S-0-0410 Probe 1 negative latched (Counter)
This parameter indicates whether a positive edge occurred at Probe 1.
Attributes
Value
Data type
binary
Data length
16
Decimal point
0
Min value
Max value
Default
Unit
Changeable in EtherCAT state
No
Cyclic transfer
AT
Device parameter
No
Related to interface revision
No
An IDN can be assigned to this parameter, allowing this parameter to be assigned to a real-time status bit. The drive only sets bit 0 of this parameter if the command S-0-0170 is enabled, S-0-0405 is set to 1, and the negative edge of S-0-0401 is enabled.
When the negative edge occurs at the input, the drive stores the parameterized source value in S-0-0131. The drive resets this bit when the controller aborts command S-0-0170 or when S-0-0405 is reset to 0.
Bit pattern:
Bit
Meaning
0
Probe 1
Probe 1
0 = not enabled
1 = enabled
1–15
Reserved
S-0-0410 Probe 1 negative latched (Counter) 1:
IDNs involved
S-0-0131, S-0-0170, S-0-0179, S-0-0305, S-0-0405
S-0-0410 Probe 1 negative latched (Counter) 2:
Additional functional description
AX5000 / Probe unit