IDN Notation Format
The IDN set supported by AX2000-B750 is listed in numerical order with a short description for each IDN. The descriptions use the following format:
Below you'll find an example of the IDN description structure.
IDN 1  Numeric Cycle Time
The cycle time of the numeric controller (TNcyc). This time corresponds to IDN 2, which specifies the SERCOS cycle time (TScyc).
Data Length:
2 bytes
Non-Volatile:
No
Data Type:
Unsigned decimal
Write Access:
CP2
Minimum:
1000
Run-Up Check:
CP2
Maximum:
8000
Cyclic Transfer:
Default:
2000
Serial Equiv:
Units:
μs
Version:
IDN Type:
SC
ADS Index Group (hex.):
0x0001
Note:
Not all IDN descriptions require all the fields listed above. Only the applicable fields are filled within an IDN description. The field definitions are as follows:
IDN x
The identification number in short-hand notation.
S-x-xxxx / P-x-xxxx
According to IEC 61491 specified notation of a SERCOS identification number.
S-x-xxxx are SERCOS standard-specific identification numbers, versus P-x-xxxx are product-specific ones.
Title
A descriptive title of the IDN (in above case it is: Numeric Cycle Time).
Information of the IDN purpose and relations/dependencies to other IDN's are named here.
Data Length
The length of IDN element 0 resp. 7, in bytes. Possible entries for this field are as follows:
2 bytes
The length of the operating data is 2 bytes.
4 bytes
The length of the operating data is 4 bytes.
1 byte var.
The length of the operating data is variable. The length of one data element is 1 byte.
2 bytes var.
The length of the operating data is variable. The length of one data element is 2 bytes.
4 bytes var.
The length of the operating data is variable. The length of one data element is 4 bytes.
Data Type
The format for interpreting and displaying the operating data. Possible entries for this field are binary, unsigned decimal, signed decimal, hexadecimal, text and IDN.
Minimum / Maximum
The allowed range of IDN element 7 data. IDN element 7 is checked for range compliance in the service channel. In general, if the range is blank in the IDN description, this means that IDN elements 5 and 6 are not supported. The ranges of some IDNs are dependent upon the value of other IDNs, drive parameters or motor parameters.
Default
The default value for IDN element 7 data. An IDN will revert to its default value after a firmware upgrade. The default may be a fixed value, or it may be stored in non-volatile memory. A blank “Default” field indicates that the IDN does not have a default value.
Units
The units of IDN element 7 data and of the minimum, maximum, and default fields. The units of some IDNs are obtained from the operating data of other IDNs. IDNs of data type “binary”, “text”, or “IDN” do not have units and the “Units” field is left blank in the IDN description.
Non-Volatile
Indicates whether the IDN operation data can be saved in non-volatile memory. Possible entries for this field are as follows:
(blank)     - The operating data is stored in volatile memory and is lost when logic power is removed.
Yes           - The operating data may be stored in non-volatile memory and will be retained after power down.
Write Access
The SERCOS communication phases (CPx) during which an IDN may be written. In general, an IDN may be read through the service channel during communication phases CP2 and above. However, writing to an IDN may be restricted during some communication phases or while the drive is enabled. An entry of “Read-only” indicates that the IDN cannot be written during any communication phase.
Run-Up Check
The SERCOS communication phases (CPx) during which the validity of the operating data is checked. Possible entries for this field are as follows:
(blank)
The validity of the operating data is not checked
CP2
The validity of the operating data will be checked in the procedure “S-0-0127 Communication phase 3 transition check.”
CP3
The validity of the operating data will be checked in the procedure “S-0-0128 Communication phase 4 transition check.”
Cyclic Transfer
Indicates whether cyclic transfer is possible for IDN element 7. Possible entries for this field are as follows:
(blank)
The operating data is not cyclic.
MDT
The IDN may be transferred within the MDT as cyclic data.
AT
The IDN may be transferred within the AT as cyclic data.
Serial Equivalent
An equation of equivalent protocol commands that may be issued through the RS-232/485 serial port (e.g., through the Microsoft Windows® HyperTerminal program to be started with:  Start | Run ... type hypertrm.exe) to obtain the IDN data. The contents of the IDN can be obtained by evaluating the equation. The field is blank in the IDN description if no equivalent serial commands are available.
Version
The drive Firmware version from which on this IDN is supported.
IDN Type
The
IndexGroup
Names the ADS IndexGroup to use for accessing this IDN via ADS in a hexa-decimal format. The IndexOffset, which is also necessary for the ADS command, specifies the required element from this SERCOS IDN in this context. The IndexOffset (IdxOffs) to use, varies from case to case.
IndexOffset specification:
0 or 7
value
1
Data Status
2
Name (read only)
3
Attribute (refer to SERCOS specification IEC 61491)
4
Unit
5
Minimum
6
Maximum
TwinCAT PLC contains a function block library (TcSystem.lib) for the ADSREAD and ADSWRITE access of objects accessible via the ADS protocol.