Connection example – DC link network (60...170 A devices)
This connection technology enables you to establish a DC link network for servo drives from the AX5160…AX5193 series.
The following figure describes a possible configuration example of a DC link network:
Connection example – DC link network (60...170 A devices) 1:
Legend:
F0-n
Mains fuses = UL fuse (480 VAC)
FDC1-DCn
DC link fuses (DC fuses) = UL fuse (700 VAC / 800 VDC)
e.g. ferrule FWP from Cooper-Bussmann
K0
Common mains contactor
L0
Mains choke
Z1-n
Mains filter
optional for AX5160 and AX5170
for AX5190…AX5193: required to comply with C3 per EN 61800-3
NOTICE
Connection example – DC link network (60...170 A devices) 2:
Configuration of a DC link network!
Before implementing a DC link network, please contact your UL certification body and discuss the other necessary boundary conditions.
Dimensioning of the UL fuse FDC1-FDCn
The dimensioning of the fuses FDC1 to FDCn in the DC link is application-dependent. The motor and the load profile are incorporated directly into the calculation. Please consider this when dimensioning.
NOTICE
Connection example – DC link network (60...170 A devices) 3:
Fuse holders with UL approval
Note when using UL circuit breakers that the necessary fuse holders also have to carry UL approval.
Mains choke
To ensure balancing of all servo drives, a common mains choke (Lo) must be provided. The rated current of the mains choke must be ≥ the rated current of the common mains fuse (F0) of the drive system (see chapter Mains fuse). The short-circuit voltage of the mains chokes must be
Uk = 2%.
Dimensioning the mains fuse
The following chapter describes the dimensioning of the mains fuses to be used for individual devices and the use of mains fuses in the DC link network.
Series AX5160…AX5193 (60 A…170 A):
Individual device:
DC link network:
The local regulations and the local conditions (ambient temperature, cable routing, etc.) must be referred to when determining the permissible current carrying capacity of the cables (selection of the necessary cross-section – see chapter Motors and Cables).
Dimensioning example:
1 x AX5172
2 x AX5192
1 x AX5193
72 A
286 A
170 A
= 528 A x 1.1 = 581 A
630 A selected
Mains switch-on conditions:
The mains must be switched through to all servo drives simultaneously. Therefore, use a common mains contactor (K0) for all servo drives. The phase error detection (grid monitoring) of the servo drives must be active. Observe the relevant parameterization for this (P-0-0204 Disable Umain monitoring and Umain phase error detection).
Parameterization P-0-0204:
The default values of the parameter P-0-0204 (Power management control word) are set to:
In the DC link network the default values of the parameter P-0-0204 are to be checked before commissioning and set to the above values if discrepancies are found.
Parameterization P-0-0214:
To parameterize an AX5160 – AX5193 DC link network, the following settings must be made in parameter P-0-0214 (DC link connection mode):
The external braking resistor is activated in both cases.
Mains filter:
If mains filters are used, a separate mains filter must be used for each servo drive. The mains filter must be positioned as close to the servo drive as possible. Use short cables without loops.
A suitable shield connection is ensured by adhering to the following points:
Max. cable sizes accepted by the connecting terminals:
The maximum cable cross-sections are dictated by the maximum cable sizes that can be accepted by the connecting terminals on the servo drive (see table below):
Device type
Mains terminal
Motor terminal
DC link terminal
Rb terminal
min.
[mm² / AWG]
max.
[mm² / AWG]
min.
[mm² / AWG]
max.
[mm² / AWG]
min.
[mm² / AWG]
max.
[mm² / AWG]
min.
[mm² / AWG]
max.
[mm² / AWG]
AX5160
4 / 12)
35 / 2
4 / 12
35 / 2
4 / 12
35 / 2
4 / 12
35 / 2
AX5172
4 / 12
35 / 2
4 / 12
35 / 2
4 / 12
35 / 2
4 / 12
35 / 2
AX5190
25 / 4
95 / 2/0
35 / 2
95 / 3/0
25 / 6
50 / 2/0
25 / 6
50 / 2/0
AX5191
25 / 4
95 / 2/0
35 / 2
95 / 3/0
25 / 6
50 / 2/0
25 / 6
50 / 2/0
AX5192
25 / 4
95 / 2/0
50 / 1/0
150 / 300
50 / 1/0
150 / 300
25 / 6
50 / 2/0
AX5193
25 / 4
95 / 2/0
50 / 1/0
150 / 300
50 / 1/0
150 / 300
25 / 6
50 / 2/0
Dimensioning of the braking resistors for operation in the DC link network:
In individual braking situations the energy balance in the DC link network can be generative. Servo drives from the AX5160…AX5193 series do not have an internal braking resistor. External braking resistors must be used to dissipate the resulting energy. The braking resistor must always be connected to the connection provided on the servo drive.
In a DC link network, it is possible to dispense with one or more braking resistors under the following conditions:
Part of the braking energy is also stored in the DC link, independent of the braking resistor. The more servo drives there are in the DC link network, the larger the storage capacity. It is therefore possible to store more energy.
The following must be considered when dimensioning the braking resistors:
Servo drive
AX5160
AX5172
AX5190
AX5191
AX5192
AX5193
Min. braking resistance
(external braking resistor)
13 Ω
13 Ω
10 Ω
10 Ω
6.5 Ω
6.5 Ω
Connection example – DC link network (60...170 A devices) 5:
Where
Ppeak_Br_DC
is the peak braking power of the entire DC link network and
Peff_Br_DC
is the effective braking power of the entire group
DC link network with other AX5000 servo drives:
Connection example – DC link network (60...170 A devices) 6:
No DC link network permissible with devices for 1.5 A…40 A!
Servo drives from the AX5101…AX5140 series are excluded from the DC link network with servo drives from the AX5160…AX5193 series and may NOT be connected to one another! The DC link network described here is permissible only for AX5160…AX5193 servo drives!