Cables
General specification
Beckhoff offers pre-assembled motor and feedback cables for faster and flawless installation. Design, dimensioning and installation have significant influence on the function of a servo system. Beckhoff servo cables have been tested with regard to the material used, screening and connection, in order to guarantee proper function and compliance with statutory requirements such as EMC. The use of other may invalidate the warranty.
Wire cross-section depending on the cable length (according to EN60402)
Minimum wire cross-section depending on cable length and current
Line load for different types of installation:
Fire hazard! If several servo drives are operated at the same time the resulting total current of the configuration must be considered for dimensioning of the cables. The information provides in this section should be regarded as guidance. It is not intended as a substitute for professional design based on the specific application. |
Cable cross-section | Three-core non-metallic sheathed cable or conduit | Three-core non-metallic sheathed cable, stacked on wall | Three-core non-metallic sheathed cable, side by side, horizontal | |
[mm²] | [AWG] | [A] | [A] | [A] |
1.5 | 16 | 12.2 | 15.2 | 16.1 |
2.5 | 12 | 16.5 | 21.0 | 22 |
4 | 10 | 23 | 28.0 | 30 |
6 | 10 | 29 | 36.0 | 37 |
10 | 8 | 40 | 50.0 | 52 |
16 |
| 53 | 66.0 | 70 |
25 |
| 67 | 84.0 | 88 |
35 |
| 83 | 104.0 | 114 |
Line load according to EN60204-1, Table 5, at an ambient temperature of 40°C
Two cable qualities are offered: Cables for fixed installation (static application), and cables for highly dynamic applications such as drag chains.
General data | Specification |
Min. bending radius | 18 x outside diameter |
Max. horizontal velocity | 180 m/min |
Max. acceleration | 5 m/s² |
Max. no. of cycles | 50,000 |
Max. tensile load | 20 N/mm² |
Operating temperature | -10°C to +80°C |
Standards and specifications | Motor cable | Encoder cable |
UL AWM-listed | 80°C 1000 V | 80°C 30 V |
CSA AWM-listed | 75°C 1000V | 75°C 30 V |
VDE (U0 / U) | 0.6 / 1 kV | --- |
Flame resistance | DIN EN 50265-2-1 | |
Oil resistance | UL 1581 | |
Silicone-free | yes | |
CFC-free | yes | |
Halogen-free | no | |
Specification | Motor cable | Encoder cable |
Sheath | Specification | |
Material | PVC according to UL AWM & CSA AWM | |
Screen | tinned copper braid, optical cover ≥ 85 % | |
Separator | polyester tape | |
Diameter | 11.3 mm ± 0.4 mm | 7.6 mm ± 0.3 mm |
Weight | ____ kg / km | ____ kg / km |
Colour | orange RAL 2003 | green RAL 6018 |
Power | 4x1.5 mm² | 2x0.5 mm² |
Conductor material | bare copper Cl. 5 (IEC 60228) | tinned copper 19 x 0.18 mm |
Insulation | TEO Flexene ® polymer compound according to UL AWM & CSA AWM | polypropylene, according to UL AWM & CSA AWM |
Colour code | black (1 - 3) + green/yellow | |
Signal | 2x(2x0.75) mm² | 7x(2x0.14) mm² |
Conductor material | bare copper Cl. 5 (IEC 60228) | tinned copper 7 x 0.16 mm |
Structure | pair-wise twisted | |
Screen per pair | tinned copper sheath, optical cover ≥ 85 % | --- |
Separator | fleece tape | --- |
Colour code | pair 1: black (5 - 6) | |
Electrical specification |
Test conditions | 20°C |
Conductor resistance | IEC 60228 Cl. 5 | 0.5 mm²: ≤ 40 Ω/km |
Insulation resistance | ≥ 2500 MΩ x km | |
Operating voltage | ≤ 1000 V | ≤ 30 V |
Test voltage: |
| 1500 VDC |
Capacitance |
Cables for flexible installation / highly dynamic operation
Min. bending radius | 7 x outside diameter |
Max. horizontal velocity | 240 m/min |
Max. acceleration | 30 m/s² |
max. moved horizontal length | 20 m |
max. vertical length | 5 m |
Max. no. of cycles | 10 million |
VDE | 0.6 / 1 kV | --- |
CFC-free | yes | |
Halogen-free | yes | |
Material | TMPU halogen-free, accordingly UL AWM & CSA AWM | |
Diameter | 12.2 mm ± 0.4 mm | 7.6 mm ± 0.3 mm |
Conductor material | bare copper Cl. 5 (IEC 60228) | tinned copper 7 x 0,16 mm |
Test voltage: |
| 1500 VDC |
Capacitance |