Power supply
Notice
Fuse protection of the load voltage
The electrical fuse protection of the load voltage must be selected in such a way that the maximum current flowing is limited to 3 times the nominal current (max. 1 second)!
Notice
Malfunction due to equalizing currents on the protective conductor
In the event of a fault, the resulting equalizing currents can lead to higher currents on the return conductors of the circuits and can damage them and/or the product.
  • The power supplies UP and US of the integrated stepper motor drive must either both be designed as SELV or both as PELV.
  • Design the power supplies for the load voltage UP and the control voltage US as SELV (Safety Extra Low Voltage) with safe isolation so that there is no connection to earth, protective conductor or active parts of the two circuits with each other.
  • Design the power supplies for the load voltage UP and the control voltage US as PELV (Protective Extra Low Voltage) with safe isolation so that there is no connection to earth, protective conductor or active parts of the two circuits with each other. Use a circuit breaker according to the power supply, e.g.
    circuit breaker 400 V 10 kA, 2-pole, B, 6 A, D=70 mm, article number 5SY4206-6, manufacturer Siemens.
The integrated stepper motor drive ASI8100 requires two supply voltages for operation:
The voltages must be fed in at slot X5.
Power supply 1:
To easily set up the power supply, use the following accessories:
EP9208-1035
EtherCAT Box, 8-channel power distribution, passive, M12, L-coded
For more information, see Power supply