KL5051 - Bidirectional SSI encoder interface
Register description
The registers can be read or written via the register communication. They are used for the parameterization of the terminal.
R0 to R7: Registers in the internal RAM of the terminal
The process variables can be used in addition to the actual process image. Their function is specific to the terminal.
R0 to R5: reserved
R6: Diagnostic register
The diagnostic register can contain additional diagnostic information. Parity errors, for instance, that occur in serial interface terminals during data transmission are indicated here.
R7: Command register
High-Byte_Write = function parameter
Low-Byte_Write = function number
High-Byte_Read = function result
Low-Byte_Read = function number
R8 to R15: Registers in the internal ROM of the terminal
The type and system parameters are hard programmed by the manufacturer, and the user can read them but cannot change them.
R8: Terminal type
The terminal type in register R8 is needed to identify the terminal.
R9: Software version (X.y)
The software version can be read as a string of ASCII characters.
R10: Data length
R10 contains the number of multiplexed shift registers and their length in bits.
The Bus Coupler sees this structure.
R11: Signal channels
Related to R10, this contains the number of channels that are logically present. Thus for example a shift register that is physically present can perfectly well consist of several signal channels.
R12: Minimum data length
The particular byte contains the minimum data length for a channel that is to be transferred. If the MSB is set, the control and status byte is not necessarily required for the terminal function and is not transferred to the control, if the Bus Coupler is configured accordingly.
R13: Data type register
Data type register
Meaning
0x00
Terminal with no valid data type
0x01
Byte array
0x02
Structure 1 byte n bytes
0x03
Word array
0x04
Structure 1 byte n words
0x05
Double word array
0x06
Structure 1 byte n double words
0x07
Structure 1 byte 1 double word
0x08
0x11
Byte array with variable logical channel length
0x12
Structure 1 byte n bytes with variable logical channel length (e.g. 60xx)
0x13
Word array with variable logical channel length
0x14
Structure 1 byte n words with variable logical channel length
0x15
Double word array with variable logical channel length
0x16
Structure 1 byte n double words with variable logical channel length
R14: reserved
R15: Alignment bits (RAM)
The alignment bits are used to place the analog terminal in the Bus Coupler on a byte boundary.
R16 to R30: Manufacturer parameter area (SEEROM)
The manufacturer parameters are specific for each type of terminal. They are programmed by the manufacturer, but can also be modified by the controller. The manufacturer parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out.
These registers can only be altered after a code word has been set in R31.
R31 to R47: User parameter area (SEEROM)
The user parameters are specific for each type of terminal. They can be modified by the programmer. The user parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out. The user area is write-protected by a code word.
• R31: Code word register in RAM
The code word 0x1235 must be entered here so that parameters in the user area can be modified. If any other value is entered into this register, the write-protection is active. When write protection is not active, the code word is returned when the register is read. If the write protection is active, the register contains a zero value.
R32: Feature register
This register specifies the operation modes of the terminal. Thus, for instance, a user-specific scaling can be activated for the analog I/Os.
R33 - R47
Registers that depend on the terminal type.
R47 - R63
Extended registers with additional functions.
