Configuration overview
IL230x-B110 Inputs Outputs Working counter status (WcState) Online status (Info Data) ADS address (ADSAddr) EtherCAT cycle time
IL230x-B110 (IL2300-B110, IL2301-B110, IL2302-B110)
In TwinCAT System Manager Config mode enter the IL230x-B110 as an EtherCAT (Direct Mode) device under Devices (Fig. 1). Any Fieldbus Box modules already connected to the network can also be read. All boxes with extensions and configurations are uploaded automatically. You can then adapt these to meet your requirements. FreeRun status must be set in TwinCAT.
Note regarding the screenshots: IP-Link values are displayed as K-Bus values in TwinCAT.
Fbb_B110_TCAT_Sysman1
Fig. 1 TwinCAT tree IL2302-B110
CouplerState, "Online" tab
Display of general Fieldbus Box errors.
Fig. 3 CouplerState, "Online" tab
Outputs
Outputs
CouplerCtrl, "Online" tab
Display of IP-Link/K-Bus errors or deactivation of outputs.
Fig. 4 CouplerCrtl, "Online" tab
WCstate, "Online" tab
Boolean variable indicating the working counter status of the Fieldbus Box. An invalid working counter (value: 1) is displayed if invalid data were transferred by the EtherCAT slave controller.
Fig. 5 WCstate, "Online" tab
State, "Online" tab
Indicates the online status of the Fieldbus Box.
Fig. 6 State, "Online" tab
Value
0x___1
Slave in 'INIT' state
0x___2
Slave in 'PREOP' state
0x___3
Slave in 'BOOT' state
0x___4
Slave in 'SAFEOP' state
0x___8
Slave in 'OP' state
0x001_
Slave signals error
0x002_
Invalid vendorId, productCode... read
0x004_
Initialization error occurred
0x010_
Slave not present
0x020_
Slave signals link error
0x040_
Slave signals missing link
0x080_
Slave signals unexpected link
0x100_
Communication port A
0x200_
Communication port B
0x400_
Communication port C
0x800_
Communication port D
ADSAddr, Online tab
Single line indicating the AMS netID and the AMS port of the Fieldbus Box using the hexadecimal system. This information is required for mailbox communication via ADS.
Example
AC 10 07 3F 02 01 (AMS netID) = 172.16.7.63.2.1
03 E9 (port) = 1001dec
Fig. 7 ADSAddr, "Online" tab
EtherCAT / IP-Link cycle time
The IP-Link cycle time resulting from the station configuration with extension box modules is directly displayed in ConfigMode.
Fig. 8 CycleTime
If the EtherCAT cycle time exceeds the IP-Link cycle time both systems operate in synchronous mode. The IP link is started after an EtherCAT telegram and copies its inputs into the memory. They are retrieved with the next EtherCAT telegram, i.e. the inputs are always exactly one cycle old.
If the EtherCAT cycle is shorter than the IP link cycle, the K-Bus operates asynchronous relative to EtherCAT. Faster polling than "Estimated Cycle (offline)" is therefore possible but may lead to outdated input data or outputs not being set in time via the IP link.
The EtherCAT cycle applied to the IL230x-B110 Fieldbus Box modules should therefore be significantly greater than the "Estimated Cycle (offline)" (min. 250 µs, depending on the configuration). Online control in the system through "Max. Cycle (online)" or "CouplerState" is recommended.
The cycle time can also be read via CoE Online from Table 98 [LO].
Fig. 9 CycleTime via Table98[LO]
Check of the connected boxes
If you activate "Check Terminals at Startup", at startup is checked if the connected boxes fit to the configured boxes.