. 95 %, no condensation | |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |
Correct installation position | vertically on a mounting rail mounted horizontally on the wall (see chapter Installation position) | |
Protection class | IP20 | |
Approvals/markings* | CE UKCA, EAC | |
PLC | BC9191 | BC9191-0100 |
Programming/configuration | with TwinCAT via Ethernet (TwinCAT 2.11 Build 2034 or higher, no TC3) | |
Program memory | 48 kbyte (minus task-configuration minus POUs during online change) | 128 kbyte (minus task-configuration minus POUs during online change) |
Data memory | 32 kbyte | 128 kbyte |
Source code memory | 256 kbyte | |
Remanent flags | 2 kbyte | |
Persistent data | 1000 bytes | |
INPUT | 2 kbyte | |
OUTPUT | 2 kbyte | |
FLAG | 4 kbyte | |
max. variable size | 16 kbyte | |
Max. POUs | Limited by memory | |
PLC cycle time for 1,000 commands (without I/O cycle, K-bus) | approx. 0.9 ms | approx. 0.7 ms |
Number of runtime systems | 1 | |
Programming languages | IEC 6-1131-3 (IL, LD, FBD, ST, SFC) | |
Online Change | yes | |
Fieldbus | BC9191 | BC9191-0100 |
Fieldbus | Ethernet | |
Ethernet connection | 2 x RJ45 (internal switch) | |
Auto-crossing | yes | |
Data transfer rate | 10/100 Mbaud | |
Protocols | Modbus TCP/IP, Ethernet TCP/IP, Beckhoff ADS via TCP and UDP | |
Data transfer medium | 4 x 2 twisted-pair copper cable; category 3 (10 Mbaud), category 5 (100 Mbaud) | |
Distance between modules | 100 m (distributor hub to BC9191) Line: max. 100 m between two BC9191 | |
Topology | - star wiring | |
Number of I/O modules | only limited by the IP address range | |
Number of I/O points | depending on the higher-level controller | |
Connections | BC9191 | BC9191-0100 |
Number of ADS connections via TCP/IP | 5 | |
Number of ADS connections via UDP/IP | 1 | |
Number of ModbusTCP connections | 3 | |
SMTP (Simple Mail Transfer Protocol) | yes | |
SNTP (Simple Network Time Protocol) | yes | |
BootP/DHCP | yes/yes | |
UDP socket connections | 3 | |
TCP socket connections | 3 | |
![]() | Try using as few TCP/IP connections as possible The number of TCP/IP connections should be reduced to a minimum. The fewer TCP/IP connections you use, the more time the BC9191 has for its actual task. If possible, use communication via ADS instead of TCP/IP or UDP/IP communication. Communicate with "reasonable" time intervals for TCP/IP and for UDP/IP connections. |