Register description
The registers can be read or written via the register communication. They are used for the parameterization of the terminal.
R0 to R7: Registers in the internal RAM of the terminal
The process variables can be used in addition to the actual process image. Their function is specific to the terminal.
R8 to R15: Registers in the internal ROM of the terminal
The type and system parameters are hard programmed by the manufacturer, and the user can read them but cannot change them.
Data type register
Meaning
0x00
Terminal with no valid data type
0x01
Byte array
0x02
Structure 1 byte n bytes
0x03
Word array
0x04
Structure 1 byte n words
0x05
Double word array
0x06
Structure 1 byte n double words
0x07
Structure 1 byte 1 double word
0x08
0x11
Byte array with variable logical channel length
0x12
Structure 1 byte n bytes with variable logical channel length (e.g. 60xx)
0x13
Word array with variable logical channel length
0x14
Structure 1 byte n words with variable logical channel length
0x15
Double word array with variable logical channel length
0x16
Structure 1 byte n double words with variable logical channel length
R16 to R30: Manufacturer parameter area (SEEROM)
The manufacturer parameters are specific for each type of terminal. They are programmed by the manufacturer, but can also be modified by the controller. The manufacturer parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out.
These registers can only be altered after a code word has been set in R31.
R31 to R47: User parameter area (SEEROM)
The user parameters are specific for each type of terminal. They can be modified by the programmer. The user parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out. The user area is write-protected by a code word.
Register description 1:
• R31: Code word register in RAM
The code word 0x1235 must be entered here so that parameters in the user area can be modified. If any other value is entered into this register, the write-protection is active. When write protection is not active, the code word is returned when the register is read. If the write protection is active, the register contains a zero value.
Feature bit no.
Description of the operation mode
Bit 0
1
User scaling (R33, R34) active [0]
Bit 1
1
Manufacturer scaling (R19, R20) active [1]
Bit 2
1
Watchdog timer active [1]
In the delivery state, the watchdog timer is switched on.
Bit 3
1
Sign / amount representation [0]
Sign / amount representation is active instead of two's-complement representation. (-1 = 0x8001).
Bit 4
1
Siemens output format [0]
This bit is used for inserting status information on the lowest 3 bits (see below).
Bits 5 to 7
Reserved, don't change
Bit 8
1
Over range Protection [1]
If values exceed or fall below the limits of the registers OVRL (R21) and UNRL (R22), the status bits are set and the measuring range is restricted accordingly.
Bit 9
1
Limit value 1 active [0]
The process data are compared with limit value 1 (R35), and appropriate status bits are set.
Bit 10
1
Limit value 2 active [0]
The process data are compared with limit value 2 (R36), and appropriate status bits are set.
Bit 11
1
Filter1 active [0]
For filter properties, see R37
Bits 12 to 15
If the Siemens output format is selected, the lowest three bits are used for status evaluation. The process data is represented in bits 15 to 3, with bit 15 representing the sign bit. Scaling of the measured value according to the Siemens standard has to be done via user scaling (R33, R34).
KL3061, KL3062
Measured value
Bits 15 to 3
Bit 2
X
Bit1
Error
Bit 0
Overflow
Measured value > 10 V
0
0
1
Measured value <10 V
Process data
0
0
0
KL3064
Measured value
Bits 15 to 3
Bit 2
X
Bit1
Error
Bit 0
Overflow
X
ERROR
Overflow
0
0
1
Process data
0
0
0
Register description 2:
Applies to all terminals from firmware version 3x.
This documentation applies to all terminals from firmware version 3x. The version information can be found on the right-hand side of the terminal in the serial number: xxxx3xxx.
Example: 52983A2A => the firmware version is 3A.
R37
Explanation
0x0000
2nd order FIR filter
default value
0x0100
1st order IIR filter, cut-off frequency Fg approx.1 kHz
The implemented IIR filters do not have any notch behavior, i.e., they do not explicitly suppress any frequency.
0x0200
1st order IIR filter, cut-off frequency Fg approx. 100 Hz
0x0300
1st order IIR filter, cut-off frequency Fg approx. 50 Hz
0x0400
1st order IIR filter, cut-off frequency Fg approx. 20 Hz
0x0500
1st order IIR filter, cut-off frequency Fg approx. 10 Hz
0x0600
1st order IIR filter, cut-off frequency Fg approx. 5 Hz
0x0700
1st order IIR filter, cut-off frequency Fg approx. 1 Hz
0x1000
50 Hz FIR filter
Averaging over 16 values and first notch 25 Hz
In contrast to the IIR filters, FIR filter have notch behavior. The timer settings of the notch filter are made via channel 0 of the terminal. This means that the 50 Hz filter on channel 0 and the 60 Hz filter on channel 1 cannot be active simultaneously.
0x2000
60 Hz FIR filter
Averaging over 16 values and first notch 20 Hz
Other values
No filter active