X01 for single-phase devices
Valid for:
- All single-phase devices in the AF1000 series
- AF11xx-1xxx
- AF12xx-1xxx
Network connection on connection strip X01

Feature | Implementation |
|---|---|
Connection type | Connection strip |
Contact type | Direct plug-in technique |
Number of contacts | 5-pin |
Connectable conductors at this connection
|
Technical parameter |
Unit |
min. |
max. |
|---|---|---|---|
Clamping range | mm² | 0.34 | 4 |
Conductor connection cross-section AWG | AWG | 20 | 12 |
solid wire H05(07) V-U | mm² | 0.5 | 2.5 |
stranded wire H05(07) V-K | mm² | 0.5 | 4 |
with ferrule with collar DIN 46 228/4 | mm² | 0.34 | 2.5 |
with ferrule DIN 46 228/1 | mm² | 0.5 | 2.5 |
Stripping length | mm | 8 | 10 |
If single wires or strands are used, the wiring route from the filter to the mains connection must be realized with twisted wires or strands.
Contact assignment at this connection
Terminal point | Connection |
|---|---|
L | Phase L |
N | Neutral conductor N |
PE | Protective conductor, PE |
RB+ | External braking resistor + |
RB- | External braking resistor - |